ADS1015 non linear output

Other Parts Discussed in Thread: ADS1015

I'm using ADS1015 in one of my development.I have configured for 2.048 volt reference with single ended analog input.  As per design we are dropping the 4-20mA current from a pressure transmitter across a 220 ohm resistor. I have given this current in column E in the following table. Actual voltage we got at the ADC input is in the column F. Column G is the expected ADC count for the respective voltage in the column F. But we are getting the getting ADC count as per column H. In the attachment you can see that there is no variation even when the ADC input voltage is varied.We have checked this with different reference voltage setting (4.096, 6.192). We are getting same kind of missing codes.

Can somebody share your inputs to overcome this issue?

E F G H
mA volts Exp.Counts Actual Counts
4 0.92 920 921
4.01 0.9223 922 927
4.02 0.9246 925 928
4.03 0.9269 927 928
4.04 0.9292 929 928
4.05 0.9315 932 928
4.06 0.9338 934 928
4.07 0.9361 936 930
4.08 0.9384 938 935
4.09 0.9407 941 942
4.1 0.943 943 947
4.11 0.9453 945 949
4.12 0.9476 948 949
4.13 0.9499 950 949
4.14 0.9522 952 949
4.15 0.9545 955 949
4.16 0.9568 957 949
4.17 0.9591 959 955
4.18 0.9614 961 961
4.19 0.9637 964 965
4.2 0.966 966 969
4.21 0.9683 968 969
4.22 0.9706 971 969
4.23 0.9729 973 969
4.24 0.9752 975 969
4.25 0.9775 977 969
4.26 0.9798 980 974
4.27 0.9821 982 980
4.28 0.9844 984 985
4.29 0.9867 987 989
4.3 0.989 989 989
4.31 0.9913 991 989
4.32 0.9936 994 989
4.33 0.9959 996 989
4.34 0.9982 998 989
4.35 1.0005 1001 993
4.36 1.0028 1003 999
4.37 1.0051 1005 1003
4.38 1.0074 1007 1009
4.39 1.0097 1010 1009
4.4 1.012 1012 1009
4.41 1.0143 1014 1009
4.42 1.0166 1017 1009
4.43 1.0189 1019 1009
4.44 1.0212 1021 1014
4.45 1.0235 1024 1019
4.46 1.0258 1026 1023
4.47 1.0281 1028 1029
4.48 1.0304 1030 1029
4.49 1.0327 1033 1029
4.5 1.035 1035 1029
4.51 1.0373 1037 1029
4.52 1.0396 1040 1029
4.53 1.0419 1042 1031
4.54 1.0442 1044 1037
4.55 1.0465 1047 1042
4.56 1.0488 1049 1048
4.57 1.0511 1051 1050
4.58 1.0534 1053 1050
4.59 1.0557 1056 1050
4.6 1.058 1058 1050
4.61 1.0603 1060 1050
4.62 1.0626 1063 1050
4.63 1.0649 1065 1056
4.64 1.0672 1067 1063
4.65 1.0695 1070 1068
4.66 1.0718 1072 1070

 

Regards,

Kalimuthu C

  • Kalimuthu,

    It appears that you have a lot of noise in your system.  You might want to take a look at your input with an oscilloscope to see how stable your input is.  A voltmeter will take a series of reading and average them.  If there is a lot of noise (mV) on the inputs you should see this with the scope.

    You could have noise on your power supply as well and you may want to verify this too.  Another possibility is layout issues.  You need to keep digital and analog signal traces seperate, and have a good ground plane (and not just a bunch of ground traces) to the power supply.  You also need bypass caps at your supply pin to the ADS1015.

    Best regards,

    Bob B