[FAQ] Why are the fault shutdown slave rails not off immediately? UCD90xxx

Expert 3855 points
Other Parts Discussed in Thread: UCD90120A, UCD9090, UCD90160A, UCD90160, UCD90240, UCD90320U, UCD90120, UCD9090A, UCD90124, UCD90124A, UCD90320

The faulted rail is configurable to either shutdown immediate or soft off. This is set at the fault response as shown in Figure 25.

For all fault shutdown slave rails, they are sequenced off based on their own sequencing configurations such as dependencies and delays.

For more FAQ please check the following document.

UCD90xxx Family Frequently Asked Questions and Answers 