Power Supply
We are looking for a solution for a special power supply.
The power supply is operated either with 1 phase or 3 phases against the neutral.
If I feed with 1 phase, the other two power supplies must be locked.
With a 3-phase supply, I need an output line 4.5kW, with 1 phase is a reduced power
The output is 325V DC
No galvanic isolation
Is there a way to solve this with a reference design?
http://www.ti.com/lit/ug/tidube1c/tidube1c.pdf
http://www.ti.com/lit/df/slur515/slur515.pdf
Input
Nominal Input Voltage 1x230VAC or as an option Nominal Input Voltage 3x230VAC
Line Frequency 40-70 Hz
Output
Nominal DC Output 325V DC
Max Output Power about 3000W @ 1x230VAC Input or as an option Max Output Power 4500W @ 3x230VAC Input
PSU |
Parameter |
Nominal Input AC Voltage |
1×230 VAC or 3×230 VAC (L-N) |
Input Toleranz |
230 VAC (@+/-10% >> 207 – 253) (L-N) |
Max Input AC Voltage |
1×270 VAC (L-N) (253 @ 10%) |
Max Output Power Cont. |
4500 W@ 3 Phase Single Phase reduced |
Max Output Power Peak |
6000 W, Single Phase reduced |
Nominal DC bus Output |
325 VDC (at nominal AC Input Voltage) |
DC Output Cont. Current |
15 A |
DC Output Peak Current |
25 A |
Shunt Power (Peak) |
no |
Ambient operating temperature |
-10° bis +50° |
Cooling |
without fan / without air flow |
Maximum non-condensing humidity |
90% |
Isolation |
not isolated |
Here a link to the drawing