Part Number: DAC7750
Hi,
I am working with the DAC7750 current output DAC and implementing pH-to-current conversion for an industrial transmitter application.
Requirement
We have a pH range of 0 to 14, which maps to:
-
0–20 mA mode → 0 pH = 0 mA, 14 pH = 20 mA
-
4–20 mA mode → 0 pH = 4 mA, 14 pH = 20 mA
Additionally, we have a requirement to support:
-
Overrange (e.g., pH > 14 → current slightly above 20 mA, say up to ~20.5 mA)
-
Underrange (e.g., pH < 0 → current slightly below 4 mA in 4–20 mode)
Current Understanding
From the datasheet, DAC7750 supports:
-
0–20 mA
-
4–20 mA
-
0–24 mA output ranges
However, it appears that:
-
In 4–20 mA mode, output is limited to 4–20 mA (no true overrange possible)
-
In 0–20 mA mode, output is limited to 0–20 mA
-
The DAC saturates at configured full-scale and does not internally support overrange/underrange signaling
Proposed Approach
To handle overrange/underrange, we are considering:
-
Initializing DAC in 0–24 mA mode
-
Using application-level scaling:
-
0–20 mA → normal operating range
20 mA → overrange region
-
<4 mA (for 4–20 behavior) → underrange region
Example:
-
0 pH → 0 mA (or 4 mA for 4–20 behavior)
-
14 pH → 20 mA
-
pH > 14 → allow current up to ~24 mA (within DAC capability)
Questions
-
Is it recommended to use 0–24 mA mode to implement overrange/underrange behavior for 0–20 mA and 4–20 mA applications?
-
Are there any limitations or accuracy concerns when operating in 0–24 mA mode but using only a subset (0–20 mA/4-20mA) for normal operation?
-
Does DAC7750 provide any internal mechanism for overrange indication, or is this strictly application-level handling?
-
Are there any calibration or gain considerations when using extended range like this?
- What are the configurations and hardware confirmations required for Accuracy and Linearity purpose for 600ohm load condition
- What is the importance of Boost circuitry and without boost circuitry, is there any accuracy effect on this?
Goal
We want to achieve behavior similar to industrial transmitters:
-
Normal: 4–20 mA
-
Overrange: ~20-20.5 mA
-
Underrange: ~3.5–4 mA
DAC Schematic FYR,
Any guidance or confirmation on the recommended approach would be very helpful.
Awaiting for your response
Thanks in advance!