Is it possible to give us the recommended minimum wire size of power cables for the following condition?
Pout:60W
RL:4Ω
Cable length:80cm
and is there some document for calculation method of recommended minimum wire size?
Thanks
Go
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Hi,
Is it possible to give us the recommended minimum wire size of power cables for the following condition?
Pout:60W
RL:4Ω
Cable length:80cm
and is there some document for calculation method of recommended minimum wire size?
Thanks
Go
Hi, Go,
Sorry, we are a little bit busy right now. I have asked my colleague to get back with you later this week.
-d2
Go,
22 Gauge wire (AWG) is the minimum based on you peak current demand of ~6A for 60W. You can use the website below as a reference.
Go,
The 22 AWG is 16-ohms per kft, so ~1.3-mohms per in. You will have to decide your length and the amount of loss in the wire your application can tolerate. The loss will be 1.3-mohms x wire length (in) x rms current at max output power.