4-20mA current loop: measurement changes when earth GND connected

Prodigy 120 points

Replies: 18

Views: 188

Part Number: INA219

Hi group,

I am following up on a previous post regarding the use of INA219 for a current loop measurement (question was resolved, with thanks to Ian Williams).

We have implemented the test circuit shown below, where the current loop and a controller are supplied by separate, isolated (floating) DC supplies.  The INA219 is on a breakout board (details at https://learn.adafruit.com/adafruit-ina219-current-sensor-breakout/downloads).  The controller provides 3.3V and is connected to SCL/SDA of the INA219 via the breakout board.

The expected V_shunt value is read back from the INA219, except if an earth ground is introduced on the 0V side of the +5VDC supply as shown.  In that case, the measured value drops by 10-20%.

We are trying to understand why the measurement would change.  Does this introduce another pathway for current flow, through the INA219?  Or is there another reason this would affect the measured V_shunt?  It seems we are making an assumption about isolation that is not valid.

Thank you in advance for any theories or suggestions.

  • Hi Kevin,

    The inputs of the INA219 do have some bias current (20uA typical), so there is a current pathway from the inputs to GND, it is not isolated. The 10-20% shift does seem extreme, though.

    If you use a multimeter and measure the VIN+, VIN-, VS, and GND pins, how do they change with the GND connected vs. disconnected?

    Best regards,

    Ian Williams
    Applications Manager
    Current Sensing

  • In reply to Ian Williams:

    Hi Ian,

    During testing, we did measure from Vs to GND and VIN+ to GND (i.e., the GND reference of the INA219 breakout board).  We did not check VIN-, we can try that as well when making additional measurements.

    Here are the other values:

    Floating: Vs-GND=3.3V, (VIN+)-GND=0.85V

    Grounded: Vs-GND=3.3V, (VIN+)-GND=1.52V

    Since both supplies are isolated (floating) as shown, we were not quite sure what to expect between Vs and VIN+, but in the end the perceived "bus voltage" is quite small.

    Thank you for your thoughts on this.

    Best regards,

    Kevin

  • In reply to Kevin72:

    Hi Kevin,

    I think a signal ground connection is missing at the input side of INA219, as shown in figure 29 of datasheet, allowing the input bias currents of INA219 to flow back to signal ground:

    Kai

  • In reply to kai klaas69:

    Hi Kai,

    Thanks for your message.  Your point is related to the original question, whether we can make this measurement while keeping the two supplies isolated from each other (i.e., not tying 0V of the two supplies together).

    It seems to work until the earth GND is introduced, which comes as a consequence of plugging external equipment to test connectors on the controller card, which then creates the path shown as a dashed line.  I'm not sure why that would affect the measured V_shunt value.

    Best regards,

    Kevin

  • In reply to Kevin72:

    Hi Kevin,

    can you please show an exact schematic of your test circuit? And please add the measurement values into this schematic.

    Kai

  • In reply to Ian Williams:

    Hi Ian,

    Sorry for the long delay, we were setting up a second unit to make those additional measurements.  We measured the voltages and current externally as shown below, as well as reading back the reported shunt voltage from the INA219.

    Value No GND With GND
    Vs 3.30 V 3.30 V
    V+ 0.772 V 1.304 .. 1.319 V (*)
    V- 0.768 V 1.301 .. 1.314 V (*)
    Vdiff 4.0 mV 4.0 mV
    Vshunt 3.97 mV 3.66 mV
    Iloop 3.99 mA 3.99 mA

    (*) V+ and V- are fluctuating when GND is introduced

    So, the externally measured loop current and voltage across the shunt resistance remain consistent and as expected when an external ground connection is introduced.  However, V+ and V- become unstable; these are measured across the two supply "domains" (possibly the 0V reference in the 5V power domain is now noisy?).

    The shunt voltage reported by the INA219 also changes - would that be expected in this case?  Are there any other measurements you would suggest?

    Note that we use the maximum averaging period.  Are V+ and V- averaged separately before computing a difference, or is the difference (V+)-(V-) continually averaged?

    Thanks for your help,

    Kevin

  • In reply to kai klaas69:

    Hi Kai,

    The schematic for the INA219 test board can be found at learn.adafruit.com/.../36267 (it is from Adafruit).

    Unfortunately I cannot provide a schematic for the controller unit, it is a 3rd party design.  I have added some measurements to the high-level block diagram in the previous post, maybe that can help to understand the issue?

    Thanks,

    Kevin

  • In reply to Kevin72:

    Hi Kevin,

    I think that this happens:

    Kai

  • In reply to kai klaas69:

    Hello Kai,

    Thank you for that illustration.  It makes sense that there must be another path for current flow that is affecting the INA219 readout.

    It is still not clear to me why V_diff (measured externally) is different than V_shunt (reported by the INA219).  Wouldn't they be similarly affected?  Maybe it requires a full understanding of the internal operations of the INA219 and the DMM.

    Also, the offset when GND is connected is not fixed - at different I_loop values, the error changes proportionally.  For example with I_loop = 15 mA, V_diff = 15 mV but V_shunt = 13.68 mV.  At 10 mA, the values are 10 mV and 9.16 mV.  So, it appears V_shunt is always ~ 0.92 of the expected value.  Would you expect such a proportional response, rather than a fixed leakage?

    Thanks again for your ideas on this.  If you can think of other measurements that could be useful, please let me know.

    Best regards,

    Kevin

  • In reply to Kevin72:

    Hi Kevin,

    schematics in datasheets are always highly simplified. Sometimes it's difficult to find out what's really going on inside such a chip :-)

    I would run a test: Supply both circuits with batteries, without any connection to mains voltage. But have the signal ground of INA219 connected to safety ground. Do you still see an error?

    Then exchange one (later both) battery by a SELV supply. Look for a SELF supply which specifies the stray capacitance between mains voltage and output and choose a supply with very low stray capacitance.

    Kai