DRV110 I peak set 1A, Does it mean the Current Peak Point is 1A ?
red: I coil
green: MOSFET Drain
thanks!
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Hello,
DRV110 I peak set 1A, Does it mean the Current Peak Point is 1A ?
No it is the solenoid pull-in current level that is set for the drive first. This will allow the solenoid to pull-in rapidly. After the pull-in to hold the solenoid plunger in position a lower current can be used. This is automatically changed to hold current in the DRV110. See below from the datasheet.
See below information in the datasheet for configuring peak and hold currents. Thank you.
Regards, Murugavel