If I use Topology #2 as shown in the datasheet of lmp 90100 then how to calculate temperature from the ADC OUTPUT CODE?
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
If I use Topology #2 as shown in the datasheet of lmp 90100 then how to calculate temperature from the ADC OUTPUT CODE?
Hi,
Once you have the ADC reading for CH0 and CH1 as shown in equation 4 on page 51 of the datasheet you can use the ADC formula on page 50 to determine VIN for both channels. Then subtract Vch0 - Vch1 to get the differential voltage, divide this by the value of IB1. This gives you the resistance of the RTD. You then use the lookup table for the RTD to determine the temperature.
Mike