Part Number: TMS320F28386D
AUTOSAR requires the Pwm_DeInit.
One question, Does TI provide the simple way to reset the registers to the default value?

This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Part Number: TMS320F28386D
AUTOSAR requires the Pwm_DeInit.
One question, Does TI provide the simple way to reset the registers to the default value?

Hi,
Really sorry for the delay in response.
To answer the question, we don't have a specific function which deinitializes all the registers to default value, but if incase you would wish to stop the PWM, you can choose to turn off the TBCLKSYNC bit which is the PWM clock enable / disable bit.
Also, there are individual bit / register level functions which you can use to configure the register back to the default value.
I hope this helps.
Regards,
Aditya