Hi TI,
I have a design with LM5066I to protect a power output to user. It is +48V at 16A max. I originally designed it to startup with no load, enable (EN) controlled by a digital signal (refer to LM5066I_original excel calculator) and it is working as expected. However, when I preloaded the user terminal with 16A before the eFuse is enabled, no +48V at the user terminal. I believed the MOSFET power is hitting the power limit threshold that I set to be 159W.
Using the excel calculator (refer to LM5066I_new excel calculator), I increase the power limit to 200W and startup load to 7A. I do not have much flexibility to change the MOSFET because I already have my board fabricated. With these conditions, the "recommended slew rate" field is "NA" but I can still set the dVdT rate on Vout to be 0.02V/ms to have a good SOA margin for the MOSFET. Is this something valid? The startup inrush current level is way below the load current and using SS mode seems useless. Switching to power limit mode is also not an option because of the MOSFET SOA. Is there anything else I can do to make the design work or changing MOSFET is my only option? Please advice.
I am also confused with the Start-up: FET Power graph in the calculator. If I startup with Vinmax=51.36V and Iload=7A, the max power is 359.52W but the graph shows 86W. Can you explain how it calculate the MOSFET power?
Thanks