XTR116: XTR116 full bridge sensor EXC- ground

Part Number: XTR116
Other Parts Discussed in Thread: PGA308

Tool/software:

I'm using an XTR116 in conjunction with a PGA308 for 4-20mA conditioning on a full bridge sensor.  All grounds appear to be tied to I-RET except for the EXC- of the full bridge.  I would assume that this EXC- ground (circled in green of attached image, needs to be isolated from the I-RET grounds.  I'm assuming this EXC- ground can just be floating or tied to chassis ground.  Looking for verification that it doesn't need to be somehow tied back to the XTR or PGA grounds.  Thanks! 

  • HI Ryan,

    In a 2-wire current transmitter module, the bridge sensor and instrumentation amplifier (PGA308) driving the XTR116 2-wire current transmitter, all need to be referred to the same local ground (IRET). IRET needs to be isolated from the 4-20mA loop supply. 

    Also, on a 4-20mA 2-wire current transmitter application, the total current consumption of the XTR116 + PGA308 + bridge sensor needs to be less than 4-mA.

    Please connect the bridge sensor to IRET as shown on the modified figure below. This is an error on Figure 6-3, and will need to be corrected.

      

    Thank you and Regards,

    Luis

  • Luis,

    Thank you for the response and clarification, this is very helpful.  This makes more sense to me in terms of how the overall concept works as well.  I was really struggling to come up with a separate chassis ground for it without affecting current drain/offset through the bridge. 

    Best,

    Ryan