Tool/software:
Team,
We are using 2 x DAC161S997 for a dual-channel 4-20mA transmitter. Both the DACs share common ground with MCU and there is inbuilt isolation in transmitter circuit.
In the field when both the transmitter outputs are connected to Single Ended inputs of PLC, then it is observed that current for both channels balances to a middle value.
i.e. if
Transmitter CH1 = 6mA
Transmitter CH2 = 8mA
When channels are connected to PLC input AI1 and AI2 respectively then current of both channels balance to middle value of 7mA.
PLC Inputs are Single Ended, Passive (i.e. no Loop Power) and have internal burden resistance of 250 ohms. As per the circuit below both transmitter channels are fed from independent power supply PSU1 and PSU2.
If only any one channel is connected to PLC then the issue is not observed.
Since the PLC inputs are single ended we are not sure if adding external 2x 4-20mA signal isolators will help in resolving the issue.
The Circuit for DAC is as follows: