Part Number: TMS320F280039C
Hello,
I am using TMS320F280039C and have a question about ADC Sample and Hold behavior on ADCC3.
PS_ON is an external switch signal and can be Low or Floating.
PS_ON is pulled up to 3.3 V through a 100 kohm resistor.
PS_ON_IN is used to sense PS_ON and is connected to ADC channel ADCC3 (ACQPS = 10).
Observed behavior is that when PS_ON is floating at 3.3 V and the main DCDC output (12V_main) turns off, PS_ON cannot maintain 3.3 V and temporarily drops close to 0 V, then rises again.
When PS_ON_IN is disconnected from the ADC pin (left open), PS_ON remains stable at 3.3 V.
This means the issue occurs only when ADCC3 is connected.

Based on the TRM input model for ADCC3, the total ADC input capacitance is about 11.3 pF and Ron is about 860 ohms.
With ACQPS = 10, the ADC Sample and Hold operation requires significantly more current than the 33 µA that can be supplied by a 100 kohm pull‑up.

My questions are:
Is it possible that the ADCC3 Sample and Hold operation or internal analog structure can discharge an externally pulled‑up signal during a power event such as main output turn‑off?
With a high source impedance (100 kohm pull‑up), is ADC input voltage droop an expected behavior?
What source impedance or circuit topology does TI recommend when sensing a status signal like PS_ON using the ADC?
Thank you for your support.