LAUNCHXL-F280049C: CAN Transmission Issue
Part Number: LAUNCHXL-F280049C
Hello E2E Experts,
We use three LAUNCHXL-F280049C to combine their CAN bus together. One or to CAN bus will be shut down . CAN use polled communication without using interrupts.When configure CAN ,set ABO=0. IF we set ABO=1 communicate is normal .There will be no bus shutdown. We would like to know whether the CAN bus will be shutdown when Auto-Bus-On is disable.On the PCB F280049 that we designed ,there is the same problem. At first,we suspecte it was a hardware issue.Later ,when we switched to the LAUNCHXL-F280049C the proble persisted. It seems to be related to the software configure.
we use LAUNCHXL-F280049C Debuger shows that the error register of CAN inidicates excessive TEC(CAN_ERRC).
The relevant code for the CAN section is provided in the attachment.
TICSC
  • Hello E2E Experts, I hope you can help US. Thank you very much
  • Hello Wang,
    Bit timing setup shows the baud rate at 125Kbps.  Can you provide more details on the problem/setup:
    1.) What is the main source of device clock (internal oscillator or external clock) and what is SYSCLK configured to?  What is the clock configuration?
    2.) Error is coming from transmission that is causing the node to go bus off.  Can you provide CAN frame waveform when node starts transmitting frames?
    Joseph
  • yes we can use 125kbps
    1 we use external clock
    // FILE:   f28004x_sysctrl.c
    // TITLE:  f28004x Device System Control Initialization & Support Functions.
    // DESCRIPTION:  Example initialization of system resources.
    // $Copyright:
    // Copyright (C) 2022 Texas Instruments Incorporated - http://www.ti.com/
    // Redistribution and use in source and binary forms, with or without
    // modification, are permitted provided that the following conditions
    // are met:
    //   Redistributions of source code must retain the above copyright
    //   notice, this list of conditions and the following disclaimer.
    //   Redistributions in binary form must reproduce the above copyright
    //   notice, this list of conditions and the following disclaimer in the
    //   documentation and/or other materials provided with the
    //   distribution.
    //   Neither the name of Texas Instruments Incorporated nor the names of
    //   its contributors may be used to endorse or promote products derived
    //   from this software without specific prior written permission.
    // THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS
    // "AS IS" AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT
    // LIMITED TO, THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR
    // A PARTICULAR PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT
    // OWNER OR CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL,
    // SPECIAL, EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT
    // LIMITED TO, PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE,
    // DATA, OR PROFITS; OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY
    // THEORY OF LIABILITY, WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT
    // (INCLUDING NEGLIGENCE OR OTHERWISE) ARISING IN ANY WAY OUT OF THE USE
    // OF THIS SOFTWARE, EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
    // Included Files
    #include "f28004x_device.h"     // Headerfile Include File
    #include "f28004x_examples.h"   // Examples Include File
    #include "device.h"
    #ifdef __cplusplus
    using std::memcpy;
    #endif
    // Functions that will be run from RAM need to be assigned to
    // a different section.  This section will then be mapped to a load and
    // run address using the linker cmd file.
    // *IMPORTANT*
    // IF RUNNING FROM FLASH, PLEASE COPY OVER THE SECTION ".TI.ramfunc"  FROM FLASH
    // TO RAM PRIOR TO CALLING InitSysCtrl(). THIS PREVENTS THE MCU FROM THROWING
    // AN EXCEPTION WHEN A CALL TO DELAY_US() IS MADE.
    #ifndef __cplusplus
    #pragma CODE_SECTION(InitFlash, ".TI.ramfunc");
    #pragma CODE_SECTION(FlashOff, ".TI.ramfunc");
    #endif
    // The following values are used to validate PLL Frequency using DCC
    #define   PLL_RETRIES              100
    #define   PLL_LOCK_TIMEOUT        2000
    #define   DCC_COUNTER0_WINDOW      100
    // Macro used for adding delay between 2 consecutive writes to CLKSRCCTL1
    // register.
    // Delay = 300 NOPs
    #define SYSCTRL_CLKSRCCTL1_DELAY  asm(" RPT #250 || NOP \n RPT #50 || NOP")
    #define _FLASH
    // InitSysCtrl - Initialization of system resources.
    void
    InitSysCtrl(void)
        // Disable the watchdog
        DisableDog();
    #ifdef _FLASH
        // Copy time critical code and Flash setup code to RAM
        // This includes the following functions:  InitFlash();
        // The  RamfuncsLoadStart, RamfuncsLoadSize, and RamfuncsRunStart
        // symbols are created by the linker. Refer to the device .cmd file.
        memcpy(&RamfuncsRunStart, &RamfuncsLoadStart, (size_t)&RamfuncsLoadSize);
        // Call Flash Initialization to setup flash waitstates
        // This function must reside in RAM
        InitFlash();
    #endif
        // PLLSYSCLK = (XTAL_OSC) * (IMULT + FMULT) / (PLLSYSCLKDIV)
    #ifdef _LAUNCHXL_F280049C
        InitSysPll(XTAL_OSC,IMULT_10,FMULT_0,PLLCLK_BY_2);//崔幔XTAL_OSC
    #else
        InitSysPll(XTAL_OSC_SE,IMULT_10,FMULT_0,PLLCLK_BY_2);//崔幔XTAL_OSC
    #endif
    #ifndef _FLASH
        // Call Device_cal function when run using debugger
        // This function is called as part of the Boot code. The function is called
        // in the InitSysCtrl function since during debug time resets, the boot code
        // will not be executed and the gel script will reinitialize all the
        // registers and the calibrated values will be lost.
        Device_cal();
    #endif
        // Turn on all peripherals
        InitPeripheralClocks();
    // InitPeripheralClocks - This function initializes the clocks for the
    // peripherals. Note: In order to reduce power consumption, turn off the
    // clocks to any peripheral that is not specified for your part-number or is
    // not used in the application
    void
        EALLOW;
        ClkCfgRegs.LOSPCP.all= 0x0002;//崔幔  低速时钟25M   100M\2*N
        CpuSysRegs.PCLKCR0.bit.CLA1 = 1;
        CpuSysRegs.PCLKCR0.bit.DMA = 1;
        CpuSysRegs.PCLKCR0.bit.CPUTIMER0 = 1;
        CpuSysRegs.PCLKCR0.bit.CPUTIMER1 = 1;
        CpuSysRegs.PCLKCR0.bit.CPUTIMER2 = 1;
        CpuSysRegs.PCLKCR0.bit.HRPWM = 1;
    //    CpuSysRegs.PCLKCR0.bit.TBCLKSYNC = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM1 = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM2 = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM3 = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM4 = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM5 = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM6 = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM7 = 1;
        CpuSysRegs.PCLKCR2.bit.EPWM8 = 1;
        CpuSysRegs.PCLKCR3.bit.ECAP1 = 1;
        CpuSysRegs.PCLKCR3.bit.ECAP2 = 1;
        CpuSysRegs.PCLKCR3.bit.ECAP3 = 1;
        CpuSysRegs.PCLKCR3.bit.ECAP4 = 1;
        CpuSysRegs.PCLKCR3.bit.ECAP5 = 1;
        CpuSysRegs.PCLKCR3.bit.ECAP6 = 1;
        CpuSysRegs.PCLKCR3.bit.ECAP7 = 1;
        CpuSysRegs.PCLKCR4.bit.EQEP1 = 1;
        CpuSysRegs.PCLKCR4.bit.EQEP2 = 1;
        CpuSysRegs.PCLKCR6.bit.SD1 = 1;
        CpuSysRegs.PCLKCR7.bit.SCI_A = 1;
        CpuSysRegs.PCLKCR7.bit.SCI_B = 1;
        CpuSysRegs.PCLKCR8.bit.SPI_A = 1;
        CpuSysRegs.PCLKCR8.bit.SPI_B = 1;
        CpuSysRegs.PCLKCR9.bit.I2C_A = 1;
        CpuSysRegs.PCLKCR10.bit.CAN_A = 1;
        CpuSysRegs.PCLKCR10.bit.CAN_B = 1;
        CpuSysRegs.PCLKCR13.bit.ADC_A = 1;
        CpuSysRegs.PCLKCR13.bit.ADC_B = 1;
        CpuSysRegs.PCLKCR13.bit.ADC_C = 1;
        CpuSysRegs.PCLKCR14.bit.CMPSS1 = 1;
        CpuSysRegs.PCLKCR14.bit.CMPSS2 = 1;
        CpuSysRegs.PCLKCR14.bit.CMPSS3 = 1;
        CpuSysRegs.PCLKCR14.bit.CMPSS4 = 1;
        CpuSysRegs.PCLKCR14.bit.CMPSS5 = 1;
        CpuSysRegs.PCLKCR14.bit.CMPSS6 = 1;
        CpuSysRegs.PCLKCR14.bit.CMPSS7 = 1;
        CpuSysRegs.PCLKCR15.bit.PGA1 = 1;
        CpuSysRegs.PCLKCR15.bit.PGA2 = 1;
        CpuSysRegs.PCLKCR15.bit.PGA3 = 1;
        CpuSysRegs.PCLKCR15.bit.PGA4 = 1;
        CpuSysRegs.PCLKCR15.bit.PGA5 = 1;
        CpuSysRegs.PCLKCR15.bit.PGA6 = 1;
        CpuSysRegs.PCLKCR15.bit.PGA7 = 1;
        CpuSysRegs.PCLKCR18.bit.FSIRX_A = 1;
        CpuSysRegs.PCLKCR18.bit.FSITX_A = 1;
        CpuSysRegs.PCLKCR16.bit.DAC_A = 1;
        CpuSysRegs.PCLKCR16.bit.DAC_B = 1;
        CpuSysRegs.PCLKCR19.bit.LIN_A = 1;
        CpuSysRegs.PCLKCR20.bit.PMBUS_A = 1;
        CpuSysRegs.PCLKCR21.bit.DCC_0 = 1;
        EDIS;
    // DisablePeripheralClocks -
    void
    DisablePeripheralClocks()
        EALLOW;
        CpuSysRegs.PCLKCR0.all = 0;
        CpuSysRegs.PCLKCR2.all = 0;
        CpuSysRegs.PCLKCR3.all = 0;
        CpuSysRegs.PCLKCR4.all = 0;
        CpuSysRegs.PCLKCR6.all = 0;
        CpuSysRegs.PCLKCR7.all = 0;
        CpuSysRegs.PCLKCR8.all = 0;
        CpuSysRegs.PCLKCR9.all = 0;
        CpuSysRegs.PCLKCR10.all = 0;
        CpuSysRegs.PCLKCR13.all = 0;
        CpuSysRegs.PCLKCR14.all = 0;
        CpuSysRegs.PCLKCR15.all = 0;
        CpuSysRegs.PCLKCR16.all = 0;
        CpuSysRegs.PCLKCR18.all = 0;
        CpuSysRegs.PCLKCR19.all = 0;
        CpuSysRegs.PCLKCR20.all = 0;
        CpuSysRegs.PCLKCR21.all = 0;
        EDIS;
    // InitFlash - This function initializes the Flash Control registers
    //                  CAUTION
    // This function MUST be executed out of RAM. Executing it
    // out of OTP/Flash will yield unpredictable results
    #ifdef __cplusplus
    #pragma CODE_SECTION(".TI.ramfunc");
    #endif
    void
    InitFlash(void)
        EALLOW;
        // At reset bank and pump are in sleep
        // A Flash access will power up the bank and pump automatically
        // Power up Flash bank and pump and this also sets the fall back mode of
        // flash and pump as active
        Flash0CtrlRegs.FPAC1.bit.PMPPWR = 0x1;
        Flash0CtrlRegs.FBFALLBACK.bit.BNKPWR0 = 0x3;
        Flash0CtrlRegs.FBFALLBACK.bit.BNKPWR1 = 0x3;
        // Disable Cache and prefetch mechanism before changing wait states
        Flash0CtrlRegs.FRD_INTF_CTRL.bit.DATA_CACHE_EN = 0;
        Flash0CtrlRegs.FRD_INTF_CTRL.bit.PREFETCH_EN = 0;
        // Set waitstates according to frequency
        //                CAUTION
        // Minimum waitstates required for the flash operating
        // at a given CPU rate must be characterized by TI.
        // Refer to the datasheet for the latest information.
    #if CPU_FRQ_100MHZ
        if((ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL == 0x0)   ||
           (ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL == 0x2)   ||
           (ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL == 0x3))
            Flash0CtrlRegs.FRDCNTL.bit.RWAIT = 0x5;
        else
            Flash0CtrlRegs.FRDCNTL.bit.RWAIT = 0x4;
    #endif
        // Enable Cache and prefetch mechanism to improve performance
        // of code executed from Flash.
        Flash0CtrlRegs.FRD_INTF_CTRL.bit.DATA_CACHE_EN = 1;
        Flash0CtrlRegs.FRD_INTF_CTRL.bit.PREFETCH_EN = 1;
        // At reset, ECC is enabled. If it is disabled by application software
        // and if application again wants to enable ECC
        Flash0EccRegs.ECC_ENABLE.bit.ENABLE = 0xA;
        EDIS;
        // Force a pipeline flush to ensure that the write to
        // the last register configured occurs before returning.
        __asm(" RPT #7 || NOP");
    // FlashOff - This function powers down the flash
    //                   CAUTION
    // out of OTP/Flash will yield unpredictable results.
    // Note: a flash access after the flash pump and banks are powered down will
    // wake the pump and bank
    #ifdef __cplusplus
    #endif
    void
    FlashOff(void)
        EALLOW;
        // Configure the fallback power mode as sleep
        Flash0CtrlRegs.FBFALLBACK.bit.BNKPWR0 = 0;
        Flash0CtrlRegs.FBFALLBACK.bit.BNKPWR1 = 0;
        Flash0CtrlRegs.FPAC1.bit.PMPPWR = 0;
        EDIS;
    // ServiceDog - This function resets the watchdog timer.
    // Enable this function for using ServiceDog in the application
    void
    ServiceDog(void)
        EALLOW;
        WdRegs.WDKEY.bit.WDKEY = 0x0055;
        WdRegs.WDKEY.bit.WDKEY = 0x00AA;
        EDIS;
    // DisableDog - This function disables the watchdog timer.
    void
    DisableDog(void)
        volatile Uint16 temp;
        EALLOW;
        // Grab the clock config so we don't clobber it
        temp = WdRegs.WDCR.all & 0x0007;
        WdRegs.WDCR.all = 0x0068 | temp;
        EDIS;
    void EnableDog(void)
        EALLOW;
        WdRegs.WDCR.all = 0x002FU;
        EDIS;
    // InitPll - This function initializes the PLL registers.
    // Note: This function uses the DCC to check that the PLLRAWCLK is running at
    // the expected rate. If you are using the DCC, you must back up its
    // configuration before calling this function and restore it afterward.
    void
    InitSysPll(Uint16 clock_source, Uint16 imult, Uint16 fmult, Uint16 divsel)
        Uint32 timeout, retries, temp_syspllmult, pllLockStatus;
        bool status;
        if(((clock_source & 0x3) == ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL)    &&
           (((clock_source & 0x4) >> 2) == ClkCfgRegs.XTALCR.bit.SE)           &&
                         (imult  == ClkCfgRegs.SYSPLLMULT.bit.IMULT)           &&
                         (fmult  == ClkCfgRegs.SYSPLLMULT.bit.FMULT)           &&
                         (divsel == ClkCfgRegs.SYSCLKDIVSEL.bit.PLLSYSCLKDIV))
            // Everything is set as required, so just return
            return;
        if(((clock_source & 0x3) != ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL) ||
           (((clock_source & 0x4) >> 2) != ClkCfgRegs.XTALCR.bit.SE))
            switch (clock_source)
                case INT_OSC1:
                    SysIntOsc1Sel();
                    break;
                case INT_OSC2:
                    SysIntOsc2Sel();
                    break;
                case XTAL_OSC:
                    SysXtalOscSel();
                    break;
                case XTAL_OSC_SE:
                    SysXtalOscSESel();
                    break;
        EALLOW;
        // First modify the PLL multipliers
        if(imult != ClkCfgRegs.SYSPLLMULT.bit.IMULT ||
           fmult != ClkCfgRegs.SYSPLLMULT.bit.FMULT)
            // Bypass PLL and set dividers to /1
            ClkCfgRegs.SYSPLLCTL1.bit.PLLCLKEN = 0;
            // Delay of at least 60 OSCCLK cycles required post PLL bypass
            asm(" RPT #60 || NOP");
            ClkCfgRegs.SYSCLKDIVSEL.bit.PLLSYSCLKDIV = 0;
            // Evaluate PLL multipliers
            temp_syspllmult = ((fmult << 8U) | imult);
            // Loop to retry locking the PLL should the DCC module indicate
            // that it was not successful.
            for(retries = 0; (retries < PLL_RETRIES); retries++)
                EALLOW;
                // Disable SYSPLL (Turn off PLL)
                ClkCfgRegs.SYSPLLCTL1.bit.PLLEN = 0;
                // Atleast 60 cycle delay between powerdown to powerup
                // Program PLL multipliers
                ClkCfgRegs.SYSPLLMULT.all = temp_syspllmult;
                // Enable SYSPLL
                ClkCfgRegs.SYSPLLCTL1.bit.PLLEN = 1;
                timeout = PLL_LOCK_TIMEOUT;
                pllLockStatus = ClkCfgRegs.SYSPLLSTS.bit.LOCKS;
                // Wait for the SYSPLL lock
                while((pllLockStatus != 1) && (timeout != 0U))
                    timeout--;
                EDIS;
                status = IsPLLValid(clock_source, imult, fmult);
                // Check DCC Status, if no error break the loop
                if(status)
                    break;
        else
            status = true;
        if(status)
            EALLOW;
            // Set divider to produce slower output frequency to limit current increase
            if(divsel != PLLCLK_BY_126)
                ClkCfgRegs.SYSCLKDIVSEL.bit.PLLSYSCLKDIV = divsel + 1;
            else
                ClkCfgRegs.SYSCLKDIVSEL.bit.PLLSYSCLKDIV = divsel;
            // Enable PLLSYSCLK is fed from system PLL clock
            ClkCfgRegs.SYSPLLCTL1.bit.PLLCLKEN = 1;
            // Small 100 cycle delay
            asm(" RPT #100 || NOP");
            // Set the divider to user value
            EDIS;
    // CsmUnlock - This function unlocks the CSM. User must replace 0xFFFF's with
    // current password for the DSP.
    Uint16
    CsmUnlock()
        // Write to the key registers to unlock the device. The 0x0FFFFFFFF's
        // are dummmy passwords. User should replace them with the correct password
        // for the DSP.
        // Note: F28004x has default password keys which are not all 0xFFFFFFFF.
        // See DCSM chapter of Technical Reference Manual for default passwords.
        EALLOW;
        DcsmBank0Z1Regs.Z1_CSMKEY0 = 0xFFFFFFFF;
        DcsmBank0Z1Regs.Z1_CSMKEY1 = 0xFFFFFFFF;
        DcsmBank0Z1Regs.Z1_CSMKEY2 = 0xFFFFFFFF;
        DcsmBank0Z1Regs.Z1_CSMKEY3 = 0xFFFFFFFF;
        DcsmBank0Z2Regs.Z2_CSMKEY0 = 0xFFFFFFFF;
        DcsmBank0Z2Regs.Z2_CSMKEY1 = 0xFFFFFFFF;
        DcsmBank0Z2Regs.Z2_CSMKEY2 = 0xFFFFFFFF;
        DcsmBank0Z2Regs.Z2_CSMKEY3 = 0xFFFFFFFF;
        EDIS;
        return 0;
    // SysIntOsc1Sel - This function switches to Internal Oscillator 1 and turns
    // off all other clock sources to minimize power consumption
    void
    SysIntOsc1Sel (void)
        EALLOW;
        ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL = 2; // Clk Src = INTOSC1
        ClkCfgRegs.XTALCR.bit.OSCOFF=1;             // Turn off XTALOSC
        EDIS;
    // SysIntOsc2Sel - This function switches to Internal oscillator 2 from
    // External Oscillator and turns off all other clock sources to minimize
    // power consumption
    // NOTE: If there is no external clock connection, when switching from
    //       INTOSC1 to INTOSC2, EXTOSC and XLCKIN must be turned OFF prior
    //       to switching to internal oscillator 1
    void
    SysIntOsc2Sel (void)
        EALLOW;
        ClkCfgRegs.CLKSRCCTL1.bit.INTOSC2OFF=0;         // Turn on INTOSC2
        SYSCTRL_CLKSRCCTL1_DELAY;
        ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL = 0;     // Clk Src = INTOSC2
        EDIS;
    // PollX1Counter - Clear the X1CNT counter and then wait for it to saturate
    // four times.
    static void
    PollX1Counter(void)
        Uint16 loopCount = 0;
        // Delay for 1 ms while the XTAL powers up
        // 2000 loops, 5 cycles per loop + 9 cycles overhead = 10009 cycles
        F28x_usDelay(2000);
        // Clear and saturate X1CNT 4 times to guarantee operation
        do
            // Keep clearing the counter until it is no longer saturated
            while(ClkCfgRegs.X1CNT.all > 0x1FF)
                ClkCfgRegs.X1CNT.bit.CLR = 1;
            // Wait for the X1 clock to saturate
            while(ClkCfgRegs.X1CNT.all != 0x3FFU)
            // Increment the counter
            loopCount++;
        }while(loopCount < 4);
    // SysXtalOscSel - This function switches to External CRYSTAL oscillator and
    // turns off all other clock sources to minimize power consumption. This option
    // may not be available on all device packages
    void
    SysXtalOscSel (void)
        EALLOW;
        ClkCfgRegs.XTALCR.bit.OSCOFF = 0;     // Turn on XTALOSC
        ClkCfgRegs.XTALCR.bit.SE = 0;         // Select crystal mode
        EDIS;
        PollX1Counter();
        // Select XTAL as the oscillator source
        EALLOW;
        ClkCfgRegs.CLKSRCCTL1.bit.OSCCLKSRCSEL = 1;
        EDIS;
        // If a missing clock failure was detected, try waiting for the X1 counter
        // to saturate again. Consider modifying this code to add a 10ms timeout.
        while(ClkCfgRegs.MCDCR.bit.MCLKSTS != 0)
            EALLOW;
            ClkCfgRegs.MCDCR.bit.MCLKCLR = 1;
            EDIS;
            PollX1Counter();
            EALLOW;
            EDIS;
    // SysXtalOscSESel - This function switches to external oscillator in
    // single-ended mode and turns off all other clock sources to minimize power
    // consumption. This option may not be available on all device packages
    void
    SysXtalOscSESel (void)
        EALLOW;
        ClkCfgRegs.XTALCR.bit.SE = 1;         // Select single-ended mode
        EDIS;
        PollX1Counter();
        // Select XTALOSC as the oscillator source
        EALLOW;
        EDIS;
        // If missing clock detected, there is something wrong with the oscillator
        // module.
        if(ClkCfgRegs.MCDCR.bit.MCLKSTS != 0)
            ESTOP0;
    // IDLE - Enter IDLE mode
    void
    IDLE()
        EALLOW;
        CpuSysRegs.LPMCR.bit.LPM = LPM_IDLE;
        EDIS;
        asm(" IDLE");
    // HALT - Enter HALT mode
    void
    HALT()
        EALLOW;
        CpuSysRegs.LPMCR.bit.LPM = LPM_HALT;
        EDIS;
        asm(" IDLE");
    // SysCtl_isPLLValid()
    bool
    IsPLLValid(Uint16 oscSource, Uint16 imult, Uint16 fmult)
        Uint32 dccCounterSeed0, dccCounterSeed1, dccValidSeed0;
        // Setting Counter0 & Valid Seed Value with +/-12% tolerance
        dccCounterSeed0 = DCC_COUNTER0_WINDOW - 12U;
        dccValidSeed0 = 24U;
        // Multiplying Counter-0 window with PLL Integer Multiplier
        dccCounterSeed1 = DCC_COUNTER0_WINDOW * imult;
        // Multiplying Counter-0 window with PLL Fractional Multiplier
        switch(fmult)
            case FMULT_0pt25:
                // FMULT * CNTR0 Window = 0.25 * 100 = 25, gets added to cntr0
                // seed value
                dccCounterSeed1 = dccCounterSeed1 + 25U;
                break;
            case FMULT_0pt5:
                // FMULT * CNTR0 Window = 0.5 * 100 = 50, gets added to cntr0
                // seed value
                dccCounterSeed1 = dccCounterSeed1 + 50U;
                break;
            case FMULT_0pt75:
                // FMULT * CNTR0 Window = 0.75 * 100 = 75, gets added to cntr0
                // seed value
                dccCounterSeed1 = dccCounterSeed1 + 75U;
                break;
            default:
                // No fractional multiplier
                dccCounterSeed1 = dccCounterSeed1;
                break;
        // Enable Peripheral Clock Domain PCLKCR21 for DCC
        EALLOW;
        // Clear Error & Done Flag
        Dcc0Regs.DCCSTATUS.bit.ERR = 1;
        Dcc0Regs.DCCSTATUS.bit.DONE = 1;
        // Disable DCC
        Dcc0Regs.DCCGCTRL.bit.DCCENA = 0x5;
        // Disable Error Signal
        Dcc0Regs.DCCGCTRL.bit.ERRENA = 0x5;
        // Disable Done Signal
        Dcc0Regs.DCCGCTRL.bit.DONEENA = 0x5;
        // Configure Clock Source0 to whatever is set as a clock source for PLL
        switch(oscSource)
            case INT_OSC1:
                Dcc0Regs.DCCCLKSRC0.bit.CLKSRC0 = 1; // Clk Src0 = INTOSC1
                break;
            case INT_OSC2:
                Dcc0Regs.DCCCLKSRC0.bit.CLKSRC0 = 2; // Clk Src0 = INTOSC2
                break;
            case XTAL_OSC:
            case XTAL_OSC_SE:
                Dcc0Regs.DCCCLKSRC0.bit.CLKSRC0 = 0; // Clk Src0 = XTAL
                break;
        // Configure Clock Source1 to PLL
        Dcc0Regs.DCCCLKSRC1.bit.KEY = 0xA; // Clk Src1 Key to enable clock source selection for count1
        Dcc0Regs.DCCCLKSRC1.bit.CLKSRC1 = 0; // Clk Src1 = PLL
        // Configure COUNTER-0, COUNTER-1 & Valid Window
        Dcc0Regs.DCCCNTSEED0.bit.COUNTSEED0 = dccCounterSeed0; // Loaded Counter0 Value
        Dcc0Regs.DCCVALIDSEED0.bit.VALIDSEED = dccValidSeed0;  // Loaded Valid Value
        Dcc0Regs.DCCCNTSEED1.bit.COUNTSEED1 = dccCounterSeed1; // Loaded Counter1 Value
        // Enable Single Shot Mode
        Dcc0Regs.DCCGCTRL.bit.SINGLESHOT = 0xA;
        // Enable Error Signal
        Dcc0Regs.DCCGCTRL.bit.ERRENA = 0xA;
        // Enable Done Signal
        Dcc0Regs.DCCGCTRL.bit.DONEENA = 0xA;
        // Enable DCC to start counting
        Dcc0Regs.DCCGCTRL.bit.DCCENA = 0xA;
        EDIS;
        // Set time out for the loop
        uint32_t timeout = dccCounterSeed1;
        // Wait until Error or Done Flag is generated
        while(((Dcc0Regs.DCCSTATUS.all & 3) == 0) && (timeout != 0U))
            timeout--;
        // Returns true if DCC completes without error
        return(((Dcc0Regs.DCCSTATUS.all & 3) == 2) && (Dcc0Regs.DCCCNT0.all == 0) &&
               (Dcc0Regs.DCCVALID0.all == 0) && (Dcc0Regs.DCCCNT1.all == 0));
    // End of File
    2 now we only have normal communication Waveform
  • Hello Wang,
    Thank you for sending the CAN frame.  I do not see any anomalies on the waveform but i cannot see if ACK has been sent by the receiving node based on the picture.  Can you zoom in near the CRC field and see if there is an ACK bit?  Also once the first frame is sent by the transmitting node, can you immediately stop (break point) and display the CAN_ES register content?
    Just to clarify, the use case that is failing is SYCLK = 100MHz and CAN Bit Timing is set to 125Kbps, correct?
    I do not see any issues with the external clock configuration to produce the 100MHz SYSCLK for the chip.
    Thanks and regards,
    Joseph
  • I wasn't able to reply in time today because I had to deal with some other matters.
    I wonder if you have conducted the replication test? We don't experience immediate malfunction right after power-on and start communication. Instead, the CAN bus will be shut down after a certain period of time.
  • Hi Wang,
    Our validation tests connect several C28x including f28004x chips together through CAN bus with the tests running for several hours with no issue.  What is the length of the CAN bus that you are using?  Based from the previous CAN_ES log you have shared, it looks like there was a sudden increase in transmission error.  Do you have the ability to connect to the debugger to inspect other registers like RESC (reset cause register) to see if reset may have toggled?  Can you also check to see if SYSCLK is still configured at 100MHz?  There is no suspected cause yet as to why CAN communication fails after sometime for your case so just looking for clues on what might have caused this to happen.
    Joseph
  • The length of the CAN bus about 1m.The CAN bus matching resistance is 60 Ω.Because using CAN_ES_TXOK to determine whether the transmission is complete in three machines.We use CAN_IF1CMD_BUSY judge in the function vEcanDrive_TxDataBufferProcess is no problem.So we no doubt RESET or SYSCLK. In use CAN_IF1CMD_BUSY if we one time in multiple frames use the function of vEcanDrive_Push2TxDataBuffer will be Lose frame. In out all test the Auto-Bus-On is disable. If the Auto-Bus-On is enable We can't see CAN bus shutdown. CAN bus is actually in the state of the switch switch switch.
  • Understood your point on RESER and SYSCLK issue.  Auto-Bus On (ABO) enable is behaving correctly for your case.  When enabled, CAN automatically recovers from the bus off condition due to transmission errors.  Will enabling the ABO bit cause a problem in your application?
    Need to understand in your setup where the bus error is coming from.  Is there a CAN log you can look at to see the events happening in the bus before the bus off condition occurred?