BridgelessPFC example project possible mistakes(contolSUITE3.3.4)

The example project is BridgelessPFC, in the BridgelessPFC-Main.c there  may exist some mistakes

Line901-910

// PWM based ISR trigger

PieVectTable.EPWM1_INT = &DPL_ISR;         // Map Interrupt

PieCtrlRegs.PIEIER3.bit.INTx1 = 1;         // PIE level enable, Grp3 / Int1, ePWM1

EPwm1Regs.CMPB = 80;                       // ISR trigger point

EPwm1Regs.ETSEL.bit.INTSEL = ET_CTRU_CMPB;     // INT on CompareB-Up event

EPwm1Regs.ETSEL.bit.INTEN = 1;              // Enable INT

//   EPwm1Regs.ETPS.bit.INTPRD = ET_1ST;         // Generate INT on every event                                              

EPwm1Regs.ETPS.bit.INTPRD = ET_2ND;         // Generate INT on every event

Is this comment right?ET_1ST means Generate INT on every event,but ET_2ND means Generate INT on every other event

Line557-560 

// Configure ePWMs to generate ADC SOC pulses

EPwm1Regs.ETSEL.bit.SOCAEN = 1;                    // Enable ePWM1 SOCA pulse

EPwm1Regs.ETSEL.bit.SOCASEL = ET_CTR_ZERO;     // SOCA from ePWM1 Zero event

EPwm1Regs.ETPS.bit.SOCAPRD = ET_1ST;           // Trigger ePWM1 SOCA on every event

As the project document(BLPFC_Rev1.1.pdf Page 11) introduced,


the PWM switching frequency is 200kHz, the ISR and ADC sampling frequency are 100kHz, the ISR is triggered on CompareB-Up event, and ADCSOCA from ePWM1 Zero event, but the following code:

EPwm1Regs.ETPS.bit.INTPRD = ET_2ND;

EPwm1Regs.ETPS.bit.SOCAPRD = ET_1ST;

As this configuration, the ISR frequency is 100kHz and ADC sampling frequency is 200kHz,

maybe the right configuration should be:

EPwm1Regs.ETPS.bit.INTPRD = ET_2ND;

EPwm1Regs.ETPS.bit.SOCAPRD = ET_2ND;

Is this right?

  • Sampling ADC signals faster than the interrupt frequency means that the sampled values are ignored in every other 200kHz (ADC sampling) cycle. So the existing configuration is good. The other configuration you suggested should also result in similar PFC performance.

    Shamim

  • Hi Shamim,you are right,the existing configuration is good,but it may be better to coincide with its introduction pdf file,what's more I have found some more misleading comments(for example a float number is Q12 format,but the comment says it's Q11,etc),for a TI beginner,correct comments are very helpful.