TMS320F28069M: Motor speed runaway with Instaspin

Part Number: TMS320F28069M


Hi,

We are having some trouble with the speed control of our C2000 based custom board. We are using Instaspin MOTION software to control the speed of a BLDC motor, and most of the time the control is fine, but we are experimenting some speed runaways. The conditions in which the speed runaway condition occurs are the following:

  • Always in the first run (so initial speed = 0)
  • Independent of the reference value
  • Speed loop based PI

And the hardware specs are:

  • µC: TMS320F28069MPZT
  • Encoder:
  • Motor:

According to the customer, the motor is ignoring the reference value and then spins to the maximum speed of the motor. After that condition, they have to turn the system down in order to get the motor idle status. They ensure that all connections are checked and fine.

All control parameters are tunned accordingly to the Instaspin Labs, and indeed the control is fine excepting those occasionally speed runaways. Because of that we can’t imagine the source of the problem, since as far as we know and according to our measures, the overall status of the system is OK. At TI forums we found this topic, which seems to be the same problem we have, and we can confirm that changing the USER_MOTOR_RES_EST_CURRENT value the problem is mitigating, but not disappearing. According to Lab’s guidelines, we have reached the theoretical “perfect” value of that variable, so we have no improve margin in that way.

May you please confirm that the problem may be related with that variable, and what else can we do to completely solve the problem? The customer is really worried because the system is causing damages at the installation, so we need some 100% sure guidelines to completely avoid this problem.

Thank you very much in advance,

Best regards

  • Is sensored based instaSPIN-motion? Or sensorless? Any current waveform for showing the issue you mentioned? What do you mean speed runaway?

  • Hi Yanming,

    I contacted with the customer requesting some graphics and as soon as I receive them I'll share. When I say speed runaway I mean overspeed condition, when motor spins at its maximum speed (may not be the proper word after all).

    I'll contact soon.

  • In the following picture you can see in the left that the reference speed of the vehicle is 0 but the real speed of the vehicle increases to its maximum value. In the right side of the picture you can see the normal behavior, with a vehicle reference 0 value and a vehicle real 0 value. To clarify, motor A and B are opposites, that is why always have same modulus but different sign.

    Here is another picture with a non-zero reference value, and as you can see, the real and reference speed values are always the same, and the motor A and B always opposites.

    I hope these graphics are clear enough to understand the problem. If there is anything else I can do, let me know.

    EDIT: It is sensor based Instaspin MOTION.

  • It's better to have the current waveform captured by an oscilloscope.

    1. Enable Rs recalculation and set the right USER_MOTOR_RES_EST_CURRENT value to ensure both the encoder and the motor are aligned on a zero degree electrical angle.

    2. Make sure that motor parameters and ADC offset are correct.

    3. Set the right acceleration. Don't use a high acceleration during start run the motor.

  • Hi Yanming,

    Sorry for the delay, but customer is busy so they won't be able to send us images by the moment. Anyway, I take some pics of the current waveform in our installations. Here they are:

    RampUp + Fine time

    Fine time

    Current value

    So as you can see after Rs recalculation, in this case the motor spins to the correct speed reference. However, we found that the RampUp time and ResEst current are not appliying correctly. These are the values we used in the pictures above:

    • USER_EST_FREQ_Hz = 15000
    • IndEstCurrent = 30
    • RampUpWaitTime = 2 * USER_EST_FREQ_Hz
    • FineWaitTime = 5 * USER_EST_FREQ_Hz

    We have seen that changing FineWaitTime works correctly, but changing RampUpWaitTime has no effect. Changing IndEstCurrent has some effects on the maximum current value, but doesn't match with the assigned value.

    We are 100% sure that the problem occur during the encoder alingment process, but we don't see anything wrong. May you provide us some guidance on how to face this problem? 

    EDIT

    We got some pics with the problem. All the variables have the same value excepting FineWaitTime, which has the original value (we have checked that this has no effect on system operation). 

    As you can see, as soon as the Rs recalculation ends the motor spins at its maximum speed until we take some action. Hope this help.

    BTW, can we somehow check if the alignment process is correctly done? We think that could be very useful to solve this problem.

  • As mentioned above, please try the following steps.

    1. Enable Rs recalculation and set the right USER_MOTOR_RES_EST_CURRENT value to ensure both the encoder and the motor are aligned on a zero degree electrical angle.

    2. Make sure that motor parameters and ADC offset are correct.

    3. Set the right acceleration. Don't use a high acceleration during start run the motor.

  • I don't know what do you mean. As you can see, Rs recalculation is enabled and the parameters you mention are the correct ones according to the TI documentation and labs.

    I can't provide pics with final configuration because the problem happens very occasionaly in customer installations, but we have not been able to replicate it in our installations.

    Again, we think that parameters and software implementation is fine, but the problem may probably be in the zero alignment. We came to this conclusion after experimentation and everything point to it.

    Our priority at this moment is to check somehow if the alignment is correctly done, is there any way? Any advise?

    And why the Rs recalculation times (specifically RampUp time) are not applying correctly?

  • You can try run the motor without load first to see if there is the same issue. And to check if the issue is only appeared at running the motor with heavy load. If yes, that means the rotor is not aligned to the zero position for encoder offset calibration.

    You should set an enough FineWaitTime for implementing the Rs recalculation to make sure that the rotor is forced to zero position.

  • Thanks for your reply Yanming. Unfortunately, the load can't be detached from the motor as they both are integrated. Here in our installations we can experiment without load, but we have not been able to replicate the problem with the same config they are using. 

    With respect to Fine time, at this moment we have set 1.25 seconds. We can increment this value (as well as customer can) but we prefer not to increment this value too much. Would, for example, a 3 seconds fine time be enough? Should it be greater?

    EDIT

    We are trying to verify the correct alignment of the motor. At this moment we are injecting current through the U phase, and the next step is to inject current though the V phase to check the encoder counts. In this way, we can ensure that the motor is correctly aligned if the number of counts is the correct one. How can we change the phase at which the current is injected?

  • Using a light load could be ok for checking if the rotor is forced to zero position.

    The default time is 7 seconds for fine time, 2 seconds for coarse time. You might try to set the fine time to 5s.

    It's better to inject a positive current to d-axis, and force the rotor angle to zero for alignment.

  • Apparently we solve the problem doing 2 alignments in a row. This way, by the moment at least, we are able to confirm that the encoder counts are the correct ones comparing the results of the 2 alignments. Also increased the fine time, at this moment to 3s, we will be experimenting a few days with this value, algo with the 5s you proposed, and then I will update information about the problem, ie if it has been corrected in all situations, if there is any configuration better than another etc.

    Regards

  • Good. You have to ensure the rotor is forced to zero position for encoder offset calibration every time.

  • Hi Yanming,

    I have 3 questions related to the Rs recalculation process. I'm attaching a current waveform obtained with the current test parameters.

    1. Why Rs RampUp time is still not in concordance with the value we set in user.c? Other times are applying correctly.
    2. Have you some idea why this spike occurs? It happens often, sometimes it is almost unnoticeable, but generally is as huge as this pic shows.
    3. The current level on the second Rs recalculation is extremely small compared to the first one (USER_MOTOR_RES_EST_CURRENT is set to 10A, so first recal is applying more than assigned, and the second less than assigned).

    Regards

  • Why Rs RampUp time is still not in concordance with the value we set in user.c? Other times are applying correctly.

    It also depends on the current ramp rate, you might ignore this, and just make sure that the fine time is correct that is import to force the rotor to the zero position.

    Have you some idea why this spike occurs? It happens often, sometimes it is almost unnoticeable, but generally is as huge as this pic shows.

    It seems like the reference torque current is too large. You might reset or configure the integral variable of both speed and current PI to a appropriate value.

    The current level on the second Rs recalculation is extremely small compared to the first one (USER_MOTOR_RES_EST_CURRENT is set to 10A, so first recal is applying more than assigned, and the second less than assigned).

    Phase 2 and 3 are not for Rs recalculation. Do you enable force angle?

  • Hi Yanming,

    We finally solved the problems discussed last day except RampUp time, but as you recommended, we will focus on Fine time. More experimenting need to be done in order to afirm 100% sure that the problem has been solved, but apparently it is so.

    Thanks for your support and time, you can close this thread.

    Best regards