How does wire break detection work?
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Wire break detection only works in sink mode. In application the sensors can be far from PLC modules and connected with long cables/wires. Hence, wire break is monitored continuously. Wire break feature will detect if the connection on INx is complete or not.
Sink mode switches between 24V / Open. When VIN = 24 V, the wire is intact since voltage is detected at INx. When the switch is Open, no current flows into INx. The switch will have a parallel path through the wire break resistor so that a minimum current will flow through INx and complete the circuit. If the current is lower than the minimum value, then there is a wire break detected.