This thread has been locked.

If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.

TMS320F280049C: Ensuring Correct SCI Flash Kernel Loading to RAM and Behavior

Part Number: TMS320F280049C
Other Parts Discussed in Thread: C2000WARE

Hi Folks,

Wanted to branch out this question because it's more targeted, but I am attempting to perform SCI boot (CPU1_RAM config) from a host custom board ("HOST") to a custom board containing the TMS ("TMS").

Per logic analyzer screenshot below, I am confident that I am able to get the TMS (brown) into the right boot mode, as when I'm loading the flash kernel, it reflects everything the HOST (red) sends up until the last few bytes (0x06, 0x00, 0x00, 0x00, which appear to indicate the end of the kernel image).

However, after that point, I can't get any echo, even if I use autobaud characters, as you can begin to see (the stream of 0x41's). I do this for about five seconds, and then I try to send an erase packet (delimited by 0x1B on either side), just as a test, but nothing happens (no response):

Note that even if I send nothing for the 5 seconds and then fire off the autobaud followed by the erase packet, I still get no autobaud.

Questions:

1. Am I not waiting long enough?

2. Am I sending the character (currently 0x41)?

3. Is my baud incorrect (keeping it slow at 4800)?

4. Is my packet incorrectly constructed? Even a checksum error or something like that should be able to return a packet with a status error, no?

5. What other steps can I take to debug my code?

Best Regards,

Ankur Aggarwal

  • Hi Ankur, 

    1. 5 seconds should be long enough. 

    2. The character looks correct. 

    3. The examples usually use 9600, but 4800 should be ok. 

    4. Looks like the header and footer have the LSB and MSB switched. The LSB needs to be sent before the MSB. The checksum also needs to include the data sent along with the Erase command. If there are errors during transmission, the kernel returns a NAK. Before that though, if the autobaud lock is not occurring, the packet you are transmitting probably isn't making it to the kernel. 

    5. Did you make any changes to the kernel example when using it on your custom board? Were you able to run the example without issues on a ControlCard or launchpad? Knowing what changes were made if any will help pinpoint the issue. 

    Thanks, 

    Anu

  • Hi Anu,

    Thanks for your response!

    We haven't tried on the Launchpad board, but I don't believe we've changed the example, other than configuring it to CPU1_RAM.

    Best Regards,

    Ankur Aggarwal

  • Ankur,

    Thank you for the info.

    Anu is OOO today.  She will get back to you in a day or two.

    Thanks and regards,
    Vamsi

  • Hi Ankur, 

    What is your clock source on your custom board?

    You can try the following two things: 

    1. Run the flash kernel example on a launchpad or CC and see if you get any issues. 

    2. Run the sci_ex4_echoback example with your custom board and have the autobaud lock enabled. This will help narrow down whether autobaud lock is working. 

    Thanks, 

    Anu

  • Hi Anu,

    Thanks again for your response!

    1. We use the internal oscillator of the TMS320F280049C chip itself.

    2. The strange thing about the autobaud lock is that it only seems to work with the built-in bootloader that's already in the ROM, but not with the flash kernel once that appears to have been loaded into RAM. Is that something you've seen before, and have recommendations on how to fix?

    3. I'm going to look into setting this up on our Launchpad boards. In the mean time, can you please let us know if these are the appropriate parts for the CC solution?

    https://www.mouser.com/ProductDetail/Texas-Instruments/TMDSHSECDOCK?qs=%2Fha2pyFadujs5cHMYWRkT4lBSTb4GdS9V2O%2FdrqvzmkSOjF%252BEpsZ%252Bg%3D%3D

    https://www.ti.com/tool/TMDSCNCD280049C#supported-products

    These two seem to be in stock.

    I also found this unit being recommended for serial connections:

    https://www.ti.com/tool/TMDSFSIADAPEVM#included

    However, this one is not in stock. Do you think it is strictly required, if we already have a custom host control board from which we can wire over UART signals?

    Best Regards,

    Ankur A.

  • Ankur, 

    The example is configured to run with the external oscillator. You can change the clock source in the example to run with the internal oscillator, this may help resolve your issue. Section 3.7.11 of the TRM shows how to configure the INTOSC as the clock source.

    The CC and docking station look fine, you do not need the additional resource you linked. 

    Thanks, 

    Anu

  • Anu, 

    This clock issue was a huge find! I'm able to do some basic GPIO toggling after making what looks like the changes recommended in that section you indicated, so that's definitely progress that helps me move forward.

    If you don't mind, I'm going to continue to keep this channel open just in case I run into further issues, but this is definitely the right start! 

    Best Regards,

    Ankur Aggarwal

  • Ankur, 

    Glad you are able to make some progress, and sure if you have further flash kernel related issues you can post them here, if they are related to something else go ahead and start a new thread. 

    Thanks, 

    Anu

  • Hi Anu,

    So I'm able to load what I think is a working flash kernel over UART. As I send data over it, though, the behavior I get back, as shown in the image, is a little strange:

    1) I see the autobaud character echoed,

    2) then I send the packet, 3) then I receive 0xA5,

    4) then a long time later (100ms?), well after I send the second packet, I just get the header byte echoed

    5) ~30-45ms later after the header, I receive what looks like the status packet.

    Is this right? If not, what should I actually be expecting, and what might likely explain the observed behavior on the logic analyzer?

    Best Regards,

    Ankur Aggarwal

  • Quick Update:

    As you can see, I can now get a status packet with an address of 0x12345678, which according to the document appears to be a good thing. However, I'm not 100% sure how to interpret the earlier part of the packet, after the header and length (0x65 0x00 0x00 0x50).

    Also, what does it mean to get a NAK instead of an ACK as a response?

    Best Regards,

    Ankur A.

  • Ankur, 

    What commands are you sending in the first screenshot? 

    In the second screenshot, after the header and length are sent by the kernel, the command and status are sent, this is likely what you are seeing. 

    If a NAK is received, it means that some portion of a packet may not have been received by the host correctly. 

    Thanks, 

    Anu

  • Hi Anu,

    Thanks for your response!

    In both instances, I'm attempting to send an erase command to CPU1.

    However, if I'm seeing both a NAK and a 0x5000 for status, that tracks that there may be an error. But then how can I be receiving 0x12345678 for address?

    Also, I don't see how my command is being reflected in the received packet? 0x0065 does not correspond to any of the commands per this document:

    http://file.elecfans.com/web1/M00/00/0E/o4YBAFnLrxKATROGAAYPkh4x3QU718.pdf

    I'm wondering if any timing issues are lingering. Do you have any recommendations on how to sanity check that I configured my clock correctly? Furthermore, do you have any other thoughts on what might be happening?

    Best Regards,

    Ankur

  • Ankur, 

    I will check with a clock expert on what checks you can perform to make sure the clock is configured correctly and get back to you in a day or so. I am not really sure why the behavior you described is occurring, have you been able to run the example on a CC and see what the logic analyzer shows? Is your host side sending commands in the same manner that the host side programmer in C2000Ware is?

    Thanks, 

    Anu

  • Update:

    I am finally able to get a proper ACK character. The issue was my checksum computation.

    Best Regards,

    Ankur

  • Further update:

    When I send the DFU command (total length of 10, data length of 0, since data comes after), I get an 0xA5 (NAK). Is my packet constructed correctly?

    Best Regards,

    Ankur

  • Sorry, here's the image:

  • Ankur, 

    Can you share what your clock configuration looks like? After changing the clock source to the internal oscillator, did you change your IMULT value accordingly? 

    For your question regarding the DFU command, it looks correct. In general for sending commands, are you following the functions found in the serial_flash_programmer utility? You can find the source code for the utility in C2000Ware_x_xx_xx_xx\utilities\flash_programmers\serial_flash_programmer\serial_flash_programmer\source. 

    Thanks, 

    Anu

  • Hi Anu,

    My clock configuration is as follows:

    #define DEVICE_SETCLOCK_CFG         (SYSCTL_OSCSRC_OSC2 | SYSCTL_IMULT(0x13) |  \
                                         SYSCTL_FMULT_1_4 | SYSCTL_SYSDIV(2) |   \
                                         SYSCTL_PLL_ENABLE)
    I think I am nearing the home stretch.
    I am sending my data in blocks, but I haven't quite gotten the DFU to work. I am terminating my procedure with a call to "run" as shown below.
    Is the Run packet (14 bytes) constructed correctly?
    Am I also supposed to wait for a status packet from either DFU or RUN? If so, how long do I wait? And is there a handshake that I need to send in between blocks, such as echoing the checksum that comes back?
    Best Regards,
    Ankur
  • Ankur, 

    The Run packet looks correct. 

    After each command, the kernel sends back a packet with information about the packet. To see how the host side receives this packet, you can refer to the getPacket function found in f021_SendMessage.cpp in the source files for the serial_flash_prgrammer host utility found in C2000Ware. The host side just takes in the data from the kernel and prints to the console if errors were detected in the packet. 

    For the clock configuration, what clock frequency are you aiming for?

    Thanks, 

    Anu

  • Hi Anu,

    I guess the clock speed I  was going for was 100MHz? Not super committed to that particular number, though.

    I guess to be more specific, do I need to Ack every checksum that comes back from the kernel?

    More broadly, I'm sending the entire application, followed by 00 (as shown), followed by the run packet, but the application is not in fact running. Assuming the application file has been constructed correctly, what is the next place to look as far as debugging is concerned?

    Thanks,

    Ankur

  • Ankur, 

    The application file should have the block of 00 00 at the end of the file needed to signal to the kernel that the file transmission is complete. There should be no need to send another 00 from the host between the application and the run command. Once the application is finished being transmitted, the kernel should send a status packet. As a part of this status packet, there will be checksums sent and after each byte of the checksum, the kernel waits for an ACK. On the host side in the programmer utility, the checksum is received in bytes and after each byte, the host sends an ACK. 

    To check whether the clock speed is at 100 MHz, you can check whether the values you are plugging into the DEVICE_SETCLOCK_CFG value equal 100 MHz. The formula should be commented above the define. 

    Thanks,

    Anu

  • In addition, have you had the chance to run the example on a CC? That will be a good baseline to compare your program against and will help with pinpointing any transmission issues you are having since you can set breakpoints on the target and host side. 

    Thanks, 

    Anu

  • I just got the Control Card today and tried using it. I've configured the S1:A and S1 switches as shown in the image (what the documentation suggests is required for UART communication).

    But when I try the command, I get stuck during autobaud, even though pin 76 (SCIRX) on the docking station pulls high according to the oscilloscope!

    C:\ti\C2000Ware_MotorControl_SDK_3_02_00_00\c2000ware\utilities\flash_programmers\serial_flash_programmer>serial_flash_programmer.exe -d f28004x -k ./f28004x_fw_upgrade_example/flashapi_ex2_sci_kernel.txt -a ./f28004x_fw_upgrade_example/led_ex1_blinky.txt -p COM9 -b 9600 -v
    C2000 Serial Firmware Upgrader
    Copyright (c) 2013 Texas Instruments Incorporated.  All rights reserved.
    getting comm state
    building comm DCB
    adjusting port settings
    calling f021_DownloadKernel CPU1 Kernel
    Downloading ./f28004x_fw_upgrade_example/flashapi_ex2_sci_kernel.txt to device...
    Attempting autobaud to load kernel...
    Can you please tell me what's going on and how to fix this? I'd like to get a working example to compare what's happening on the logic analyzer in order to figure out a solution for my custom board.
    Best Regards,
    Ankur A.
  • Ok, followup:

    1) I got the control card working. I think there was an issue with how the CC was sitting in the docking station. Because I think it was loose.

    2) I got it working on my custom board, too, by observing how the protocol works in a known example. As it turns out, one needs to respond with an ACK to *every single byte* that comes back after the flash kernel is downloaded and autobaud is resumed, as well as an extra ACK after the DFU response comes back.

    Hopefully this thread proves useful to future onlookers wanting to set up a similar project.

    Thanks for all your help!

    Best Regards,

    Ankur Aggarwal