Hi support,
1. When using Two Shunt Sensing & Two AMC1303Mx, Is it Possible to each AMC1303Mx AGND common?
<System Architecture - Use Two Shunt Sensing>
2. Is it Possible to AMC1303Mx AGND and DGND common?
Thanks,
Sanghee
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Hi support,
1. When using Two Shunt Sensing & Two AMC1303Mx, Is it Possible to each AMC1303Mx AGND common?
<System Architecture - Use Two Shunt Sensing>
2. Is it Possible to AMC1303Mx AGND and DGND common?
Thanks,
Sanghee
Hi Sanghee,
Thank you for confirming.
The device will function from an analog perspective if both supply grounds are tied together, however the device will provide no isolation between the high and low side since the grounds are tied together.
If you are having difficulty powering the high-side of the device, I would recommend looking at our AMC33xx devices, such as the AMC3306.
Please let me know if you have additional questions.