Hi,
I found the post below very interesting
https://e2e.ti.com/blogs_/b/powerhouse/posts/how-to-improve-power-factor-correction-with-dff
I would like to know if Texas has released any C2000 kits or application notes that use DFF control?
Please see TIDM-HV-1PH-DCAC on ti.com
The control diagram shows the feed-forward control
Shamim
Shamin,
The documentation of the tidm-1000 (tiducj0g.pdf)
in equation 13 (6.4.2)
duty1PU = ( ( iL1Meas - iL1Ref ) * Gi_GainKp + v1Meas) / vBusHalfMeas
I don't understand why duty cycle feedforward is v1Meas/VbusHalfMeas. In this case the duty is smaller when V1Meas is small in relation to Vbus. Shouldn't it be (Vbus - V1meas)/Vbus? So that Duty is bigger when V1meas is smaller?
This equation comes from the current loop model shown in Fig 5, page 9. You should be able to derive this by looking at the diagram.
When output volt (V1Meas) is smaller then duty is smaller because Vbus is constant.
Shamim