Hello,  on page 81 of the lab manual, where we calculate Ki,series(PU)=(Rs/Ls)*Ti=0.01428, but, when i ran the program, gMotorVars.Ki_Idq=0.0428, which is exactly 3 times the value I calculated.  I am lost, where did the "3" come from?

Another silly question.  I would like to measure the currents on the test points using an oscilloscope.  are the test points outputted from an A/D on the board? in other words, are they actually voltages that map current to volts? I do a lot of data acquisiton in my job, where (for example) 0-1 amp = 0-10 volts, where 1V=0.1A.  how do i actually connect the oscilloscope?  and the same for the PWM test points on the board.  Please help, i need to monitor the currents for Lab 5a, and other labs.

 

Thank you

  • check your variable values.

    The gains are calculated in calcPIgains() which you can see in proj_lab5a.c

     

    void calcPIgains(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;

      float_t Ls_d = EST_getLs_d_H(obj->estHandle);
      float_t Ls_q = EST_getLs_q_H(obj->estHandle);
      float_t Rs = EST_getRs_Ohm(obj->estHandle);
      float_t RoverLs_d = Rs/Ls_d;
      float_t RoverLs_q = Rs/Ls_q;
      float_t fullScaleCurrent = EST_getFullScaleCurrent(obj->estHandle);
      float_t fullScaleVoltage = EST_getFullScaleVoltage(obj->estHandle);
      float_t ctrlPeriod_sec = CTRL_getCtrlPeriod_sec(handle);
      _iq Kp_Id = _IQ((0.25*Ls_d*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Id = _IQ(RoverLs_d*ctrlPeriod_sec);

     

    I don't beleive the test points are hooked up to an MCU pin by default.  If you need to monitor the current I highly suggest a current probe.

    If you want to graph the values in CCS it's pretty simple to do. InstaSPIN-MOTION proj5f has an example of using the graphs.  You can also search the forum for examples of using the DLOG memory buffers to store data (which can be transmitted or graphed).   Unfortunately there isn't a functional example of datalogging a bunch of information.

    There is a 3rd party who should introduce a CAN solution this summer, and they will offer a data acquisition feature through CAN to the PC which should be nice.

     

  • Ti was miscalculated in the lab maunal.  USER_NUM_PWM_TICKS_PER_ISR_TICK also should be multiflied in the Ti calculation. In other words,

    Ti = (1/(USER_PWM_FREQ_KHz*1000)) * (USER_NUM_PWM_TICKS_PER_ISR_TICK) * (USER_NUM_ISR_TICKS_PER_CTRL_TICK)

         = (1/45000) * (3) * (1)

     

    You can measure the phase current at the IA-FB test point as below. However, the current will be looked pulse type because current is only captured during Low switch turn-on. 

    If you need DAC for current monitoring, you can also use DAC_PWM1(J5-22). Of course, you need to add some codes for DAC output. 

    I am not sure if this answer is what you are thinking or not.

    -Steve  

  • You're correct on the Ki documentation, we haven't updated since we added the PWM_TICKS variable.

    I've added that to our bug list to fix. Thanks.

     

  • Hi Chris,

    I followed lab5f to graph several vars, by adding codes:

    1. Define graphing Variables;

    2. Init graphing Variables (in main func);

    3. Store graphing values (in main ISR);

    My question is after doing these, how I write/develop my own .GraphProp file to be imported into CCS?? Just like what lab5f does.

     

  • Tools --> Graph

    click Export button to save the .GraphProp file

     

  • Chris,

    When selecting the vars to graph, in main ISR, I believe I should take care of the scaling for current and voltage so that they can be plotted in Amps and Volts, like:

    gMotorVars.Iq_A = _IQmpy(CTRL_getIq_in_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_CURRENT_A));

    gMotorVars.Vq = _IQmpy(CTRL_getVq_in_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_VOLTAGE_V));

    Then, do I need to do this to the speed(gMotorVars.Speed_krpm) and torque (gMotorVars.Torque_lbin)? Are the currents and voltages the only things need to be re-scaled like above?

  • The speed value can be "get" directly in KRPM

      // get the speed estimate
      gMotorVars.Speed_krpm = EST_getSpeed_krpm(obj->estHandle);

    The Torque however has a bug in the EST_getTorque function.  This has to be "get" by a calculation that takes quite a few cycles. You probably can't run this in your interrupt.

    Notice we moved in MW _12 to this:

      // get the torque estimate
      gMotorVars.Torque_lbin = calcTorque_lbin(handle);

    and the calcToruqe function is

    float_t calcTorque_Nm(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      float_t Id_A = _IQtoF(PID_getFbackValue(obj->pidHandle_Id)) * USER_IQ_FULL_SCALE_CURRENT_A;
      float_t Iq_A = _IQtoF(PID_getFbackValue(obj->pidHandle_Iq)) * USER_IQ_FULL_SCALE_CURRENT_A;
      float_t Polepairs = (float_t)USER_MOTOR_NUM_POLE_PAIRS;
      float_t Flux_Wb = EST_getFlux_Wb(obj->estHandle);
      float_t Lsd_H = EST_getLs_d_H(obj->estHandle);
      float_t Lsq_H = EST_getLs_q_H(obj->estHandle);

      return((Flux_Wb * Iq_A + (Lsd_H - Lsq_H) * Id_A * Iq_A) * Polepairs * 1.5);
    } // end of calcTorque_Nm() function

    float_t calcTorque_lbin(CTRL_Handle handle)
    {

      return(calcTorque_Nm(handle) * MATH_Nm_TO_lbin_SF);
    } // end of calcTorque_lbin() function

     

    We are looking for a fix for this as it is a nice feature to get a torque value from the estimator each estimator cycle...

     

  • I agree - the torq is one of what we care most generally.

    Two more questions for graph coding:

    1. Are all of currents and voltages need scaling then? For instance: 

    gMotorVars.Iq_A = _IQmpy(CTRL_getIq_in_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_CURRENT_A));

    gMotorVars.Vq = _IQmpy(CTRL_getVq_out_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_VOLTAGE_V));

    etc.

    2. The code you provided is for MotorWare 12, right?? My code above are from MotorWare 11, so I'm assuming this is the reason for the difference.

  • 1. Yes, these are the same equations. You don't HAVE to do the multiply and put it into full scale values. It takes up MIPS in your interrupt....it does make it easier to read I guess, but you can also just plot the _pu values and you will see everything in -1.0 to 1.0 scale.  Your choice.  With yoru F28069M @ 15 KHz you have plenty of MIPS to do these sort of things.

    2. Yes, that was copied from _12.  The torque calculation is new in _12, but the others should be the same from _11.

     

  • After a couple of successful graph of Id, Iq etc., I tried to add a new var. "Ia" to be graphed. But bunch of errors reported after building.

    What I did include:

    1. main.h: add "_iq Ia" in "typedef struct _MOTOR_Vars_t_"; add "_IQ(0.0), \" in "#define MOTOR_Vars_INIT";

    2. main.c: add "gMotorVars.Ia = CTRL_getIa_in_pu(ctrlHandle)" in main ISR;

    3. ctrl.h: add "inline _iq CTRL_getIa_in_pu(CTRL_Handle handle)" to return the Ia value from "CTRL_getIab_in_pu" which is in ctrl.c

    Is there anything I missed? Attaching the error report here...

  • 1. you don't HAVE to put Ia into the gMotorVars structure, but it's ok that you did

    2. if you are going to do this you need to set-up a CTRL_get function which you started to do in 3.

    but for a new function you need to set-up the address and create get and set functions.

    Is this just a value that you can pul from one of the existing functions? Is it one of these?

    void CTRL_getIab_in_pu(CTRL_Handle handle,MATH_vec2 *pIab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;

      pIab_in_pu->value[0] = obj->Iab_in.value[0];
      pIab_in_pu->value[1] = obj->Iab_in.value[1];

      return;
    }

  • 1. N/A

    2. The func you provided is already in ctrl.c and my func "CTRL_getIa_in_pu" in my 3 is based on that.

    Anyways, attaching my main.c, main.h, ctrl.c and ctrl.h here...

    /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
     * *  Neither the name of Texas Instruments Incorporated nor the names of
     *    its contributors may be used to endorse or promote products derived
     *    from this software without specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    
     
     
    //! \file   solutions/instaspin_motion/src/ctrl.c
    //! \brief  Contains the various functions related to the controller (CTRL) object
    //!
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    
    // **************************************************************************
    // the includes
    
    #include <math.h>
    
    
    // drivers
    
    
    // modules
    #include "sw/modules/dlog/src/32b/dlog4ch.h"
    #include "sw/modules/math/src/32b/math.h"
    
    
    // platforms
    #include "ctrl.h"
    #include "drv.h"
    #include "user.h"
    
    
    #ifdef FLASH
    #pragma CODE_SECTION(CTRL_run,"ramfuncs");
    #pragma CODE_SECTION(CTRL_setup,"ramfuncs");
    #endif
    
    
    // **************************************************************************
    // the defines
    
    
    // **************************************************************************
    // the globals
    
    
    // **************************************************************************
    // the function prototypes
    
    void CTRL_getGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       _iq *pKp,_iq *pKi,_iq *pKd)
    {
    
      *pKp = CTRL_getKp(handle,ctrlType);
      *pKi = CTRL_getKi(handle,ctrlType);
      *pKd = CTRL_getKd(handle,ctrlType);
    
      return;    
    } // end of CTRL_getGains() function
    
    
    void CTRL_getIab_filt_pu(CTRL_Handle handle,MATH_vec2 *pIab_filt_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_filt_pu->value[0] = obj->Iab_filt.value[0];
      pIab_filt_pu->value[1] = obj->Iab_filt.value[1];
    
      return;
    } // end of CTRL_getIab_filt_pu() function
    
    
    void CTRL_getIab_in_pu(CTRL_Handle handle,MATH_vec2 *pIab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_in_pu->value[0] = obj->Iab_in.value[0];
      pIab_in_pu->value[1] = obj->Iab_in.value[1];
    
      return;
    } // end of CTRL_getIab_in_pu() function
    
    
    void CTRL_getIdq_in_pu(CTRL_Handle handle,MATH_vec2 *pIdq_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_in_pu->value[0] = obj->Idq_in.value[0];
      pIdq_in_pu->value[1] = obj->Idq_in.value[1];
    
      return;
    } // end of CTRL_getIdq_in_pu() function
    
    
    void CTRL_getIdq_ref_pu(CTRL_Handle handle,MATH_vec2 *pIdq_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_ref_pu->value[0] = obj->Idq_ref.value[0];
      pIdq_ref_pu->value[1] = obj->Idq_ref.value[1];
    
      return;
    } // end of CTRL_getIdq_ref_pu() function
    
    
    _iq CTRL_getMagCurrent_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getIdRated_pu(handle));
    } // end of CTRL_getMagCurrent_pu() function
    
    
    _iq CTRL_getMaximumSpeed_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getSpd_max_pu(handle));
    } // end of CTRL_getMaximumSpeed_pu() function
    
    
    void CTRL_getVab_in_pu(CTRL_Handle handle,MATH_vec2 *pVab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_in_pu->value[0] = obj->Vab_in.value[0];
      pVab_in_pu->value[1] = obj->Vab_in.value[1];
    
      return;
    } // end of CTRL_getVab_in_pu() function
    
    
    void CTRL_getVab_out_pu(CTRL_Handle handle,MATH_vec2 *pVab_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_out_pu->value[0] = obj->Vab_out.value[0];
      pVab_out_pu->value[1] = obj->Vab_out.value[1];
    
      return;
    } // end of CTRL_getVab_out_pu() function
    
    
    void CTRL_getVdq_out_pu(CTRL_Handle handle,MATH_vec2 *pVdq_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVdq_out_pu->value[0] = obj->Vdq_out.value[0];
      pVdq_out_pu->value[1] = obj->Vdq_out.value[1];
    
      return;
    } // end of CTRL_getVdq_out_pu() function
    
    
    void CTRL_getWaitTimes(CTRL_Handle handle,uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          pWaitTimes[stateCnt] = obj->waitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_getWaitTimes() function
    
    
    void CTRL_run(CTRL_Handle handle,DRV_Handle drvHandle,
                  const DRV_AdcData_t *pAdcData,
                  DRV_PwmData_t *pPwmData)
    {
      uint_least16_t count_isr = CTRL_getCount_isr(handle);
      uint_least16_t numIsrTicksPerCtrlTick = CTRL_getNumIsrTicksPerCtrlTick(handle);
    
    
      // if needed, run the controller
      if(count_isr >= numIsrTicksPerCtrlTick)
        {
          CTRL_State_e ctrlState = CTRL_getState(handle);
    
          // reset the isr count
          CTRL_resetCounter_isr(handle);
    
          // increment the state counter
          CTRL_incrCounter_state(handle);
    
          // increment the trajectory count
          CTRL_incrCounter_traj(handle);
    
          // run the appropriate controller
          if(ctrlState == CTRL_State_OnLine)
            {
        	  CTRL_Obj *obj = (CTRL_Obj *)handle;
    
              // increment the current count
              CTRL_incrCounter_current(handle);
    
              // increment the speed count
              CTRL_incrCounter_speed(handle);
    
              if(EST_getState(obj->estHandle) >= EST_State_MotorIdentified)
                {
                  // run the online controller
                  CTRL_runOnLine_User(handle,pAdcData,pPwmData);
                }
              else
                {
                  // run the online controller
                  CTRL_runOnLine(handle,pAdcData,pPwmData);
                }
            }
          else if(ctrlState == CTRL_State_OffLine)
            {
              // run the offline controller
              CTRL_runOffLine(handle,drvHandle,pAdcData,pPwmData);
            }
        }
      else
        {
          // increment the isr count
          CTRL_incrCounter_isr(handle);
        }
    
      return;
    } // end of CTRL_run() function
    
    
    void CTRL_setGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       const _iq Kp,const _iq Ki,const _iq Kd)
    {
    
      CTRL_setKp(handle,ctrlType,Kp);
      CTRL_setKi(handle,ctrlType,Ki);
      CTRL_setKd(handle,ctrlType,Kd);
    
      return;    
    } // end of CTRL_setGains() function
    
    
    void CTRL_setMagCurrent_pu(CTRL_Handle handle,const _iq magCurrent_pu)
    {
    
      CTRL_setIdRated_pu(handle,magCurrent_pu);
    
      return;    
    } // end of CTRL_setMagCurrent_pu() function
    
    
    void CTRL_setMaximumSpeed_pu(CTRL_Handle handle,const _iq maxSpeed_pu)
    {
    
      CTRL_setSpd_max_pu(handle,maxSpeed_pu);
    
      return;    
    } // end of CTRL_setMaximumSpeed_pu() function
    
    
    void CTRL_setParams(CTRL_Handle handle,USER_Params *pUserParams)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq Kp,Ki,Kd;
      _iq outMin,outMax;
      _iq maxModulation;
    
      MATH_vec2 Iab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_ref_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_in_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vdq_out_pu = {_IQ(0.0),_IQ(0.0)};
    
    
      // assign the motor type
      CTRL_setMotorParams(handle,pUserParams->motor_type,
                          pUserParams->motor_numPolePairs,
                          pUserParams->motor_ratedFlux,
                          pUserParams->motor_Ls_d,
                          pUserParams->motor_Ls_q,
                          pUserParams->motor_Rr,
                          pUserParams->motor_Rs);
    
    
      // assign other controller parameters
      CTRL_setNumIsrTicksPerCtrlTick(handle,pUserParams->numIsrTicksPerCtrlTick);
      CTRL_setNumCtrlTicksPerCurrentTick(handle,pUserParams->numCtrlTicksPerCurrentTick);
      CTRL_setNumCtrlTicksPerSpeedTick(handle,pUserParams->numCtrlTicksPerSpeedTick);
      CTRL_setNumCtrlTicksPerTrajTick(handle,pUserParams->numCtrlTicksPerTrajTick);
    
      CTRL_setCtrlFreq_Hz(handle,pUserParams->ctrlFreq_Hz);
      CTRL_setTrajFreq_Hz(handle,pUserParams->trajFreq_Hz);
      CTRL_setTrajPeriod_sec(handle,_IQ(1.0/pUserParams->trajFreq_Hz));
    
      CTRL_setCtrlPeriod_sec(handle,pUserParams->ctrlPeriod_sec);
    
      CTRL_setMaxVsMag_pu(handle,_IQ(pUserParams->maxVsMag_pu));
    
      CTRL_setIab_in_pu(handle,&Iab_out_pu);
      CTRL_setIdq_in_pu(handle,&Idq_out_pu);
      CTRL_setIdq_ref_pu(handle,&Idq_ref_pu);
    
      CTRL_setIdRated_pu(handle,_IQ(pUserParams->IdRated/pUserParams->iqFullScaleCurrent_A));
    
      CTRL_setVab_in_pu(handle,&Vab_in_pu);
      CTRL_setVab_out_pu(handle,&Vab_out_pu);
      CTRL_setVdq_out_pu(handle,&Vdq_out_pu);
    
      CTRL_setSpd_out_pu(handle,_IQ(0.0));
    
      CTRL_setRhf(handle,0.0);
      CTRL_setLhf(handle,0.0);
      CTRL_setRoverL(handle,0.0);
    
    
      // reset the counters
      CTRL_resetCounter_current(handle);
      CTRL_resetCounter_isr(handle);
      CTRL_resetCounter_speed(handle);
      CTRL_resetCounter_state(handle);
      CTRL_resetCounter_traj(handle);
    
    
      // set the wait times for each state
      CTRL_setWaitTimes(handle,&pUserParams->ctrlWaitTime[0]);
    
    
      // set flags
      CTRL_setFlag_enableEpl(handle,false);
      CTRL_setFlag_enableCtrl(handle,false);
      CTRL_setFlag_enableEpl(handle,false);
      CTRL_setFlag_enableOffset(handle,true);
      CTRL_setFlag_enableSpeedCtrl(handle,true);
      CTRL_setFlag_enableUserMotorParams(handle,false);
      CTRL_setFlag_enableDcBusComp(handle,true);
    
    
      // initialize the controller error code
      CTRL_setErrorCode(handle,CTRL_ErrorCode_NoError);
    
    
      // set the default controller state
      CTRL_setState(handle,CTRL_State_Idle);
    
    
      // set the number of current sensors
      CTRL_setupClarke_I(handle,pUserParams->numCurrentSensors);
    
    
      // set the number of voltage sensors
      CTRL_setupClarke_V(handle,pUserParams->numVoltageSensors);
    
    
      // set the default Id PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Id,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Id,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Id,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp,Ki,Kd);
    
    
      // set the default the Iq PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Iq,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Iq,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Iq,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp,Ki,Kd);
    
    
      // set the default speed PID controller parameters
      Kp = _IQ(0.02*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz/pUserParams->iqFullScaleCurrent_A);
      Ki = _IQ(2.0*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz*pUserParams->ctrlPeriod_sec/pUserParams->iqFullScaleCurrent_A);
      Kd = _IQ(0.0);
      outMin = _IQ(-1.0);
      outMax = _IQ(1.0);
    
      PID_setGains(obj->pidHandle_spd,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_spd,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_spd,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_spd,Kp,Ki,Kd);
    
    
      // set the speed reference
      CTRL_setSpd_ref_pu(handle,_IQ(0.0));
    
    
      // set the default Id current trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxSlope(obj->trajHandle_Id,_IQ(0.0));
    
    
      // set the default the speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxSlope(obj->trajHandle_spd,_IQ(0.0));
    
    
      // set the default maximum speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxSlope(obj->trajHandle_spdMax,_IQ(0.0)); // not used
    
      
      // set the default estimator parameters
      CTRL_setEstParams(obj->estHandle,pUserParams);
    
    
      // set the maximum modulation for the SVGEN module
      maxModulation = SVGEN_4_OVER_3;
      SVGEN_setMaxModulation(obj->svgenHandle,maxModulation);
    
      return;
    } // end of CTRL_setParams() function
    
    
    void CTRL_setSpd_ref_pu(CTRL_Handle handle,const _iq spd_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_pu() function
    
    
    void CTRL_setSpd_ref_krpm(CTRL_Handle handle,const _iq spd_ref_krpm)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq krpm_to_pu_sf = EST_get_krpm_to_pu_sf(obj->estHandle);
    
      _iq spd_ref_pu = _IQmpy(spd_ref_krpm,krpm_to_pu_sf);
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_krpm() function
    
    
    void CTRL_setup(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      uint_least16_t count_traj = CTRL_getCount_traj(handle);
      uint_least16_t numCtrlTicksPerTrajTick = CTRL_getNumCtrlTicksPerTrajTick(handle);
    
    
      // as needed, update the trajectory
      if(count_traj >= numCtrlTicksPerTrajTick)
        {
          _iq intValue_Id = TRAJ_getIntValue(obj->trajHandle_Id);
    
          // reset the trajectory count
          CTRL_resetCounter_traj(handle);
    
          // run the trajectories
          CTRL_runTraj(handle);
        } // end of if(gFlag_traj) block
    
      return;
    } // end of CTRL_setup() function
    
    
    void CTRL_setupClarke_I(CTRL_Handle handle,uint_least8_t numCurrentSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numCurrentSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else if(numCurrentSensors == 2)
        {
          alpha_sf = _IQ(1.0);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_I,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_I,numCurrentSensors);
    
      return;
    } // end of CTRL_setupClarke_I() function
    
    
    void CTRL_setupClarke_V(CTRL_Handle handle,uint_least8_t numVoltageSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numVoltageSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
     else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_V,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_V,numVoltageSensors);
    
      return;
    } // end of CTRL_setupClarke_V() function
    
    
    void CTRL_setWaitTimes(CTRL_Handle handle,const uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          obj->waitTimes[stateCnt] = pWaitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_setWaitTimes() function
    
    
    bool CTRL_updateState(CTRL_Handle handle)
    {
      CTRL_State_e ctrlState = CTRL_getState(handle);
      bool flag_enableCtrl = CTRL_getFlag_enableCtrl(handle);
      bool stateChanged = false;
    
    
      if(flag_enableCtrl)
        {
          uint_least32_t waitTime = CTRL_getWaitTime(handle,ctrlState);
          uint_least32_t counter_ctrlState = CTRL_getCount_state(handle);
    
    
          // check for errors
          CTRL_checkForErrors(handle);
    
    
          if(counter_ctrlState >= waitTime)
            {
              // reset the counter
              CTRL_resetCounter_state(handle);
    
    
              if(ctrlState == CTRL_State_OnLine)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  _iq Id_target = TRAJ_getTargetValue(obj->trajHandle_Id);
    
                  // update the estimator state
                  bool flag_estStateChanged = EST_updateState(obj->estHandle,Id_target);
    
                  if(flag_estStateChanged)
                    {
                      // setup the controller
                      CTRL_setupCtrl(handle);
    
                      // setup the trajectory
                      CTRL_setupTraj(handle);
                    }
    
                  if(EST_isOnLine(obj->estHandle))
                    {
                      // setup the estimator for online state
                      CTRL_setupEstOnLineState(handle);
                    }
    
                  if(EST_isLockRotor(obj->estHandle) || 
                     (EST_isIdle(obj->estHandle) && EST_isMotorIdentified(obj->estHandle)))
                    {
                      // set the enable controller flag to false
                      CTRL_setFlag_enableCtrl(handle,false);
    
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_Idle);
                    }
                }
              else if(ctrlState == CTRL_State_OffLine)
                {
                  // set the next controller state
                  CTRL_setState(handle,CTRL_State_OnLine);
                }
              else if(ctrlState == CTRL_State_Idle)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  bool  flag_enableUserMotorParams = CTRL_getFlag_enableUserMotorParams(handle);
    
                  if(flag_enableUserMotorParams)
                    {
                      // initialize the motor parameters using values from the user.h file
                      CTRL_setUserMotorParams(handle);
                    }
    
                  if(EST_isIdle(obj->estHandle))
                    {
                      // setup the estimator for idle state
                      CTRL_setupEstIdleState(handle);
    
                      if(EST_isMotorIdentified(obj->estHandle))
                        {
                          if(CTRL_getFlag_enableOffset(handle))
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OffLine);
                            }
                          else
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OnLine);
                            }
                        }
                      else
                        {
                          // set the next controller state
                          CTRL_setState(handle,CTRL_State_OffLine);
                        }
                    }
                  else if(EST_isLockRotor(obj->estHandle))
                    {
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_OnLine);
                    }
                }
            }  // if(counter_ctrlState >= waitTime) loop
        } 
      else
        {
          CTRL_Obj *obj = (CTRL_Obj *)handle;
    
          // set the next controller state
          CTRL_setState(handle,CTRL_State_Idle);
    
          // set the estimator to idle
          if(!EST_isLockRotor(obj->estHandle))
            {
              if(EST_isMotorIdentified(obj->estHandle))
                {
                  EST_setIdle(obj->estHandle);
                }
              else
                {
                  EST_setIdle_all(obj->estHandle);
    
                  EST_setRs_pu(obj->estHandle,_IQ30(0.0));
                }
            }
        }
    
    
      // check to see if the state changed
      if(ctrlState != CTRL_getState(handle))
        {
          stateChanged = true;
        }
    
      return(stateChanged);
    } // end of CTRL_updateState() function
    
    // end of file
    

    2844.ctrl.h

    1563.main.h

    /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, LineStream Technologies Incorporated
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
    * *  Neither the names of Texas Instruments Incorporated, LineStream
     *    Technologies Incorporated, nor the names of its contributors may be
     *    used to endorse or promote products derived from this software without
     *    specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    //! \file   solutions/instaspin_motion/src/proj_lab05f.c
    //! \brief  Comparing performance of PI velocity controller & SpinTAC velocity controller
    //!
    //! (C) Copyright 2012, LineStream Technologies, Inc.
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    //! \defgroup PROJ_LAB05f PROJ_LAB05f
    //@{
    
    //! \defgroup PROJ_LAB05f_OVERVIEW Project Overview
    //!
    //! Comparing performance of PI velocity controller & SpinTAC velocity controller
    //!
    
    // **************************************************************************
    // the includes
    
    // system includes
    #include <math.h>
    #include "main.h"
    
    #ifdef FLASH
    #pragma CODE_SECTION(mainISR,"ramfuncs");
    #endif
    
    // Include header files used in the main function
    
    
    // **************************************************************************
    // the defines
    
    #define LED_BLINK_FREQ_Hz   5
    
    
    // **************************************************************************
    // the globals
    
    uint_least16_t gCounter_updateGlobals = 0;
    
    bool Flag_Latch_softwareUpdate = true;
    
    CTRL_Handle ctrlHandle;
    
    DRV_Handle drvHandle;
    
    USER_Params gUserParams;
    
    DRV_PwmData_t gPwmData;
    
    DRV_AdcData_t gAdcData;
    
    _iq gMaxCurrentSlope = _IQ(0.0);
    
    #ifdef FAST_ROM_V1p6
    CTRL_Obj *controller_obj;
    #else
    CTRL_Obj ctrl;				//v1p7 format
    #endif
    
    ST_Obj st_obj;
    ST_Handle stHandle;
    
    uint16_t gLEDcnt = 0;
    
    volatile MOTOR_Vars_t gMotorVars = MOTOR_Vars_INIT;
    
    // Graphing Variables
    volatile bool Graph_Flag_Enable_update = false;
    volatile unsigned int Graph_Counter = 0;
    volatile unsigned short Graph_Tick_Counter = 0;
    volatile unsigned short Graph_Tick_Counter_Value = 10;
    
    #define GRAPH_SIZE 600        // Having more buffered points to show
    
    //#define GRAPH_SIZE 300
    volatile _iq Graph_Data[GRAPH_SIZE];
    volatile _iq Graph_Data2[GRAPH_SIZE];
    volatile _iq SpeedRef_krpm_previous = _IQ(0.0);
    
    #ifdef FLASH
    // Used for running BackGround in flash, and ISR in RAM
    extern uint16_t *RamfuncsLoadStart, *RamfuncsLoadEnd, *RamfuncsRunStart;
    #endif
    
    
    #ifdef DRV8301_SPI
    // Watch window interface to the 8301 SPI
    DRV_SPI_8301_Vars_t gDrvSpi8301Vars;
    #endif
    
    
    // **************************************************************************
    // the functions
    
    void main(void)
    {
      uint_least8_t estNumber = 0;
    
    #ifdef FAST_ROM_V1p6
      uint_least8_t ctrlNumber = 0;
    #endif
    
      // Only used if running from FLASH
      // Note that the variable FLASH is defined by the project
      #ifdef FLASH
      // Copy time critical code and Flash setup code to RAM
      // The RamfuncsLoadStart, RamfuncsLoadEnd, and RamfuncsRunStart
      // symbols are created by the linker. Refer to the linker files.
      memCopy((uint16_t *)&RamfuncsLoadStart,(uint16_t *)&RamfuncsLoadEnd,(uint16_t *)&RamfuncsRunStart);
      #endif
    
      uint_least8_t graphCounter = 0;
    
      // initialize the driver
      drvHandle = DRV_init(&drv,sizeof(drv));
    
    
      // initialize the user parameters
      USER_setParams(&gUserParams);
    
    
      // set the driver parameters
      DRV_setParams(drvHandle,&gUserParams);
    
    
      // initialize the controller
    #ifdef FAST_ROM_V1p6
      ctrlHandle = CTRL_initCtrl(ctrlNumber, estNumber);  		//v1p6 format (06xF and 06xM devices)
      controller_obj = (CTRL_Obj *)ctrlHandle;
    #else
      ctrlHandle = CTRL_initCtrl(estNumber,&ctrl,sizeof(ctrl));	//v1p7 format default
    #endif
    
    
      // set the default controller parameters
      CTRL_setParams(ctrlHandle,&gUserParams);
    
    
      // setup faults
      DRV_setupFaults(drvHandle);
    
    
      // initialize the interrupt vector table
      DRV_initIntVectorTable(drvHandle);
    
    
      // enable the ADC interrupts
      DRV_enableAdcInts(drvHandle);
    
    
      // enable global interrupts
      DRV_enableGlobalInts(drvHandle);
    
    
      // enable debug interrupts
      DRV_enableDebugInt(drvHandle);
    
    
      // disable the PWM
      DRV_disablePwm(drvHandle);
    
    
      // enable DC bus compensation
      CTRL_setFlag_enableDcBusComp(ctrlHandle, true);
    
    
      // initialize the SpinTAC Components
      stHandle = ST_init(&st_obj, sizeof(st_obj));
      
      
      // setup the SpinTAC Components
      ST_setupVelCtl(stHandle);
    
      
      // initialize the Graph Variables
      for(graphCounter=0; graphCounter<GRAPH_SIZE; graphCounter++) {
    	  Graph_Data[graphCounter] = 0;
    	  Graph_Data2[graphCounter] = 0;
      }  
    
    
    #ifdef DRV8301_SPI
      // turn on the DRV8301 if present
      DRV_enable8301(drvHandle);
      // initialize the DRV8301 interface
      DRV_8301_SpiInterface_init(drvHandle,&gDrvSpi8301Vars);
    #endif
    
    
      for(;;)
      {
        // Waiting for enable system flag to be set
        while(!(gMotorVars.Flag_enableSys));
    
        Flag_Latch_softwareUpdate = true;
    
        // Dis-able the Library internal PI.  Iq has no reference now
        CTRL_setFlag_enableSpeedCtrl(ctrlHandle, false);
    
        // loop while the enable system flag is true
        while(gMotorVars.Flag_enableSys)
          {
            CTRL_Obj *obj = (CTRL_Obj *)ctrlHandle;
            ST_Obj *stObj = (ST_Obj *)stHandle;
    
            // increment counters
            gCounter_updateGlobals++;
    
            // enable/disable the use of motor parameters being loaded from user.h
            CTRL_setFlag_enableUserMotorParams(ctrlHandle,gMotorVars.Flag_enableUserParams);
    
            // enable/disable Rs recalibration during motor startup
            EST_setFlag_enableRsRecalc(obj->estHandle,gMotorVars.Flag_enableRsRecalc);
    
            // enable/disable automatic calculation of bias values
            CTRL_setFlag_enableOffset(ctrlHandle,gMotorVars.Flag_enableOffsetcalc);
    
    
            if(CTRL_isError(ctrlHandle))
              {
                // set the enable controller flag to false
                CTRL_setFlag_enableCtrl(ctrlHandle,false);
    
                // set the enable system flag to false
                gMotorVars.Flag_enableSys = false;
    
                // disable the PWM
                DRV_disablePwm(drvHandle);
              }
            else
              {
                // update the controller state
                bool flag_ctrlStateChanged = CTRL_updateState(ctrlHandle);
    
                // enable or disable the control
                CTRL_setFlag_enableCtrl(ctrlHandle, gMotorVars.Flag_Run_Identify);
    
                if(flag_ctrlStateChanged)
                  {
                    CTRL_State_e ctrlState = CTRL_getState(ctrlHandle);
    
                    if(ctrlState == CTRL_State_OffLine)
                      {
                        // enable the PWM
                        DRV_enablePwm(drvHandle);
                      }
                    else if(ctrlState == CTRL_State_OnLine)
                      {
                        if(gMotorVars.Flag_enableOffsetcalc == true)
                        {
                          // update the ADC bias values
                          DRV_updateAdcBias(drvHandle);
                        }
                        else
                        {
                          // set the current bias
                          DRV_setBias(drvHandle,DRV_SensorType_Current,0,_IQ(I_A_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Current,1,_IQ(I_B_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Current,2,_IQ(I_C_offset));
    
                          // set the voltage bias
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,0,_IQ(V_A_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,1,_IQ(V_B_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,2,_IQ(V_C_offset));
                        }
    
                        // enable the PWM
                        DRV_enablePwm(drvHandle);
                      }
                    else if(ctrlState == CTRL_State_Idle)
                      {
                        // disable the PWM
                        DRV_disablePwm(drvHandle);
                        gMotorVars.Flag_Run_Identify = false;
                      }
                  }
              }
    
    
            if(EST_isMotorIdentified(obj->estHandle))
              {
                // set the current ramp
                EST_setMaxCurrentSlope_pu(obj->estHandle,gMaxCurrentSlope);
                gMotorVars.Flag_MotorIdentified = true;
    
                // set the speed reference
                CTRL_setSpd_ref_krpm(ctrlHandle,gMotorVars.SpeedRef_krpm);
    
                // set the speed acceleration
                CTRL_setMaxAccel_pu(ctrlHandle,_IQmpy(MAX_ACCEL_KRPMPS_SF,gMotorVars.MaxAccel_krpmps));
    
                // enable the SpinTAC Speed Controller
                STVELCTL_setEnable(stObj->velCtlHandle, true);
    
                if(EST_getState(obj->estHandle) != EST_State_OnLine)
                {
                	// if the estimator is not running, place SpinTAC into reset
                	STVELCTL_setEnable(stObj->velCtlHandle, false);
                }
    			
    			// select the SpinTAC Speed Controller (true) or the PI Speed Controller (false)
                CTRL_setFlag_enableSpeedCtrl(ctrlHandle, !gMotorVars.SpinTAC.VelCtlEnb);
    
                if(Flag_Latch_softwareUpdate)
                {
                  Flag_Latch_softwareUpdate = false;
    
    #ifdef FAST_ROM_V1p6
                  if(CTRL_getFlag_enableUserMotorParams(ctrlHandle) == true)
                  {
                      // call this function to fix 1p6
                      softwareUpdate1p6(ctrlHandle);
                  }
    #endif
    
                  calcPIgains(ctrlHandle);
    
                  // initialize the watch window kp and ki current values with pre-calculated values
                  gMotorVars.Kp_Idq = CTRL_getKp(ctrlHandle,CTRL_Type_PID_Id);
                  gMotorVars.Ki_Idq = CTRL_getKi(ctrlHandle,CTRL_Type_PID_Id);
    
                  // initialize the watch window kp and ki values with pre-calculated values
                  gMotorVars.Kp_spd = CTRL_getKp(ctrlHandle,CTRL_Type_PID_spd);
                  gMotorVars.Ki_spd = CTRL_getKi(ctrlHandle,CTRL_Type_PID_spd);
    			  
    			  // initialize the watch window Bw value with the default value
                  gMotorVars.SpinTAC.VelCtlBwScale = STVELCTL_getBandwidthScale(stObj->velCtlHandle);
                }
              }
            else
              {
                Flag_Latch_softwareUpdate = true;
    
                // the estimator sets the maximum current slope during identification
                gMaxCurrentSlope = EST_getMaxCurrentSlope_pu(obj->estHandle);
              }
    
    
            // when appropriate, update the global variables
            if(gCounter_updateGlobals >= NUM_MAIN_TICKS_FOR_GLOBAL_VARIABLE_UPDATE)
              {
                // reset the counter
                gCounter_updateGlobals = 0;
    
                updateGlobalVariables_motor(ctrlHandle, stHandle);
              }
    
          } // end of while(gFlag_enableSys) loop
    
    
        // disable the PWM
        DRV_disablePwm(drvHandle);
    
        // set the default controller parameters (Reset the control to re-identify the motor)
        CTRL_setParams(ctrlHandle,&gUserParams);
    
        // setup the SpinTAC Components
        ST_setupVelCtl(stHandle);
    
      } // end of for(;;) loop
    
    } // end of main() function
    
    
    interrupt void mainISR(void)
    {
    
      static uint16_t stCnt = 0;
    
      // DPM - toggle status LED
      if(gLEDcnt++ > (uint_least32_t)(USER_PWM_FREQ_kHz * 1000 / LED_BLINK_FREQ_Hz)) {
        DRV_toggleLed(drvHandle,(GPIO_Number_e)DRV_Gpio_LED2);
        gLEDcnt = 0;
      }
    
    
      // acknowledge the ADC interrupt
      DRV_acqAdcInt(drvHandle,ADC_IntNumber_1);
    
    
      // convert the ADC data
      DRV_readAdcData(drvHandle,&gAdcData);
    
    
      // Run the SpinTAC Components
      if(stCnt++ >= ISR_TICKS_PER_SPINTAC_TICK) {
    	  ST_runVelCtl(stHandle, ctrlHandle);
    	  stCnt = 1;
      }
    
    
      // run the controller
      CTRL_run(ctrlHandle,drvHandle,&gAdcData,&gPwmData);
    
    
      // write the PWM compare values
      DRV_writePwmData(drvHandle,&gPwmData);
    
      if (!(SpeedRef_krpm_previous == gMotorVars.SpeedRef_krpm)) {
      	  Graph_Flag_Enable_update = true;
      	  Graph_Counter = 0;
      	  SpeedRef_krpm_previous = gMotorVars.SpeedRef_krpm;
      }
    
      gMotorVars.Ia = CTRL_getIa_in_pu(ctrlHandle);
    
      //gMotorVars.Iq_A = _IQmpy(CTRL_getIq_in_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_CURRENT_A));
    
      // store graph value
      if(Graph_Flag_Enable_update) {
      	  if(Graph_Counter >= GRAPH_SIZE) {
      		  Graph_Flag_Enable_update = false;
      	  }
      	  else {
      		  if(Graph_Tick_Counter == 0) {
      		      Graph_Data[Graph_Counter] = gMotorVars.Speed_krpm;
    
     		      Graph_Data2[Graph_Counter] = gMotorVars.Ia;
    
     //		  Graph_Data2[Graph_Counter] = gMotorVars.Iq_A;
      		      Graph_Counter++;
      		      Graph_Tick_Counter = Graph_Tick_Counter_Value - 1;
      		  }
      		  else {
      			  Graph_Tick_Counter--;
      		  }
      	  }
       }
    
    
      // setup the controller
      CTRL_setup(ctrlHandle);
    
    
      return;
    } // end of mainISR() function
    
    
    void updateGlobalVariables_motor(CTRL_Handle handle, ST_Handle sthandle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      ST_Obj *stObj = (ST_Obj *)sthandle;
    
    
      // get the speed estimate
      gMotorVars.Speed_krpm = EST_getSpeed_krpm(obj->estHandle);
    
      // get the torque estimate
      gMotorVars.Torque_lbin = EST_getTorque_lbin(obj->estHandle);
    
      // get the magnetizing current
      gMotorVars.MagnCurr_A = EST_getIdRated(obj->estHandle);
    
      // get the rotor resistance
      gMotorVars.Rr_Ohm = EST_getRr_Ohm(obj->estHandle);
    
      // get the stator resistance
      gMotorVars.Rs_Ohm = EST_getRs_Ohm(obj->estHandle);
    
      // get the stator inductance in the direct coordinate direction
      gMotorVars.Lsd_H = EST_getLs_d_H(obj->estHandle);
    
      // get the stator inductance in the quadrature coordinate direction
      gMotorVars.Lsq_H = EST_getLs_q_H(obj->estHandle);
    
      // get the flux
      gMotorVars.Flux_VpHz = EST_getFlux_VpHz(obj->estHandle);
    
      // get the controller state
      gMotorVars.CtrlState = CTRL_getState(handle);
    
      // get the estimator state
      gMotorVars.EstState = EST_getState(obj->estHandle);
      
      if((gMotorVars.CtrlState == CTRL_State_OnLine) && (gMotorVars.Flag_MotorIdentified == true) && (Flag_Latch_softwareUpdate == false))
        {
          // set the kp and ki speed values from the watch window
          CTRL_setKp(handle,CTRL_Type_PID_spd,gMotorVars.Kp_spd);
          CTRL_setKi(handle,CTRL_Type_PID_spd,gMotorVars.Ki_spd);
    
          // set the kp and ki current values for Id and Iq from the watch window
          CTRL_setKp(handle,CTRL_Type_PID_Id,gMotorVars.Kp_Idq);
          CTRL_setKi(handle,CTRL_Type_PID_Id,gMotorVars.Ki_Idq);
          CTRL_setKp(handle,CTRL_Type_PID_Iq,gMotorVars.Kp_Idq);
          CTRL_setKi(handle,CTRL_Type_PID_Iq,gMotorVars.Ki_Idq);
    	}
    
      // gets the Velocity Controller status
      gMotorVars.SpinTAC.VelCtlStatus = STVELCTL_getStatus(stObj->velCtlHandle);
    	
      // get the inertia setting
      gMotorVars.SpinTAC.Inertia_Aperkrpm = _IQmpy(STVELCTL_getInertia(stObj->velCtlHandle), _IQ(ST_SPEED_PU_PER_KRPM * USER_IQ_FULL_SCALE_CURRENT_A));
    
      // get the friction setting
      gMotorVars.SpinTAC.Friction_Aperkrpm = _IQmpy(STVELCTL_getFriction(stObj->velCtlHandle), _IQ(ST_SPEED_PU_PER_KRPM * USER_IQ_FULL_SCALE_CURRENT_A));
    
      // set the SpinTAC (ST) bandwidth scale
      STVELCTL_setBandwidthScale(stObj->velCtlHandle, gMotorVars.SpinTAC.VelCtlBwScale);
    
      // gets the SpinTAC (ST) bandwidth
      gMotorVars.SpinTAC.VelCtlBw_radps = STVELCTL_getBandwidth_radps(stObj->velCtlHandle);
    
      // get the Velocity Controller error
      gMotorVars.SpinTAC.VelCtlErrorID = STVELCTL_getErrorID(stObj->velCtlHandle);
    
      // enable/disable the forced angle
      EST_setFlag_enableForceAngle(obj->estHandle,gMotorVars.Flag_enableForceAngle);
    
      // enable or disable power warp
      CTRL_setFlag_enableEpl(handle,gMotorVars.Flag_enableEpl);
    
    #ifdef DRV8301_SPI
      DRV_8301_SpiInterface(drvHandle,&gDrvSpi8301Vars);
    #endif
    
      return;
    } // end of updateGlobalVariables_motor() function
    
    #ifdef FAST_ROM_V1p6
    void softwareUpdate1p6(CTRL_Handle handle)
    {
    
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t fullScaleInductance = EST_getFullScaleInductance(obj->estHandle);
      float_t Ls_coarse_max = _IQ30toF(EST_getLs_coarse_max_pu(obj->estHandle));
      int_least8_t lShift = ceil(log(obj->motorParams.Ls_d/(Ls_coarse_max*fullScaleInductance))/log(2.0));
      uint_least8_t Ls_qFmt = 30 - lShift;
      float_t L_max = fullScaleInductance * pow(2.0,lShift);
      _iq Ls_d_pu = _IQ30(obj->motorParams.Ls_d / L_max);
      _iq Ls_q_pu = _IQ30(obj->motorParams.Ls_q / L_max);
    
    
      // store the results
      EST_setLs_d_pu(obj->estHandle,Ls_d_pu);
      EST_setLs_q_pu(obj->estHandle,Ls_q_pu);
      EST_setLs_qFmt(obj->estHandle,Ls_qFmt);
    
      return;
    } // end of softwareUpdate1p6() function
    #endif
    
    void calcPIgains(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t Ls_d = EST_getLs_d_H(obj->estHandle);
      float_t Ls_q = EST_getLs_q_H(obj->estHandle);
      float_t Rs = EST_getRs_Ohm(obj->estHandle);
      float_t RoverLs_d = Rs/Ls_d;
      float_t RoverLs_q = Rs/Ls_q;
      float_t fullScaleCurrent = EST_getFullScaleCurrent(obj->estHandle);
      float_t fullScaleVoltage = EST_getFullScaleVoltage(obj->estHandle);
      float_t ctrlPeriod_sec = CTRL_getCtrlPeriod_sec(handle);
      _iq Kp_Id = _IQ((0.25*Ls_d*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Id = _IQ(RoverLs_d*ctrlPeriod_sec);
      _iq Kp_Iq = _IQ((0.25*Ls_q*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Iq = _IQ(RoverLs_q*ctrlPeriod_sec);
      _iq Kd = _IQ(0.0);
    
      // set the Id controller gains
      PID_setKi(obj->pidHandle_Id,Ki_Id);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp_Id,Ki_Id,Kd);
    
      // set the Iq controller gains
      PID_setKi(obj->pidHandle_Iq,Ki_Iq);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp_Iq,Ki_Iq,Kd);
    
      return;
    } // end of calcPIgains() function
    
    
    void ST_runVelCtl(ST_Handle sthandle, CTRL_Handle handle)
    {
    
        _iq speedFeedback, iqReference, gSpdError, gUp, gUi;
        ST_Obj *stObj = (ST_Obj *)sthandle;
        CTRL_Obj *ctrlObj = (CTRL_Obj *)handle;
    
        // Get the mechanical speed in pu
        speedFeedback = EST_getFm_pu(ctrlObj->estHandle);
    
    	// Run the SpinTAC Controller
    	// Note that the library internal ramp generator is used to set the speed reference
        STVELCTL_setVelocityReference(stObj->velCtlHandle, TRAJ_getIntValue(ctrlObj->trajHandle_spd));
    	STVELCTL_setAccelerationReference(stObj->velCtlHandle, _IQ(0.0));	// Internal ramp generator does not provide Acceleration Reference
    	STVELCTL_setVelocityFeedback(stObj->velCtlHandle, speedFeedback);
    	STVELCTL_run(stObj->velCtlHandle);
    
    	// select SpinTAC Velocity Controller
    	iqReference = STVELCTL_getTorqueReference(stObj->velCtlHandle);
    
    	if(gMotorVars.SpinTAC.VelCtlEnb == true) {
    		// Set the Iq reference that came out of SpinTAC Velocity Control
    		CTRL_setIq_ref_pu(ctrlHandle, iqReference);
    		// Update internal PI integrator, if running SpinTAC
    		gSpdError = TRAJ_getIntValue(ctrlObj->trajHandle_spd) - speedFeedback;
    		gUp = _IQmpy(gSpdError, CTRL_getKp(handle, CTRL_Type_PID_spd));
    		gUi = _IQmpy(gSpdError, CTRL_getKi(handle, CTRL_Type_PID_spd));
    		CTRL_setUi(handle, CTRL_Type_PID_spd, iqReference - gUp - gUi);
    	}
    }
    //@} //defgroup
    // end of file
    

  • oh, I see what you did. You are pulling the value I suspected you needed. This should work.

    I got this to build by updating main.h

    you need to add another variable to the right place in the structure for Ia.  I placed it 3rd from the bottom.

           _IQ(0.0), \
                             {0,0,0}, \
                             {0,0,0}}

     

      _iq Ia;

      MATH_vec3 I_bias;
      MATH_vec3 V_bias;

    }MOTOR_Vars_t;

  • But I already have them, havn't I?

    main.h: line 123 and line 183.

  • it looks like it...

    I just did this in MW _12 with InstaSPIN_FOC and myproj_lab10a  and was able to compile

    /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
     * *  Neither the name of Texas Instruments Incorporated nor the names of
     *    its contributors may be used to endorse or promote products derived
     *    from this software without specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    
     
     
    //! \file   solutions/instaspin_foc/src/ctrl.c
    //! \brief  Contains the various functions related to the controller (CTRL) object
    //!
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    
    // **************************************************************************
    // the includes
    
    #include <math.h>
    
    
    // drivers
    
    
    // modules
    #include "sw/modules/dlog/src/32b/dlog4ch.h"
    #include "sw/modules/math/src/32b/math.h"
    
    
    // platforms
    #include "ctrl.h"
    #include "hal.h"
    #include "user.h"
    
    
    #ifdef FLASH
    #pragma CODE_SECTION(CTRL_run,"ramfuncs");
    #pragma CODE_SECTION(CTRL_setup,"ramfuncs");
    #endif
    
    
    // **************************************************************************
    // the defines
    
    
    // **************************************************************************
    // the globals
    
    
    // **************************************************************************
    // the function prototypes
    
    void CTRL_getGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       _iq *pKp,_iq *pKi,_iq *pKd)
    {
    
      *pKp = CTRL_getKp(handle,ctrlType);
      *pKi = CTRL_getKi(handle,ctrlType);
      *pKd = CTRL_getKd(handle,ctrlType);
    
      return;    
    } // end of CTRL_getGains() function
    
    
    void CTRL_getIab_filt_pu(CTRL_Handle handle,MATH_vec2 *pIab_filt_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_filt_pu->value[0] = obj->Iab_filt.value[0];
      pIab_filt_pu->value[1] = obj->Iab_filt.value[1];
    
      return;
    } // end of CTRL_getIab_filt_pu() function
    
    
    void CTRL_getIab_in_pu(CTRL_Handle handle,MATH_vec2 *pIab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_in_pu->value[0] = obj->Iab_in.value[0];
      pIab_in_pu->value[1] = obj->Iab_in.value[1];
    
      return;
    } // end of CTRL_getIab_in_pu() function
    
    
    void CTRL_getIdq_in_pu(CTRL_Handle handle,MATH_vec2 *pIdq_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_in_pu->value[0] = obj->Idq_in.value[0];
      pIdq_in_pu->value[1] = obj->Idq_in.value[1];
    
      return;
    } // end of CTRL_getIdq_in_pu() function
    
    
    void CTRL_getIdq_ref_pu(CTRL_Handle handle,MATH_vec2 *pIdq_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_ref_pu->value[0] = obj->Idq_ref.value[0];
      pIdq_ref_pu->value[1] = obj->Idq_ref.value[1];
    
      return;
    } // end of CTRL_getIdq_ref_pu() function
    
    
    _iq CTRL_getMagCurrent_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getIdRated_pu(handle));
    } // end of CTRL_getMagCurrent_pu() function
    
    
    _iq CTRL_getMaximumSpeed_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getSpd_max_pu(handle));
    } // end of CTRL_getMaximumSpeed_pu() function
    
    
    void CTRL_getVab_in_pu(CTRL_Handle handle,MATH_vec2 *pVab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_in_pu->value[0] = obj->Vab_in.value[0];
      pVab_in_pu->value[1] = obj->Vab_in.value[1];
    
      return;
    } // end of CTRL_getVab_in_pu() function
    
    
    void CTRL_getVab_out_pu(CTRL_Handle handle,MATH_vec2 *pVab_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_out_pu->value[0] = obj->Vab_out.value[0];
      pVab_out_pu->value[1] = obj->Vab_out.value[1];
    
      return;
    } // end of CTRL_getVab_out_pu() function
    
    
    void CTRL_getVdq_out_pu(CTRL_Handle handle,MATH_vec2 *pVdq_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVdq_out_pu->value[0] = obj->Vdq_out.value[0];
      pVdq_out_pu->value[1] = obj->Vdq_out.value[1];
    
      return;
    } // end of CTRL_getVdq_out_pu() function
    
    
    void CTRL_getWaitTimes(CTRL_Handle handle,uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          pWaitTimes[stateCnt] = obj->waitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_getWaitTimes() function
    
    
    void CTRL_run(CTRL_Handle handle,HAL_Handle halHandle,
                  const HAL_AdcData_t *pAdcData,
                  HAL_PwmData_t *pPwmData)
    {
      uint_least16_t count_isr = CTRL_getCount_isr(handle);
      uint_least16_t numIsrTicksPerCtrlTick = CTRL_getNumIsrTicksPerCtrlTick(handle);
    
    
      // if needed, run the controller
      if(count_isr >= numIsrTicksPerCtrlTick)
        {
          CTRL_State_e ctrlState = CTRL_getState(handle);
    
          // reset the isr count
          CTRL_resetCounter_isr(handle);
    
          // increment the state counter
          CTRL_incrCounter_state(handle);
    
          // increment the trajectory count
          CTRL_incrCounter_traj(handle);
    
          // run the appropriate controller
          if(ctrlState == CTRL_State_OnLine)
            {
        	  CTRL_Obj *obj = (CTRL_Obj *)handle;
    
              // increment the current count
              CTRL_incrCounter_current(handle);
    
              // increment the speed count
              CTRL_incrCounter_speed(handle);
    
              if(EST_getState(obj->estHandle) >= EST_State_MotorIdentified)
                {
                  // run the online controller
                  CTRL_runOnLine_User(handle,pAdcData,pPwmData);
                }
              else
                {
                  // run the online controller
                  CTRL_runOnLine(handle,pAdcData,pPwmData);
                }
            }
          else if(ctrlState == CTRL_State_OffLine)
            {
              // run the offline controller
              CTRL_runOffLine(handle,halHandle,pAdcData,pPwmData);
            }
        }
      else
        {
          // increment the isr count
          CTRL_incrCounter_isr(handle);
        }
    
      return;
    } // end of CTRL_run() function
    
    
    void CTRL_setGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       const _iq Kp,const _iq Ki,const _iq Kd)
    {
    
      CTRL_setKp(handle,ctrlType,Kp);
      CTRL_setKi(handle,ctrlType,Ki);
      CTRL_setKd(handle,ctrlType,Kd);
    
      return;    
    } // end of CTRL_setGains() function
    
    
    void CTRL_setMagCurrent_pu(CTRL_Handle handle,const _iq magCurrent_pu)
    {
    
      CTRL_setIdRated_pu(handle,magCurrent_pu);
    
      return;    
    } // end of CTRL_setMagCurrent_pu() function
    
    
    void CTRL_setMaximumSpeed_pu(CTRL_Handle handle,const _iq maxSpeed_pu)
    {
    
      CTRL_setSpd_max_pu(handle,maxSpeed_pu);
    
      return;    
    } // end of CTRL_setMaximumSpeed_pu() function
    
    
    void CTRL_setParams(CTRL_Handle handle,USER_Params *pUserParams)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq Kp,Ki,Kd;
      _iq outMin,outMax;
      _iq maxModulation;
    
      MATH_vec2 Iab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_ref_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_in_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vdq_out_pu = {_IQ(0.0),_IQ(0.0)};
    
    
      // assign the motor type
      CTRL_setMotorParams(handle,pUserParams->motor_type,
                          pUserParams->motor_numPolePairs,
                          pUserParams->motor_ratedFlux,
                          pUserParams->motor_Ls_d,
                          pUserParams->motor_Ls_q,
                          pUserParams->motor_Rr,
                          pUserParams->motor_Rs);
    
    
      // assign other controller parameters
      CTRL_setNumIsrTicksPerCtrlTick(handle,pUserParams->numIsrTicksPerCtrlTick);
      CTRL_setNumCtrlTicksPerCurrentTick(handle,pUserParams->numCtrlTicksPerCurrentTick);
      CTRL_setNumCtrlTicksPerSpeedTick(handle,pUserParams->numCtrlTicksPerSpeedTick);
      CTRL_setNumCtrlTicksPerTrajTick(handle,pUserParams->numCtrlTicksPerTrajTick);
    
      CTRL_setCtrlFreq_Hz(handle,pUserParams->ctrlFreq_Hz);
      CTRL_setTrajFreq_Hz(handle,pUserParams->trajFreq_Hz);
      CTRL_setTrajPeriod_sec(handle,_IQ(1.0/pUserParams->trajFreq_Hz));
    
      CTRL_setCtrlPeriod_sec(handle,pUserParams->ctrlPeriod_sec);
    
      CTRL_setMaxVsMag_pu(handle,_IQ(pUserParams->maxVsMag_pu));
    
      CTRL_setIab_in_pu(handle,&Iab_out_pu);
      CTRL_setIdq_in_pu(handle,&Idq_out_pu);
      CTRL_setIdq_ref_pu(handle,&Idq_ref_pu);
    
      CTRL_setIdRated_pu(handle,_IQ(pUserParams->IdRated/pUserParams->iqFullScaleCurrent_A));
    
      CTRL_setVab_in_pu(handle,&Vab_in_pu);
      CTRL_setVab_out_pu(handle,&Vab_out_pu);
      CTRL_setVdq_out_pu(handle,&Vdq_out_pu);
    
      CTRL_setSpd_out_pu(handle,_IQ(0.0));
    
      CTRL_setRhf(handle,0.0);
      CTRL_setLhf(handle,0.0);
      CTRL_setRoverL(handle,0.0);
    
    
      // reset the counters
      CTRL_resetCounter_current(handle);
      CTRL_resetCounter_isr(handle);
      CTRL_resetCounter_speed(handle);
      CTRL_resetCounter_state(handle);
      CTRL_resetCounter_traj(handle);
    
    
      // set the wait times for each state
      CTRL_setWaitTimes(handle,&pUserParams->ctrlWaitTime[0]);
    
    
      // set flags
      CTRL_setFlag_enablePowerWarp(handle,false);
      CTRL_setFlag_enableCtrl(handle,false);
      CTRL_setFlag_enableOffset(handle,true);
      CTRL_setFlag_enableSpeedCtrl(handle,true);
      CTRL_setFlag_enableUserMotorParams(handle,false);
      CTRL_setFlag_enableDcBusComp(handle,true);
    
    
      // initialize the controller error code
      CTRL_setErrorCode(handle,CTRL_ErrorCode_NoError);
    
    
      // set the default controller state
      CTRL_setState(handle,CTRL_State_Idle);
    
    
      // set the number of current sensors
      CTRL_setupClarke_I(handle,pUserParams->numCurrentSensors);
    
    
      // set the number of voltage sensors
      CTRL_setupClarke_V(handle,pUserParams->numVoltageSensors);
    
    
      // set the default Id PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Id,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Id,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Id,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp,Ki,Kd);
    
    
      // set the default the Iq PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Iq,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Iq,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Iq,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp,Ki,Kd);
    
    
      // set the default speed PID controller parameters
      Kp = _IQ(0.02*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz/pUserParams->iqFullScaleCurrent_A);
      Ki = _IQ(2.0*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz*pUserParams->ctrlPeriod_sec/pUserParams->iqFullScaleCurrent_A);
      Kd = _IQ(0.0);
      outMin = _IQ(-1.0);
      outMax = _IQ(1.0);
    
      PID_setGains(obj->pidHandle_spd,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_spd,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_spd,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_spd,Kp,Ki,Kd);
    
    
      // set the speed reference
      CTRL_setSpd_ref_pu(handle,_IQ(0.0));
    
    
      // set the default Id current trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxDelta(obj->trajHandle_Id,_IQ(0.0));
    
    
      // set the default the speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxDelta(obj->trajHandle_spd,_IQ(0.0));
    
    
      // set the default maximum speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxDelta(obj->trajHandle_spdMax,_IQ(0.0)); // not used
    
      
      // set the default estimator parameters
      CTRL_setEstParams(obj->estHandle,pUserParams);
    
    
      // set the maximum modulation for the SVGEN module
      maxModulation = SVGEN_4_OVER_3;
      SVGEN_setMaxModulation(obj->svgenHandle,maxModulation);
    
      return;
    } // end of CTRL_setParams() function
    
    
    void CTRL_setSpd_ref_pu(CTRL_Handle handle,const _iq spd_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_pu() function
    
    
    void CTRL_setSpd_ref_krpm(CTRL_Handle handle,const _iq spd_ref_krpm)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq krpm_to_pu_sf = EST_get_krpm_to_pu_sf(obj->estHandle);
    
      _iq spd_ref_pu = _IQmpy(spd_ref_krpm,krpm_to_pu_sf);
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_krpm() function
    
    
    void CTRL_setup(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      uint_least16_t count_traj = CTRL_getCount_traj(handle);
      uint_least16_t numCtrlTicksPerTrajTick = CTRL_getNumCtrlTicksPerTrajTick(handle);
    
    
      // as needed, update the trajectory
      if(count_traj >= numCtrlTicksPerTrajTick)
        {
          _iq intValue_Id = TRAJ_getIntValue(obj->trajHandle_Id);
    
          // reset the trajectory count
          CTRL_resetCounter_traj(handle);
    
          // run the trajectories
          CTRL_runTraj(handle);
        } // end of if(gFlag_traj) block
    
      return;
    } // end of CTRL_setup() function
    
    
    void CTRL_setupClarke_I(CTRL_Handle handle,uint_least8_t numCurrentSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numCurrentSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else if(numCurrentSensors == 2)
        {
          alpha_sf = _IQ(1.0);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_I,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_I,numCurrentSensors);
    
      return;
    } // end of CTRL_setupClarke_I() function
    
    
    void CTRL_setupClarke_V(CTRL_Handle handle,uint_least8_t numVoltageSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numVoltageSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
     else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_V,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_V,numVoltageSensors);
    
      return;
    } // end of CTRL_setupClarke_V() function
    
    
    void CTRL_setWaitTimes(CTRL_Handle handle,const uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          obj->waitTimes[stateCnt] = pWaitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_setWaitTimes() function
    
    
    bool CTRL_updateState(CTRL_Handle handle)
    {
      CTRL_State_e ctrlState = CTRL_getState(handle);
      bool flag_enableCtrl = CTRL_getFlag_enableCtrl(handle);
      bool stateChanged = false;
    
    
      if(flag_enableCtrl)
        {
          uint_least32_t waitTime = CTRL_getWaitTime(handle,ctrlState);
          uint_least32_t counter_ctrlState = CTRL_getCount_state(handle);
    
    
          // check for errors
          CTRL_checkForErrors(handle);
    
    
          if(counter_ctrlState >= waitTime)
            {
              // reset the counter
              CTRL_resetCounter_state(handle);
    
    
              if(ctrlState == CTRL_State_OnLine)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  _iq Id_target = TRAJ_getTargetValue(obj->trajHandle_Id);
    
                  // update the estimator state
                  bool flag_estStateChanged = EST_updateState(obj->estHandle,Id_target);
    
                  if(flag_estStateChanged)
                    {
                      // setup the controller
                      CTRL_setupCtrl(handle);
    
                      // setup the trajectory
                      CTRL_setupTraj(handle);
                    }
    
                  if(EST_isOnLine(obj->estHandle))
                    {
                      // setup the estimator for online state
                      CTRL_setupEstOnLineState(handle);
                    }
    
                  if(EST_isLockRotor(obj->estHandle) || 
                     (EST_isIdle(obj->estHandle) && EST_isMotorIdentified(obj->estHandle)))
                    {
                      // set the enable controller flag to false
                      CTRL_setFlag_enableCtrl(handle,false);
    
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_Idle);
                    }
                }
              else if(ctrlState == CTRL_State_OffLine)
                {
                  // set the next controller state
                  CTRL_setState(handle,CTRL_State_OnLine);
                }
              else if(ctrlState == CTRL_State_Idle)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  bool  flag_enableUserMotorParams = CTRL_getFlag_enableUserMotorParams(handle);
    
                  if(flag_enableUserMotorParams)
                    {
                      // initialize the motor parameters using values from the user.h file
                      CTRL_setUserMotorParams(handle);
                    }
    
                  if(EST_isIdle(obj->estHandle))
                    {
                      // setup the estimator for idle state
                      CTRL_setupEstIdleState(handle);
    
                      if(EST_isMotorIdentified(obj->estHandle))
                        {
                          if(CTRL_getFlag_enableOffset(handle))
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OffLine);
                            }
                          else
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OnLine);
                            }
                        }
                      else
                        {
                          // set the next controller state
                          CTRL_setState(handle,CTRL_State_OffLine);
                        }
                    }
                  else if(EST_isLockRotor(obj->estHandle))
                    {
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_OnLine);
                    }
                }
            }  // if(counter_ctrlState >= waitTime) loop
        } 
      else
        {
          CTRL_Obj *obj = (CTRL_Obj *)handle;
    
          // set the next controller state
          CTRL_setState(handle,CTRL_State_Idle);
    
          // set the estimator to idle
          if(!EST_isLockRotor(obj->estHandle))
            {
              if(EST_isMotorIdentified(obj->estHandle))
                {
                  EST_setIdle(obj->estHandle);
                }
              else
                {
                  EST_setIdle_all(obj->estHandle);
    
                  EST_setRs_pu(obj->estHandle,_IQ30(0.0));
                }
            }
        }
    
    
      // check to see if the state changed
      if(ctrlState != CTRL_getState(handle))
        {
          stateChanged = true;
        }
    
      return(stateChanged);
    } // end of CTRL_updateState() function
    
    // end of file
    

    1134.main.h

    3301.ctrl.h

    /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
     * *  Neither the name of Texas Instruments Incorporated nor the names of
     *    its contributors may be used to endorse or promote products derived
     *    from this software without specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    //! \file   solutions/instaspin_foc/src/proj_lab10a.c
    //! \brief Space Vector Over-Modulation
    //!
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    //! \defgroup PROJ_LAB10a PROJ_LAB10a
    //@{
    
    //! \defgroup PROJ_LAB10a_OVERVIEW Project Overview
    //!
    //! Experimentation with Space Vector Over-Modulation
    //!
    
    // **************************************************************************
    // the includes
    
    // system includes
    #include <math.h>
    #include "main.h"
    
    #ifdef FLASH
    #pragma CODE_SECTION(mainISR,"ramfuncs");
    #endif
    
    // Include header files used in the main function
    
    
    // **************************************************************************
    // the defines
    
    #define LED_BLINK_FREQ_Hz   5
    
    
    // **************************************************************************
    // the globals
    
    uint_least16_t gCounter_updateGlobals = 0;
    
    bool Flag_Latch_softwareUpdate = true;
    
    CTRL_Handle ctrlHandle;
    
    HAL_Handle halHandle;
    
    USER_Params gUserParams;
    
    HAL_PwmData_t gPwmData = {_IQ(0.0), _IQ(0.0), _IQ(0.0)};
    
    HAL_AdcData_t gAdcData;
    
    _iq gMaxCurrentSlope = _IQ(0.0);
    
    CTRL_Obj *controller_obj;
    
    #ifndef FAST_ROM_V1p6
    CTRL_Obj ctrl;				//v1p7 format
    #endif
    
    uint16_t gLEDcnt = 0;
    
    volatile MOTOR_Vars_t gMotorVars = MOTOR_Vars_INIT;
    
    
    #ifdef FLASH
    // Used for running BackGround in flash, and ISR in RAM
    extern uint16_t *RamfuncsLoadStart, *RamfuncsLoadEnd, *RamfuncsRunStart;
    #endif
    
    
    SVGENCURRENT_Obj svgencurrent;
    SVGENCURRENT_Handle svgencurrentHandle;
    
    
    #ifdef DRV8301_SPI
    // Watch window interface to the 8301 SPI
    DRV_SPI_8301_Vars_t gDrvSpi8301Vars;
    #endif
    
    // **************************************************************************
    // the functions
    
    void main(void)
    {
      uint_least8_t estNumber = 0;
    
    #ifdef FAST_ROM_V1p6
      uint_least8_t ctrlNumber = 0;
    #endif
    
      // Only used if running from FLASH
      // Note that the variable FLASH is defined by the project
      #ifdef FLASH
      // Copy time critical code and Flash setup code to RAM
      // The RamfuncsLoadStart, RamfuncsLoadEnd, and RamfuncsRunStart
      // symbols are created by the linker. Refer to the linker files.
      memCopy((uint16_t *)&RamfuncsLoadStart,(uint16_t *)&RamfuncsLoadEnd,(uint16_t *)&RamfuncsRunStart);
      #endif
    
    
      // initialize the hardware abstraction layer
      halHandle = HAL_init(&hal,sizeof(hal));
    
    
      // check for errors in user parameters
      USER_checkForErrors(&gUserParams);
    
    
      // store user parameter error in global variable
      gMotorVars.UserErrorCode = USER_getErrorCode(&gUserParams);
    
    
      // do not allow code execution if there is a user parameter error
      if(gMotorVars.UserErrorCode != USER_ErrorCode_NoError)
        {
          for(;;)
            {
              gMotorVars.Flag_enableSys = false;
            }
        }
    
    
      // initialize the user parameters
      USER_setParams(&gUserParams);
    
    
      // set the hardware abstraction layer parameters
      HAL_setParams(halHandle,&gUserParams);
    
    
      // initialize the controller
    #ifdef FAST_ROM_V1p6
      ctrlHandle = CTRL_initCtrl(ctrlNumber, estNumber);  		//v1p6 format (06xF and 06xM devices)
    #else
      ctrlHandle = CTRL_initCtrl(estNumber,&ctrl,sizeof(ctrl));	//v1p7 format default
    #endif
    
      controller_obj = (CTRL_Obj *)ctrlHandle;
    
    
      {
        CTRL_Version version;
    
        // get the version number
        CTRL_getVersion(ctrlHandle,&version);
    
        gMotorVars.CtrlVersion = version;
      }
    
    
      // set the default controller parameters
      CTRL_setParams(ctrlHandle,&gUserParams);
    
    
      // Initialize and setup the 100% SVM generator
      svgencurrentHandle = SVGENCURRENT_init(&svgencurrent,sizeof(svgencurrent));
    
      {
        float_t minWidth_microseconds = 2.0;
        uint16_t minWidth_counts = (uint16_t)(minWidth_microseconds * USER_SYSTEM_FREQ_MHz / 2.0) + HAL_PWM_DBFED_CNT;
    
        SVGENCURRENT_setMinWidth(svgencurrentHandle, minWidth_counts);
      }
    
    
      // setup faults
      HAL_setupFaults(halHandle);
    
    
      // initialize the interrupt vector table
      HAL_initIntVectorTable(halHandle);
    
    
      // enable the ADC interrupts
      HAL_enableAdcInts(halHandle);
    
    
      // enable global interrupts
      HAL_enableGlobalInts(halHandle);
    
    
      // enable debug interrupts
      HAL_enableDebugInt(halHandle);
    
    
      // disable the PWM
      HAL_disablePwm(halHandle);
    
    
    #ifdef DRV8301_SPI
      // turn on the DRV8301 if present
      HAL_enableDrv(halHandle);
      // initialize the DRV8301 interface
      HAL_setupDrvSpi(halHandle,&gDrvSpi8301Vars);
    #endif
    
    
      // enable DC bus compensation
      CTRL_setFlag_enableDcBusComp(ctrlHandle, true);
    
    
      for(;;)
      {
        // Waiting for enable system flag to be set
        while(!(gMotorVars.Flag_enableSys));
    
    
        // set the current bias
        HAL_setBias(halHandle,HAL_SensorType_Current,0,_IQ(I_A_offset));
        HAL_setBias(halHandle,HAL_SensorType_Current,1,_IQ(I_B_offset));
        HAL_setBias(halHandle,HAL_SensorType_Current,2,_IQ(I_C_offset));
    
        // set the voltage bias
        HAL_setBias(halHandle,HAL_SensorType_Voltage,0,_IQ(V_A_offset));
        HAL_setBias(halHandle,HAL_SensorType_Voltage,1,_IQ(V_B_offset));
        HAL_setBias(halHandle,HAL_SensorType_Voltage,2,_IQ(V_C_offset));
    
        // Enable the Library internal PI.  Iq is referenced by the speed PI now
        CTRL_setFlag_enableSpeedCtrl(ctrlHandle, true);
    
        // loop while the enable system flag is true
        while(gMotorVars.Flag_enableSys)
          {
            CTRL_Obj *obj = (CTRL_Obj *)ctrlHandle;
    
            // increment counters
            gCounter_updateGlobals++;
    
            // enable/disable the use of motor parameters being loaded from user.h
            CTRL_setFlag_enableUserMotorParams(ctrlHandle,gMotorVars.Flag_enableUserParams);
    
            // enable/disable Rs recalibration during motor startup
            EST_setFlag_enableRsRecalc(obj->estHandle,gMotorVars.Flag_enableRsRecalc);
    
            // enable/disable automatic calculation of bias values
            CTRL_setFlag_enableOffset(ctrlHandle,gMotorVars.Flag_enableOffsetcalc);
    
    
            if(CTRL_isError(ctrlHandle))
              {
                // set the enable controller flag to false
                CTRL_setFlag_enableCtrl(ctrlHandle,false);
    
                // set the enable system flag to false
                gMotorVars.Flag_enableSys = false;
    
                // disable the PWM
                HAL_disablePwm(halHandle);
              }
            else
              {
                // update the controller state
                bool flag_ctrlStateChanged = CTRL_updateState(ctrlHandle);
    
                // enable or disable the control
                CTRL_setFlag_enableCtrl(ctrlHandle, gMotorVars.Flag_Run_Identify);
    
                if(flag_ctrlStateChanged)
                  {
                    CTRL_State_e ctrlState = CTRL_getState(ctrlHandle);
    
                    if(ctrlState == CTRL_State_OffLine)
                      {
                        // enable the PWM
                        HAL_enablePwm(halHandle);
                      }
                    else if(ctrlState == CTRL_State_OnLine)
                      {
                        // update the ADC bias values
                        HAL_updateAdcBias(halHandle);
    
    
                        // enable the PWM
                        HAL_enablePwm(halHandle);
                      }
                    else if(ctrlState == CTRL_State_Idle)
                      {
                        // disable the PWM
                        HAL_disablePwm(halHandle);
                        gMotorVars.Flag_Run_Identify = false;
                      }
                  }
              }
    
    
            if(EST_isMotorIdentified(obj->estHandle))
              {
                _iq Id_squared_pu = _IQmpy(CTRL_getId_ref_pu(ctrlHandle),CTRL_getId_ref_pu(ctrlHandle));
    
    
                //Set the maximum current controller output for the Iq and Id current controllers to enable
                //over-modulation.
                //An input into the SVM above 2/SQRT(3) = 1.1547 is in the over-modulation region.  An input of 1.1547 is where
                //the crest of the sinewave touches the 100% duty cycle.  At an input of 4/3, the SVM generator
                //produces a trapezoidal waveform touching every corner of the hexagon
                CTRL_setMaxVsMag_pu(ctrlHandle,gMotorVars.OverModulation);
    
                // set the current ramp
                EST_setMaxCurrentSlope_pu(obj->estHandle,gMaxCurrentSlope);
                gMotorVars.Flag_MotorIdentified = true;
    
                // set the speed reference
                CTRL_setSpd_ref_krpm(ctrlHandle,gMotorVars.SpeedRef_krpm);
    
                // set the speed acceleration
                CTRL_setMaxAccel_pu(ctrlHandle,_IQmpy(MAX_ACCEL_KRPMPS_SF,gMotorVars.MaxAccel_krpmps));
                if(Flag_Latch_softwareUpdate)
                {
                  Flag_Latch_softwareUpdate = false;
    
    #ifdef FAST_ROM_V1p6
                  if(CTRL_getFlag_enableUserMotorParams(ctrlHandle) == true)
                  {
                      // call this function to fix 1p6
                      softwareUpdate1p6(ctrlHandle);
                  }
    #endif
    
                  calcPIgains(ctrlHandle);
    
                  // initialize the watch window kp and ki current values with pre-calculated values
                  gMotorVars.Kp_Idq = CTRL_getKp(ctrlHandle,CTRL_Type_PID_Id);
                  gMotorVars.Ki_Idq = CTRL_getKi(ctrlHandle,CTRL_Type_PID_Id);
                }
    
              }
            else
              {
                Flag_Latch_softwareUpdate = true;
    
                // initialize the watch window kp and ki values with pre-calculated values
                gMotorVars.Kp_spd = CTRL_getKp(ctrlHandle,CTRL_Type_PID_spd);
                gMotorVars.Ki_spd = CTRL_getKi(ctrlHandle,CTRL_Type_PID_spd);
    
    
                // the estimator sets the maximum current slope during identification
                gMaxCurrentSlope = EST_getMaxCurrentSlope_pu(obj->estHandle);
              }
    
    
            // when appropriate, update the global variables
            if(gCounter_updateGlobals >= NUM_MAIN_TICKS_FOR_GLOBAL_VARIABLE_UPDATE)
              {
                // reset the counter
                gCounter_updateGlobals = 0;
    
                updateGlobalVariables_motor(ctrlHandle);
              }
    
    
            // update Kp and Ki gains
            updateKpKiGains(ctrlHandle);
    
            // enable/disable the forced angle
            EST_setFlag_enableForceAngle(obj->estHandle,gMotorVars.Flag_enableForceAngle);
    
            // enable or disable power warp
            CTRL_setFlag_enablePowerWarp(ctrlHandle,gMotorVars.Flag_enablePowerWarp);
    
    #ifdef DRV8301_SPI
            HAL_writeDrvData(halHandle,&gDrvSpi8301Vars);
    
            HAL_readDrvData(halHandle,&gDrvSpi8301Vars);
    #endif
    
          } // end of while(gFlag_enableSys) loop
    
    
        // disable the PWM
        HAL_disablePwm(halHandle);
    
        // set the default controller parameters (Reset the control to re-identify the motor)
        CTRL_setParams(ctrlHandle,&gUserParams);
        gMotorVars.Flag_Run_Identify = false;
    
      } // end of for(;;) loop
    
    } // end of main() function
    
    
    interrupt void mainISR(void)
    {
      // toggle status LED
      if(gLEDcnt++ > (uint_least32_t)(USER_ISR_FREQ_Hz / LED_BLINK_FREQ_Hz))
      {
        HAL_toggleLed(halHandle,(GPIO_Number_e)HAL_Gpio_LED2);
        gLEDcnt = 0;
      }
    
    
      // acknowledge the ADC interrupt
      HAL_acqAdcInt(halHandle,ADC_IntNumber_1);
    
    
      // convert the ADC data
      HAL_readAdcData(halHandle,&gAdcData);
    
    
      // run the current reconstruction algorithm
      SVGENCURRENT_RunRegenCurrent(svgencurrentHandle, (MATH_vec3 *)(gAdcData.I.value));
    
    
      // run the controller
      CTRL_run(ctrlHandle,halHandle,&gAdcData,&gPwmData);
    
    
      // write the PWM compare values
      HAL_writePwmData(halHandle,&gPwmData);
    
    
      // run the current ignore algorithm
      {
        uint16_t pwmValue_1 = HAL_readPwmCmpA(halHandle,PWM_Number_1);
        uint16_t pwmValue_2 = HAL_readPwmCmpA(halHandle,PWM_Number_2);
        uint16_t pwmValue_3 = HAL_readPwmCmpA(halHandle,PWM_Number_3);
    
        // run the current ignore algorithm
        SVGENCURRENT_RunIgnoreShunt(svgencurrentHandle,pwmValue_1,pwmValue_2,pwmValue_3);
      }
    
        gMotorVars.Ia = CTRL_getIa_in_pu(ctrlHandle);
    
      // Set trigger point in the middle of the low side pulse
      HAL_setTrigger(halHandle,SVGENCURRENT_getMinWidth(svgencurrentHandle));
    
    
      // setup the controller
      CTRL_setup(ctrlHandle);
    
    
      return;
    } // end of mainISR() function
    
    
    void updateGlobalVariables_motor(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      // get the speed estimate
      gMotorVars.Speed_krpm = EST_getSpeed_krpm(obj->estHandle);
    
      // get the real time speed reference coming out of the speed trajectory generator
      gMotorVars.SpeedTraj_krpm = _IQmpy(CTRL_getSpd_int_ref_pu(handle),EST_get_pu_to_krpm_sf(obj->estHandle));
    
      // get the torque estimate
      gMotorVars.Torque_lbin = calcTorque_lbin(handle);
    
      // get the magnetizing current
      gMotorVars.MagnCurr_A = EST_getIdRated(obj->estHandle);
    
      // get the rotor resistance
      gMotorVars.Rr_Ohm = EST_getRr_Ohm(obj->estHandle);
    
      // get the stator resistance
      gMotorVars.Rs_Ohm = EST_getRs_Ohm(obj->estHandle);
    
      // get the stator inductance in the direct coordinate direction
      gMotorVars.Lsd_H = EST_getLs_d_H(obj->estHandle);
    
      // get the stator inductance in the quadrature coordinate direction
      gMotorVars.Lsq_H = EST_getLs_q_H(obj->estHandle);
    
      // get the flux
      gMotorVars.Flux_VpHz = EST_getFlux_VpHz(obj->estHandle);
    
      // get the controller state
      gMotorVars.CtrlState = CTRL_getState(handle);
    
      // get the estimator state
      gMotorVars.EstState = EST_getState(obj->estHandle);
    
      // read Vd and Vq vectors per units
      gMotorVars.Vd = CTRL_getVd_out_pu(ctrlHandle);
      gMotorVars.Vq = CTRL_getVq_out_pu(ctrlHandle);
    
      // calculate vector Vs in per units
      gMotorVars.Vs = _IQsqrt(_IQmpy(gMotorVars.Vd, gMotorVars.Vd) + _IQmpy(gMotorVars.Vq, gMotorVars.Vq));
    
      // read Id and Iq vectors in amps
      gMotorVars.Id_A = _IQmpy(CTRL_getId_in_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_CURRENT_A));
      gMotorVars.Iq_A = _IQmpy(CTRL_getIq_in_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_CURRENT_A));
    
      // calculate vector Is in amps
      gMotorVars.Is_A = _IQsqrt(_IQmpy(gMotorVars.Id_A, gMotorVars.Id_A) + _IQmpy(gMotorVars.Iq_A, gMotorVars.Iq_A));
    
      // Get the DC buss voltage
      gMotorVars.VdcBus_kV = _IQmpy(gAdcData.dcBus,_IQ(USER_IQ_FULL_SCALE_VOLTAGE_V/1000.0));
    
      return;
    } // end of updateGlobalVariables_motor() function
    
    
    void updateKpKiGains(CTRL_Handle handle)
    {
      if((gMotorVars.CtrlState == CTRL_State_OnLine) && (gMotorVars.Flag_MotorIdentified == true) && (Flag_Latch_softwareUpdate == false))
        {
          // set the kp and ki speed values from the watch window
          CTRL_setKp(handle,CTRL_Type_PID_spd,gMotorVars.Kp_spd);
          CTRL_setKi(handle,CTRL_Type_PID_spd,gMotorVars.Ki_spd);
    
          // set the kp and ki current values for Id and Iq from the watch window
          CTRL_setKp(handle,CTRL_Type_PID_Id,gMotorVars.Kp_Idq);
          CTRL_setKi(handle,CTRL_Type_PID_Id,gMotorVars.Ki_Idq);
          CTRL_setKp(handle,CTRL_Type_PID_Iq,gMotorVars.Kp_Idq);
          CTRL_setKi(handle,CTRL_Type_PID_Iq,gMotorVars.Ki_Idq);
    	}
    
      return;
    } // end of updateKpKiGains() function
    
    
    #ifdef FAST_ROM_V1p6
    void softwareUpdate1p6(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t fullScaleInductance = EST_getFullScaleInductance(obj->estHandle);
      float_t Ls_coarse_max = _IQ30toF(EST_getLs_coarse_max_pu(obj->estHandle));
      int_least8_t lShift = ceil(log(obj->motorParams.Ls_d_H/(Ls_coarse_max*fullScaleInductance))/log(2.0));
      uint_least8_t Ls_qFmt = 30 - lShift;
      float_t L_max = fullScaleInductance * pow(2.0,lShift);
      _iq Ls_d_pu = _IQ30(obj->motorParams.Ls_d_H / L_max);
      _iq Ls_q_pu = _IQ30(obj->motorParams.Ls_q_H / L_max);
    
    
      // store the results
      EST_setLs_d_pu(obj->estHandle,Ls_d_pu);
      EST_setLs_q_pu(obj->estHandle,Ls_q_pu);
      EST_setLs_qFmt(obj->estHandle,Ls_qFmt);
    
      return;
    } // end of softwareUpdate1p6() function
    #endif
    
    void calcPIgains(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t Ls_d = EST_getLs_d_H(obj->estHandle);
      float_t Ls_q = EST_getLs_q_H(obj->estHandle);
      float_t Rs = EST_getRs_Ohm(obj->estHandle);
      float_t RoverLs_d = Rs/Ls_d;
      float_t RoverLs_q = Rs/Ls_q;
      float_t fullScaleCurrent = EST_getFullScaleCurrent(obj->estHandle);
      float_t fullScaleVoltage = EST_getFullScaleVoltage(obj->estHandle);
      float_t ctrlPeriod_sec = CTRL_getCtrlPeriod_sec(handle);
      _iq Kp_Id = _IQ((0.25*Ls_d*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Id = _IQ(RoverLs_d*ctrlPeriod_sec);
      _iq Kp_Iq = _IQ((0.25*Ls_q*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Iq = _IQ(RoverLs_q*ctrlPeriod_sec);
      _iq Kd = _IQ(0.0);
    
      // set the Id controller gains
      PID_setKi(obj->pidHandle_Id,Ki_Id);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp_Id,Ki_Id,Kd);
    
      // set the Iq controller gains
      PID_setKi(obj->pidHandle_Iq,Ki_Iq);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp_Iq,Ki_Iq,Kd);
    
      return;
    } // end of calcPIgains() function
    
    float_t calcTorque_Nm(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      float_t Id_A = _IQtoF(PID_getFbackValue(obj->pidHandle_Id)) * USER_IQ_FULL_SCALE_CURRENT_A;
      float_t Iq_A = _IQtoF(PID_getFbackValue(obj->pidHandle_Iq)) * USER_IQ_FULL_SCALE_CURRENT_A;
      float_t Polepairs = (float_t)USER_MOTOR_NUM_POLE_PAIRS;
      float_t Flux_Wb = EST_getFlux_Wb(obj->estHandle);
      float_t Lsd_H = EST_getLs_d_H(obj->estHandle);
      float_t Lsq_H = EST_getLs_q_H(obj->estHandle);
    
      return((Flux_Wb * Iq_A + (Lsd_H - Lsq_H) * Id_A * Iq_A) * Polepairs * 1.5);
    } // end of calcTorque_Nm() function
    
    
    float_t calcTorque_lbin(CTRL_Handle handle)
    {
    
      return(calcTorque_Nm(handle) * MATH_Nm_TO_lbin_SF);
    } // end of calcTorque_lbin() function
    
    
    //@} //defgroup
    // end of file
    
    
    
    

     

  • So weird... seems the only solution is to go back to the original files and re-do the changes...

    Could you help post me the ORIGINAL main.h and proj_lab05.c ? I'm using MW11.

  • 4452.main.h

    /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, LineStream Technologies Incorporated
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
    * *  Neither the names of Texas Instruments Incorporated, LineStream
     *    Technologies Incorporated, nor the names of its contributors may be
     *    used to endorse or promote products derived from this software without
     *    specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    //! \file   solutions/instaspin_motion/src/proj_lab05c.c
    //! \brief  InstaSPIN-MOTION Inertia Identification
    //!
    //! (C) Copyright 2012, LineStream Technologies, Inc.
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    //! \defgroup PROJ_LAB05c PROJ_LAB05c
    //@{
    
    //! \defgroup PROJ_LAB05c_OVERVIEW Project Overview
    //!
    //! InstaSPIN-MOTION Inertia Identification
    //!
    
    // **************************************************************************
    // the includes
    
    // system includes
    #include <math.h>
    #include "main.h"
    
    #ifdef FLASH
    #pragma CODE_SECTION(mainISR,"ramfuncs");
    #endif
    
    // Include header files used in the main function
    
    
    // **************************************************************************
    // the defines
    
    #define LED_BLINK_FREQ_Hz   5
    
    
    // **************************************************************************
    // the globals
    
    uint_least16_t gCounter_updateGlobals = 0;
    
    bool Flag_Latch_softwareUpdate = true;
    
    CTRL_Handle ctrlHandle;
    
    DRV_Handle drvHandle;
    
    USER_Params gUserParams;
    
    DRV_PwmData_t gPwmData;
    
    DRV_AdcData_t gAdcData;
    
    _iq gMaxCurrentSlope = _IQ(0.0);
    
    #ifdef FAST_ROM_V1p6
    CTRL_Obj *controller_obj;
    #else
    CTRL_Obj ctrl;				//v1p7 format
    #endif
    
    ST_Obj st_obj;
    ST_Handle stHandle;
    
    uint16_t gLEDcnt = 0;
    
    volatile MOTOR_Vars_t gMotorVars = MOTOR_Vars_INIT;
    
    #ifdef FLASH
    // Used for running BackGround in flash, and ISR in RAM
    extern uint16_t *RamfuncsLoadStart, *RamfuncsLoadEnd, *RamfuncsRunStart;
    #endif
    
    
    #ifdef DRV8301_SPI
    // Watch window interface to the 8301 SPI
    DRV_SPI_8301_Vars_t gDrvSpi8301Vars;
    #endif
    
    // **************************************************************************
    // the functions
    
    void main(void)
    {
      uint_least8_t estNumber = 0;
    
    #ifdef FAST_ROM_V1p6
      uint_least8_t ctrlNumber = 0;
    #endif
    
      // Only used if running from FLASH
      // Note that the variable FLASH is defined by the project
      #ifdef FLASH
      // Copy time critical code and Flash setup code to RAM
      // The RamfuncsLoadStart, RamfuncsLoadEnd, and RamfuncsRunStart
      // symbols are created by the linker. Refer to the linker files.
      memCopy((uint16_t *)&RamfuncsLoadStart,(uint16_t *)&RamfuncsLoadEnd,(uint16_t *)&RamfuncsRunStart);
      #endif
    
      // initialize the driver
      drvHandle = DRV_init(&drv,sizeof(drv));
    
    
      // initialize the user parameters
      USER_setParams(&gUserParams);
    
    
      // set the driver parameters
      DRV_setParams(drvHandle,&gUserParams);
    
    
      // initialize the controller
    #ifdef FAST_ROM_V1p6
      ctrlHandle = CTRL_initCtrl(ctrlNumber, estNumber);  		//v1p6 format (06xF and 06xM devices)
      controller_obj = (CTRL_Obj *)ctrlHandle;
    #else
      ctrlHandle = CTRL_initCtrl(estNumber,&ctrl,sizeof(ctrl));	//v1p7 format default
    #endif
    
    
      // set the default controller parameters
      CTRL_setParams(ctrlHandle,&gUserParams);
    
    
      // setup faults
      DRV_setupFaults(drvHandle);
    
    
      // initialize the interrupt vector table
      DRV_initIntVectorTable(drvHandle);
    
    
      // enable the ADC interrupts
      DRV_enableAdcInts(drvHandle);
    
    
      // enable global interrupts
      DRV_enableGlobalInts(drvHandle);
    
    
      // enable debug interrupts
      DRV_enableDebugInt(drvHandle);
    
    
      // disable the PWM
      DRV_disablePwm(drvHandle);
    
    
      // enable DC bus compensation
      CTRL_setFlag_enableDcBusComp(ctrlHandle, true);
    
    
      // initialize the SpinTAC Components
      stHandle = ST_init(&st_obj, sizeof(st_obj));
      
      
      // setup the SpinTAC Components
      ST_setupVelId(stHandle);
    
    
    #ifdef DRV8301_SPI
      // turn on the DRV8301 if present
      DRV_enable8301(drvHandle);
      // initialize the DRV8301 interface
      DRV_8301_SpiInterface_init(drvHandle,&gDrvSpi8301Vars);
    #endif
    
    
      for(;;)
      {
        // Waiting for enable system flag to be set
        while(!(gMotorVars.Flag_enableSys));
    
        Flag_Latch_softwareUpdate = true;
    
        // Dis-able the Library internal PI.  Iq has no reference now
        CTRL_setFlag_enableSpeedCtrl(ctrlHandle, true);
    
        // loop while the enable system flag is true
        while(gMotorVars.Flag_enableSys)
          {
            CTRL_Obj *obj = (CTRL_Obj *)ctrlHandle;
            ST_Obj *stObj = (ST_Obj *)stHandle;
    
            // increment counters
            gCounter_updateGlobals++;
    
            // enable/disable the use of motor parameters being loaded from user.h
            CTRL_setFlag_enableUserMotorParams(ctrlHandle,gMotorVars.Flag_enableUserParams);
    
            // enable/disable Rs recalibration during motor startup
            EST_setFlag_enableRsRecalc(obj->estHandle,gMotorVars.Flag_enableRsRecalc);
    
            // enable/disable automatic calculation of bias values
            CTRL_setFlag_enableOffset(ctrlHandle,gMotorVars.Flag_enableOffsetcalc);
    
    
            if(CTRL_isError(ctrlHandle))
              {
                // set the enable controller flag to false
                CTRL_setFlag_enableCtrl(ctrlHandle,false);
    
                // set the enable system flag to false
                gMotorVars.Flag_enableSys = false;
    
                // disable the PWM
                DRV_disablePwm(drvHandle);
              }
            else
              {
                // update the controller state
                bool flag_ctrlStateChanged = CTRL_updateState(ctrlHandle);
    
                // enable or disable the control
                CTRL_setFlag_enableCtrl(ctrlHandle, gMotorVars.Flag_Run_Identify);
    
                if(flag_ctrlStateChanged)
                  {
                    CTRL_State_e ctrlState = CTRL_getState(ctrlHandle);
    
                    if(ctrlState == CTRL_State_OffLine)
                      {
                        // enable the PWM
                        DRV_enablePwm(drvHandle);
                      }
                    else if(ctrlState == CTRL_State_OnLine)
                      {
                        if(gMotorVars.Flag_enableOffsetcalc == true)
                        {
                          // update the ADC bias values
                          DRV_updateAdcBias(drvHandle);
                        }
                        else
                        {
                          // set the current bias
                          DRV_setBias(drvHandle,DRV_SensorType_Current,0,_IQ(I_A_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Current,1,_IQ(I_B_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Current,2,_IQ(I_C_offset));
    
                          // set the voltage bias
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,0,_IQ(V_A_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,1,_IQ(V_B_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,2,_IQ(V_C_offset));
                        }
    
                        // enable the PWM
                        DRV_enablePwm(drvHandle);
                      }
                    else if(ctrlState == CTRL_State_Idle)
                      {
                        // disable the PWM
                        DRV_disablePwm(drvHandle);
                        gMotorVars.Flag_Run_Identify = false;
                      }
                  }
              }
    
    
            if(EST_isMotorIdentified(obj->estHandle))
              {
                // set the current ramp
                EST_setMaxCurrentSlope_pu(obj->estHandle,gMaxCurrentSlope);
                gMotorVars.Flag_MotorIdentified = true;
    
                // set the speed reference
                CTRL_setSpd_ref_krpm(ctrlHandle,gMotorVars.SpeedRef_krpm);
    
                // set the speed acceleration
                CTRL_setMaxAccel_pu(ctrlHandle,_IQmpy(MAX_ACCEL_KRPMPS_SF,gMotorVars.MaxAccel_krpmps));
    
                if(Flag_Latch_softwareUpdate)
                {
                  Flag_Latch_softwareUpdate = false;
    
    #ifdef FAST_ROM_V1p6
                  if(CTRL_getFlag_enableUserMotorParams(ctrlHandle) == true)
                  {
                      // call this function to fix 1p6
                      softwareUpdate1p6(ctrlHandle);
                  }
    #endif
    
                  calcPIgains(ctrlHandle);
    
                  // initializes the value for GoalSpeed and TorqueRampTime
                  gMotorVars.SpinTAC.VelIdGoalSpeed_krpm = _IQmpy(STVELID_getVelocityPositive(stObj->velIdHandle), _IQ(ST_SPEED_KRPM_PER_PU));
                  gMotorVars.SpinTAC.VelIdTorqueRampTime_sec = STVELID_getTorqueRampTime_sec(stObj->velIdHandle);
    
                }
              }
            else
              {
                Flag_Latch_softwareUpdate = true;
    
                // the estimator sets the maximum current slope during identification
                gMaxCurrentSlope = EST_getMaxCurrentSlope_pu(obj->estHandle);
              }
    
    
            // when appropriate, update the global variables
            if(gCounter_updateGlobals >= NUM_MAIN_TICKS_FOR_GLOBAL_VARIABLE_UPDATE)
              {
                // reset the counter
                gCounter_updateGlobals = 0;
    
                updateGlobalVariables_motor(ctrlHandle, stHandle);
              }
    
          } // end of while(gFlag_enableSys) loop
    
    
        // disable the PWM
        DRV_disablePwm(drvHandle);
    
        // set the default controller parameters (Reset the control to re-identify the motor)
        CTRL_setParams(ctrlHandle,&gUserParams);
    
        // setup the SpinTAC Components
        ST_setupVelId(stHandle);
    
      } // end of for(;;) loop
    
    } // end of main() function
    
    
    interrupt void mainISR(void)
    {
    
      static uint16_t stCnt = 0;
    
      // DPM - toggle status LED
      if(gLEDcnt++ > (uint_least32_t)(USER_PWM_FREQ_kHz * 1000 / LED_BLINK_FREQ_Hz)) {
        DRV_toggleLed(drvHandle,(GPIO_Number_e)DRV_Gpio_LED2);
        gLEDcnt = 0;
      }
    
    
      // acknowledge the ADC interrupt
      DRV_acqAdcInt(drvHandle,ADC_IntNumber_1);
    
    
      // convert the ADC data
      DRV_readAdcData(drvHandle,&gAdcData);
    
    
      // Run the SpinTAC Components
      if(stCnt++ >= ISR_TICKS_PER_SPINTAC_TICK) {
    	  ST_runVelId(stHandle, ctrlHandle);
    	  stCnt = 1;
      }
    
    
      // run the controller
      CTRL_run(ctrlHandle,drvHandle,&gAdcData,&gPwmData);
    
    
      // write the PWM compare values
      DRV_writePwmData(drvHandle,&gPwmData);
    
    
      // setup the controller
      CTRL_setup(ctrlHandle);
    
    
      return;
    } // end of mainISR() function
    
    
    void updateGlobalVariables_motor(CTRL_Handle handle, ST_Handle sthandle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      ST_Obj *stObj = (ST_Obj *)sthandle;
    
    
      // get the speed estimate
      gMotorVars.Speed_krpm = EST_getSpeed_krpm(obj->estHandle);
    
      // get the torque estimate
      gMotorVars.Torque_lbin = EST_getTorque_lbin(obj->estHandle);
    
      // get the magnetizing current
      gMotorVars.MagnCurr_A = EST_getIdRated(obj->estHandle);
    
      // get the rotor resistance
      gMotorVars.Rr_Ohm = EST_getRr_Ohm(obj->estHandle);
    
      // get the stator resistance
      gMotorVars.Rs_Ohm = EST_getRs_Ohm(obj->estHandle);
    
      // get the stator inductance in the direct coordinate direction
      gMotorVars.Lsd_H = EST_getLs_d_H(obj->estHandle);
    
      // get the stator inductance in the quadrature coordinate direction
      gMotorVars.Lsq_H = EST_getLs_q_H(obj->estHandle);
    
      // get the flux
      gMotorVars.Flux_VpHz = EST_getFlux_VpHz(obj->estHandle);
    
      // get the controller state
      gMotorVars.CtrlState = CTRL_getState(handle);
    
      // get the estimator state
      gMotorVars.EstState = EST_getState(obj->estHandle);
    
      // get Velocity Identify status
      gMotorVars.SpinTAC.VelIdStatus = STVELID_getStatus(stObj->velIdHandle);
    
      // get the inertia estimate
      gMotorVars.SpinTAC.InertiaEstimate_Aperkrpm = _IQmpy(STVELID_getInertiaEstimate(stObj->velIdHandle), _IQ(ST_SPEED_PU_PER_KRPM * USER_IQ_FULL_SCALE_CURRENT_A));
    
      // get the friction estimate
      gMotorVars.SpinTAC.FrictionEstimate_Aperkrpm = _IQmpy(STVELID_getFrictionEstimate(stObj->velIdHandle), _IQ(ST_SPEED_PU_PER_KRPM * USER_IQ_FULL_SCALE_CURRENT_A));
    
      // get the Velocity Identify error
      gMotorVars.SpinTAC.VelIdErrorID = STVELID_getErrorID(stObj->velIdHandle);
    
      // enable/disable the forced angle
      EST_setFlag_enableForceAngle(obj->estHandle,gMotorVars.Flag_enableForceAngle);
    
      // enable or disable power warp
      CTRL_setFlag_enableEpl(handle,gMotorVars.Flag_enableEpl);
    
    #ifdef DRV8301_SPI
      DRV_8301_SpiInterface(drvHandle,&gDrvSpi8301Vars);
    #endif
    
      return;
    } // end of updateGlobalVariables_motor() function
    
    #ifdef FAST_ROM_V1p6
    void softwareUpdate1p6(CTRL_Handle handle)
    {
    
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t fullScaleInductance = EST_getFullScaleInductance(obj->estHandle);
      float_t Ls_coarse_max = _IQ30toF(EST_getLs_coarse_max_pu(obj->estHandle));
      int_least8_t lShift = ceil(log(obj->motorParams.Ls_d/(Ls_coarse_max*fullScaleInductance))/log(2.0));
      uint_least8_t Ls_qFmt = 30 - lShift;
      float_t L_max = fullScaleInductance * pow(2.0,lShift);
      _iq Ls_d_pu = _IQ30(obj->motorParams.Ls_d / L_max);
      _iq Ls_q_pu = _IQ30(obj->motorParams.Ls_q / L_max);
    
    
      // store the results
      EST_setLs_d_pu(obj->estHandle,Ls_d_pu);
      EST_setLs_q_pu(obj->estHandle,Ls_q_pu);
      EST_setLs_qFmt(obj->estHandle,Ls_qFmt);
    
      return;
    } // end of softwareUpdate1p6() function
    #endif
    
    void calcPIgains(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t Ls_d = EST_getLs_d_H(obj->estHandle);
      float_t Ls_q = EST_getLs_q_H(obj->estHandle);
      float_t Rs = EST_getRs_Ohm(obj->estHandle);
      float_t RoverLs_d = Rs/Ls_d;
      float_t RoverLs_q = Rs/Ls_q;
      float_t fullScaleCurrent = EST_getFullScaleCurrent(obj->estHandle);
      float_t fullScaleVoltage = EST_getFullScaleVoltage(obj->estHandle);
      float_t ctrlPeriod_sec = CTRL_getCtrlPeriod_sec(handle);
      _iq Kp_Id = _IQ((0.25*Ls_d*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Id = _IQ(RoverLs_d*ctrlPeriod_sec);
      _iq Kp_Iq = _IQ((0.25*Ls_q*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Iq = _IQ(RoverLs_q*ctrlPeriod_sec);
      _iq Kd = _IQ(0.0);
    
      // set the Id controller gains
      PID_setKi(obj->pidHandle_Id,Ki_Id);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp_Id,Ki_Id,Kd);
    
      // set the Iq controller gains
      PID_setKi(obj->pidHandle_Iq,Ki_Iq);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp_Iq,Ki_Iq,Kd);
    
      return;
    } // end of calcPIgains() function
    
    
    void ST_runVelId(ST_Handle sthandle, CTRL_Handle handle)
    {
    
        _iq speedFeedback, iqReference;
        ST_Obj *stObj = (ST_Obj *)sthandle;
        CTRL_Obj *ctrlObj = (CTRL_Obj *)handle;
    
        // Get the mechanical speed in pu
        speedFeedback = EST_getFm_pu(ctrlObj->estHandle);
    
    	if(gMotorVars.SpinTAC.VelIdRun == true) {
    		// if beginning the SpinTAC Identify process
    		// set the speed reference to zero
    		gMotorVars.SpeedRef_krpm = 0;
    		// wait until the actual speed is zero
    		if((_IQabs(speedFeedback) < _IQ(ST_MIN_ID_SPEED_PU)) && (STVELID_getEnable(stObj->velIdHandle) == false)) {
    			CTRL_setFlag_enableSpeedCtrl(ctrlHandle, false);
    			gMotorVars.Flag_enableForceAngle = true;
    			EST_setFlag_enableForceAngle(ctrlObj->estHandle, gMotorVars.Flag_enableForceAngle);
    			// set the GoalSpeed
    			STVELID_setVelocityPositive(stObj->velIdHandle, _IQmpy(gMotorVars.SpinTAC.VelIdGoalSpeed_krpm, _IQ(ST_SPEED_PU_PER_KRPM)));
    			// set the Torque Ramp Time
    			STVELID_setTorqueRampTime_sec(stObj->velIdHandle, gMotorVars.SpinTAC.VelIdTorqueRampTime_sec);
    			// Enable SpinTAC Inertia Identify
    			STVELID_setEnable(stObj->velIdHandle, true);
    			// Set a positive speed reference to FAST to provide direction information
    			gMotorVars.SpeedRef_krpm = _IQ(0.001);
    			CTRL_setSpd_ref_krpm(ctrlHandle, gMotorVars.SpeedRef_krpm);
    		}
    	}
    
    	// Run SpinTAC Inertia Identify
    	STVELID_setVelocityFeedback(stObj->velIdHandle, speedFeedback);
    	STVELID_run(stObj->velIdHandle);
    
    	if(STVELID_getDone(stObj->velIdHandle) == true) {
    		// If inertia identification is successful, update the inertia setting of SpinTAC Velocity Controller
    		// EXAMPLE: STVELCTL_setInertia(stObj->velCtlHandle, STVELID_getInertiaEstimate(stObj->velIdHandle));
    		gMotorVars.SpinTAC.VelIdRun = false;
    		// return the speed reference to zero
    		gMotorVars.SpeedRef_krpm = gMotorVars.StopSpeedRef_krpm;
    		CTRL_setFlag_enableSpeedCtrl(ctrlHandle, true);
    		CTRL_setSpd_ref_krpm(ctrlHandle, gMotorVars.SpeedRef_krpm);
    	}
    	else if((STVELID_getErrorID(stObj->velIdHandle) != false) && (STVELID_getErrorID(stObj->velIdHandle) != ST_ID_INCOMPLETE_ERROR)) {
    	// if not done & in error, wait until speed is less than 1RPM to exit
    		if(_IQabs(speedFeedback) < _IQ(ST_MIN_ID_SPEED_PU)) {
    			gMotorVars.SpinTAC.VelIdRun = false;
    			// return the speed reference to zero
    			gMotorVars.SpeedRef_krpm = gMotorVars.StopSpeedRef_krpm;
    			CTRL_setFlag_enableSpeedCtrl(ctrlHandle, true);
    			CTRL_setSpd_ref_krpm(ctrlHandle, gMotorVars.SpeedRef_krpm);
    		}
    	}
    
    	// select SpinTAC Identify
    	iqReference = STVELID_getTorqueReference(stObj->velIdHandle);
    
    	// Set the Iq reference that came out of SpinTAC Velocity Control
    	CTRL_setIq_ref_pu(ctrlHandle, iqReference);
    }
    //@} //defgroup
    // end of file
    

    these are from MW _11

     

  • Sorry, chris.

    I meant proj_lab5f.c

  • /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, LineStream Technologies Incorporated
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
    * *  Neither the names of Texas Instruments Incorporated, LineStream
     *    Technologies Incorporated, nor the names of its contributors may be
     *    used to endorse or promote products derived from this software without
     *    specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    //! \file   solutions/instaspin_motion/src/proj_lab05f.c
    //! \brief  Comparing performance of PI velocity controller & SpinTAC velocity controller
    //!
    //! (C) Copyright 2012, LineStream Technologies, Inc.
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    //! \defgroup PROJ_LAB05f PROJ_LAB05f
    //@{
    
    //! \defgroup PROJ_LAB05f_OVERVIEW Project Overview
    //!
    //! Comparing performance of PI velocity controller & SpinTAC velocity controller
    //!
    
    // **************************************************************************
    // the includes
    
    // system includes
    #include <math.h>
    #include "main.h"
    
    #ifdef FLASH
    #pragma CODE_SECTION(mainISR,"ramfuncs");
    #endif
    
    // Include header files used in the main function
    
    
    // **************************************************************************
    // the defines
    
    #define LED_BLINK_FREQ_Hz   5
    
    
    // **************************************************************************
    // the globals
    
    uint_least16_t gCounter_updateGlobals = 0;
    
    bool Flag_Latch_softwareUpdate = true;
    
    CTRL_Handle ctrlHandle;
    
    DRV_Handle drvHandle;
    
    USER_Params gUserParams;
    
    DRV_PwmData_t gPwmData;
    
    DRV_AdcData_t gAdcData;
    
    _iq gMaxCurrentSlope = _IQ(0.0);
    
    #ifdef FAST_ROM_V1p6
    CTRL_Obj *controller_obj;
    #else
    CTRL_Obj ctrl;				//v1p7 format
    #endif
    
    ST_Obj st_obj;
    ST_Handle stHandle;
    
    uint16_t gLEDcnt = 0;
    
    volatile MOTOR_Vars_t gMotorVars = MOTOR_Vars_INIT;
    
    // Graphing Variables
    volatile bool Graph_Flag_Enable_update = false;
    volatile unsigned int Graph_Counter = 0;
    volatile unsigned short Graph_Tick_Counter = 0;
    volatile unsigned short Graph_Tick_Counter_Value = 10;
    #define GRAPH_SIZE 300
    volatile _iq Graph_Data[GRAPH_SIZE];
    volatile _iq Graph_Data2[GRAPH_SIZE];
    volatile _iq SpeedRef_krpm_previous = _IQ(0.0);
    
    #ifdef FLASH
    // Used for running BackGround in flash, and ISR in RAM
    extern uint16_t *RamfuncsLoadStart, *RamfuncsLoadEnd, *RamfuncsRunStart;
    #endif
    
    
    #ifdef DRV8301_SPI
    // Watch window interface to the 8301 SPI
    DRV_SPI_8301_Vars_t gDrvSpi8301Vars;
    #endif
    
    
    // **************************************************************************
    // the functions
    
    void main(void)
    {
      uint_least8_t estNumber = 0;
    
    #ifdef FAST_ROM_V1p6
      uint_least8_t ctrlNumber = 0;
    #endif
    
      // Only used if running from FLASH
      // Note that the variable FLASH is defined by the project
      #ifdef FLASH
      // Copy time critical code and Flash setup code to RAM
      // The RamfuncsLoadStart, RamfuncsLoadEnd, and RamfuncsRunStart
      // symbols are created by the linker. Refer to the linker files.
      memCopy((uint16_t *)&RamfuncsLoadStart,(uint16_t *)&RamfuncsLoadEnd,(uint16_t *)&RamfuncsRunStart);
      #endif
    
      uint_least8_t graphCounter = 0;
    
      // initialize the driver
      drvHandle = DRV_init(&drv,sizeof(drv));
    
    
      // initialize the user parameters
      USER_setParams(&gUserParams);
    
    
      // set the driver parameters
      DRV_setParams(drvHandle,&gUserParams);
    
    
      // initialize the controller
    #ifdef FAST_ROM_V1p6
      ctrlHandle = CTRL_initCtrl(ctrlNumber, estNumber);  		//v1p6 format (06xF and 06xM devices)
      controller_obj = (CTRL_Obj *)ctrlHandle;
    #else
      ctrlHandle = CTRL_initCtrl(estNumber,&ctrl,sizeof(ctrl));	//v1p7 format default
    #endif
    
    
      // set the default controller parameters
      CTRL_setParams(ctrlHandle,&gUserParams);
    
    
      // setup faults
      DRV_setupFaults(drvHandle);
    
    
      // initialize the interrupt vector table
      DRV_initIntVectorTable(drvHandle);
    
    
      // enable the ADC interrupts
      DRV_enableAdcInts(drvHandle);
    
    
      // enable global interrupts
      DRV_enableGlobalInts(drvHandle);
    
    
      // enable debug interrupts
      DRV_enableDebugInt(drvHandle);
    
    
      // disable the PWM
      DRV_disablePwm(drvHandle);
    
    
      // enable DC bus compensation
      CTRL_setFlag_enableDcBusComp(ctrlHandle, true);
    
    
      // initialize the SpinTAC Components
      stHandle = ST_init(&st_obj, sizeof(st_obj));
      
      
      // setup the SpinTAC Components
      ST_setupVelCtl(stHandle);
    
      
      // initialize the Graph Variables
      for(graphCounter=0; graphCounter<GRAPH_SIZE; graphCounter++) {
    	  Graph_Data[graphCounter] = 0;
    	  Graph_Data2[graphCounter] = 0;
      }  
    
    
    #ifdef DRV8301_SPI
      // turn on the DRV8301 if present
      DRV_enable8301(drvHandle);
      // initialize the DRV8301 interface
      DRV_8301_SpiInterface_init(drvHandle,&gDrvSpi8301Vars);
    #endif
    
    
      for(;;)
      {
        // Waiting for enable system flag to be set
        while(!(gMotorVars.Flag_enableSys));
    
        Flag_Latch_softwareUpdate = true;
    
        // Dis-able the Library internal PI.  Iq has no reference now
        CTRL_setFlag_enableSpeedCtrl(ctrlHandle, false);
    
        // loop while the enable system flag is true
        while(gMotorVars.Flag_enableSys)
          {
            CTRL_Obj *obj = (CTRL_Obj *)ctrlHandle;
            ST_Obj *stObj = (ST_Obj *)stHandle;
    
            // increment counters
            gCounter_updateGlobals++;
    
            // enable/disable the use of motor parameters being loaded from user.h
            CTRL_setFlag_enableUserMotorParams(ctrlHandle,gMotorVars.Flag_enableUserParams);
    
            // enable/disable Rs recalibration during motor startup
            EST_setFlag_enableRsRecalc(obj->estHandle,gMotorVars.Flag_enableRsRecalc);
    
            // enable/disable automatic calculation of bias values
            CTRL_setFlag_enableOffset(ctrlHandle,gMotorVars.Flag_enableOffsetcalc);
    
    
            if(CTRL_isError(ctrlHandle))
              {
                // set the enable controller flag to false
                CTRL_setFlag_enableCtrl(ctrlHandle,false);
    
                // set the enable system flag to false
                gMotorVars.Flag_enableSys = false;
    
                // disable the PWM
                DRV_disablePwm(drvHandle);
              }
            else
              {
                // update the controller state
                bool flag_ctrlStateChanged = CTRL_updateState(ctrlHandle);
    
                // enable or disable the control
                CTRL_setFlag_enableCtrl(ctrlHandle, gMotorVars.Flag_Run_Identify);
    
                if(flag_ctrlStateChanged)
                  {
                    CTRL_State_e ctrlState = CTRL_getState(ctrlHandle);
    
                    if(ctrlState == CTRL_State_OffLine)
                      {
                        // enable the PWM
                        DRV_enablePwm(drvHandle);
                      }
                    else if(ctrlState == CTRL_State_OnLine)
                      {
                        if(gMotorVars.Flag_enableOffsetcalc == true)
                        {
                          // update the ADC bias values
                          DRV_updateAdcBias(drvHandle);
                        }
                        else
                        {
                          // set the current bias
                          DRV_setBias(drvHandle,DRV_SensorType_Current,0,_IQ(I_A_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Current,1,_IQ(I_B_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Current,2,_IQ(I_C_offset));
    
                          // set the voltage bias
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,0,_IQ(V_A_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,1,_IQ(V_B_offset));
                          DRV_setBias(drvHandle,DRV_SensorType_Voltage,2,_IQ(V_C_offset));
                        }
    
                        // enable the PWM
                        DRV_enablePwm(drvHandle);
                      }
                    else if(ctrlState == CTRL_State_Idle)
                      {
                        // disable the PWM
                        DRV_disablePwm(drvHandle);
                        gMotorVars.Flag_Run_Identify = false;
                      }
                  }
              }
    
    
            if(EST_isMotorIdentified(obj->estHandle))
              {
                // set the current ramp
                EST_setMaxCurrentSlope_pu(obj->estHandle,gMaxCurrentSlope);
                gMotorVars.Flag_MotorIdentified = true;
    
                // set the speed reference
                CTRL_setSpd_ref_krpm(ctrlHandle,gMotorVars.SpeedRef_krpm);
    
                // set the speed acceleration
                CTRL_setMaxAccel_pu(ctrlHandle,_IQmpy(MAX_ACCEL_KRPMPS_SF,gMotorVars.MaxAccel_krpmps));
    
                // enable the SpinTAC Speed Controller
                STVELCTL_setEnable(stObj->velCtlHandle, true);
    
                if(EST_getState(obj->estHandle) != EST_State_OnLine)
                {
                	// if the estimator is not running, place SpinTAC into reset
                	STVELCTL_setEnable(stObj->velCtlHandle, false);
                }
    			
    			// select the SpinTAC Speed Controller (true) or the PI Speed Controller (false)
                CTRL_setFlag_enableSpeedCtrl(ctrlHandle, !gMotorVars.SpinTAC.VelCtlEnb);
    
                if(Flag_Latch_softwareUpdate)
                {
                  Flag_Latch_softwareUpdate = false;
    
    #ifdef FAST_ROM_V1p6
                  if(CTRL_getFlag_enableUserMotorParams(ctrlHandle) == true)
                  {
                      // call this function to fix 1p6
                      softwareUpdate1p6(ctrlHandle);
                  }
    #endif
    
                  calcPIgains(ctrlHandle);
    
                  // initialize the watch window kp and ki current values with pre-calculated values
                  gMotorVars.Kp_Idq = CTRL_getKp(ctrlHandle,CTRL_Type_PID_Id);
                  gMotorVars.Ki_Idq = CTRL_getKi(ctrlHandle,CTRL_Type_PID_Id);
    
                  // initialize the watch window kp and ki values with pre-calculated values
                  gMotorVars.Kp_spd = CTRL_getKp(ctrlHandle,CTRL_Type_PID_spd);
                  gMotorVars.Ki_spd = CTRL_getKi(ctrlHandle,CTRL_Type_PID_spd);
    			  
    			  // initialize the watch window Bw value with the default value
                  gMotorVars.SpinTAC.VelCtlBwScale = STVELCTL_getBandwidthScale(stObj->velCtlHandle);
                }
              }
            else
              {
                Flag_Latch_softwareUpdate = true;
    
                // the estimator sets the maximum current slope during identification
                gMaxCurrentSlope = EST_getMaxCurrentSlope_pu(obj->estHandle);
              }
    
    
            // when appropriate, update the global variables
            if(gCounter_updateGlobals >= NUM_MAIN_TICKS_FOR_GLOBAL_VARIABLE_UPDATE)
              {
                // reset the counter
                gCounter_updateGlobals = 0;
    
                updateGlobalVariables_motor(ctrlHandle, stHandle);
              }
    
          } // end of while(gFlag_enableSys) loop
    
    
        // disable the PWM
        DRV_disablePwm(drvHandle);
    
        // set the default controller parameters (Reset the control to re-identify the motor)
        CTRL_setParams(ctrlHandle,&gUserParams);
    
        // setup the SpinTAC Components
        ST_setupVelCtl(stHandle);
    
      } // end of for(;;) loop
    
    } // end of main() function
    
    
    interrupt void mainISR(void)
    {
    
      static uint16_t stCnt = 0;
    
      // DPM - toggle status LED
      if(gLEDcnt++ > (uint_least32_t)(USER_PWM_FREQ_kHz * 1000 / LED_BLINK_FREQ_Hz)) {
        DRV_toggleLed(drvHandle,(GPIO_Number_e)DRV_Gpio_LED2);
        gLEDcnt = 0;
      }
    
    
      // acknowledge the ADC interrupt
      DRV_acqAdcInt(drvHandle,ADC_IntNumber_1);
    
    
      // convert the ADC data
      DRV_readAdcData(drvHandle,&gAdcData);
    
    
      // Run the SpinTAC Components
      if(stCnt++ >= ISR_TICKS_PER_SPINTAC_TICK) {
    	  ST_runVelCtl(stHandle, ctrlHandle);
    	  stCnt = 1;
      }
    
    
      // run the controller
      CTRL_run(ctrlHandle,drvHandle,&gAdcData,&gPwmData);
    
    
      // write the PWM compare values
      DRV_writePwmData(drvHandle,&gPwmData);
    
      if (!(SpeedRef_krpm_previous == gMotorVars.SpeedRef_krpm)) {
      	  Graph_Flag_Enable_update = true;
      	  Graph_Counter = 0;
      	  SpeedRef_krpm_previous = gMotorVars.SpeedRef_krpm;
      }
    
      gMotorVars.Iq_A = _IQmpy(CTRL_getIq_in_pu(ctrlHandle), _IQ(USER_IQ_FULL_SCALE_CURRENT_A));
    
      // store graph value
      if(Graph_Flag_Enable_update) {
      	  if(Graph_Counter >= GRAPH_SIZE) {
      		  Graph_Flag_Enable_update = false;
      	  }
      	  else {
      		  if(Graph_Tick_Counter == 0) {
      		      Graph_Data[Graph_Counter] = gMotorVars.Speed_krpm;
      		      Graph_Data2[Graph_Counter] = gMotorVars.Iq_A;
      		      Graph_Counter++;
      		      Graph_Tick_Counter = Graph_Tick_Counter_Value - 1;
      		  }
      		  else {
      			  Graph_Tick_Counter--;
      		  }
      	  }
       }
    
    
      // setup the controller
      CTRL_setup(ctrlHandle);
    
    
      return;
    } // end of mainISR() function
    
    
    void updateGlobalVariables_motor(CTRL_Handle handle, ST_Handle sthandle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      ST_Obj *stObj = (ST_Obj *)sthandle;
    
    
      // get the speed estimate
      gMotorVars.Speed_krpm = EST_getSpeed_krpm(obj->estHandle);
    
      // get the torque estimate
      gMotorVars.Torque_lbin = EST_getTorque_lbin(obj->estHandle);
    
      // get the magnetizing current
      gMotorVars.MagnCurr_A = EST_getIdRated(obj->estHandle);
    
      // get the rotor resistance
      gMotorVars.Rr_Ohm = EST_getRr_Ohm(obj->estHandle);
    
      // get the stator resistance
      gMotorVars.Rs_Ohm = EST_getRs_Ohm(obj->estHandle);
    
      // get the stator inductance in the direct coordinate direction
      gMotorVars.Lsd_H = EST_getLs_d_H(obj->estHandle);
    
      // get the stator inductance in the quadrature coordinate direction
      gMotorVars.Lsq_H = EST_getLs_q_H(obj->estHandle);
    
      // get the flux
      gMotorVars.Flux_VpHz = EST_getFlux_VpHz(obj->estHandle);
    
      // get the controller state
      gMotorVars.CtrlState = CTRL_getState(handle);
    
      // get the estimator state
      gMotorVars.EstState = EST_getState(obj->estHandle);
      
      if((gMotorVars.CtrlState == CTRL_State_OnLine) && (gMotorVars.Flag_MotorIdentified == true) && (Flag_Latch_softwareUpdate == false))
        {
          // set the kp and ki speed values from the watch window
          CTRL_setKp(handle,CTRL_Type_PID_spd,gMotorVars.Kp_spd);
          CTRL_setKi(handle,CTRL_Type_PID_spd,gMotorVars.Ki_spd);
    
          // set the kp and ki current values for Id and Iq from the watch window
          CTRL_setKp(handle,CTRL_Type_PID_Id,gMotorVars.Kp_Idq);
          CTRL_setKi(handle,CTRL_Type_PID_Id,gMotorVars.Ki_Idq);
          CTRL_setKp(handle,CTRL_Type_PID_Iq,gMotorVars.Kp_Idq);
          CTRL_setKi(handle,CTRL_Type_PID_Iq,gMotorVars.Ki_Idq);
    	}
    
      // gets the Velocity Controller status
      gMotorVars.SpinTAC.VelCtlStatus = STVELCTL_getStatus(stObj->velCtlHandle);
    	
      // get the inertia setting
      gMotorVars.SpinTAC.Inertia_Aperkrpm = _IQmpy(STVELCTL_getInertia(stObj->velCtlHandle), _IQ(ST_SPEED_PU_PER_KRPM * USER_IQ_FULL_SCALE_CURRENT_A));
    
      // get the friction setting
      gMotorVars.SpinTAC.Friction_Aperkrpm = _IQmpy(STVELCTL_getFriction(stObj->velCtlHandle), _IQ(ST_SPEED_PU_PER_KRPM * USER_IQ_FULL_SCALE_CURRENT_A));
    
      // set the SpinTAC (ST) bandwidth scale
      STVELCTL_setBandwidthScale(stObj->velCtlHandle, gMotorVars.SpinTAC.VelCtlBwScale);
    
      // gets the SpinTAC (ST) bandwidth
      gMotorVars.SpinTAC.VelCtlBw_radps = STVELCTL_getBandwidth_radps(stObj->velCtlHandle);
    
      // get the Velocity Controller error
      gMotorVars.SpinTAC.VelCtlErrorID = STVELCTL_getErrorID(stObj->velCtlHandle);
    
      // enable/disable the forced angle
      EST_setFlag_enableForceAngle(obj->estHandle,gMotorVars.Flag_enableForceAngle);
    
      // enable or disable power warp
      CTRL_setFlag_enableEpl(handle,gMotorVars.Flag_enableEpl);
    
    #ifdef DRV8301_SPI
      DRV_8301_SpiInterface(drvHandle,&gDrvSpi8301Vars);
    #endif
    
      return;
    } // end of updateGlobalVariables_motor() function
    
    #ifdef FAST_ROM_V1p6
    void softwareUpdate1p6(CTRL_Handle handle)
    {
    
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t fullScaleInductance = EST_getFullScaleInductance(obj->estHandle);
      float_t Ls_coarse_max = _IQ30toF(EST_getLs_coarse_max_pu(obj->estHandle));
      int_least8_t lShift = ceil(log(obj->motorParams.Ls_d/(Ls_coarse_max*fullScaleInductance))/log(2.0));
      uint_least8_t Ls_qFmt = 30 - lShift;
      float_t L_max = fullScaleInductance * pow(2.0,lShift);
      _iq Ls_d_pu = _IQ30(obj->motorParams.Ls_d / L_max);
      _iq Ls_q_pu = _IQ30(obj->motorParams.Ls_q / L_max);
    
    
      // store the results
      EST_setLs_d_pu(obj->estHandle,Ls_d_pu);
      EST_setLs_q_pu(obj->estHandle,Ls_q_pu);
      EST_setLs_qFmt(obj->estHandle,Ls_qFmt);
    
      return;
    } // end of softwareUpdate1p6() function
    #endif
    
    void calcPIgains(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      float_t Ls_d = EST_getLs_d_H(obj->estHandle);
      float_t Ls_q = EST_getLs_q_H(obj->estHandle);
      float_t Rs = EST_getRs_Ohm(obj->estHandle);
      float_t RoverLs_d = Rs/Ls_d;
      float_t RoverLs_q = Rs/Ls_q;
      float_t fullScaleCurrent = EST_getFullScaleCurrent(obj->estHandle);
      float_t fullScaleVoltage = EST_getFullScaleVoltage(obj->estHandle);
      float_t ctrlPeriod_sec = CTRL_getCtrlPeriod_sec(handle);
      _iq Kp_Id = _IQ((0.25*Ls_d*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Id = _IQ(RoverLs_d*ctrlPeriod_sec);
      _iq Kp_Iq = _IQ((0.25*Ls_q*fullScaleCurrent)/(ctrlPeriod_sec*fullScaleVoltage));
      _iq Ki_Iq = _IQ(RoverLs_q*ctrlPeriod_sec);
      _iq Kd = _IQ(0.0);
    
      // set the Id controller gains
      PID_setKi(obj->pidHandle_Id,Ki_Id);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp_Id,Ki_Id,Kd);
    
      // set the Iq controller gains
      PID_setKi(obj->pidHandle_Iq,Ki_Iq);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp_Iq,Ki_Iq,Kd);
    
      return;
    } // end of calcPIgains() function
    
    
    void ST_runVelCtl(ST_Handle sthandle, CTRL_Handle handle)
    {
    
        _iq speedFeedback, iqReference, gSpdError, gUp, gUi;
        ST_Obj *stObj = (ST_Obj *)sthandle;
        CTRL_Obj *ctrlObj = (CTRL_Obj *)handle;
    
        // Get the mechanical speed in pu
        speedFeedback = EST_getFm_pu(ctrlObj->estHandle);
    
    	// Run the SpinTAC Controller
    	// Note that the library internal ramp generator is used to set the speed reference
        STVELCTL_setVelocityReference(stObj->velCtlHandle, TRAJ_getIntValue(ctrlObj->trajHandle_spd));
    	STVELCTL_setAccelerationReference(stObj->velCtlHandle, _IQ(0.0));	// Internal ramp generator does not provide Acceleration Reference
    	STVELCTL_setVelocityFeedback(stObj->velCtlHandle, speedFeedback);
    	STVELCTL_run(stObj->velCtlHandle);
    
    	// select SpinTAC Velocity Controller
    	iqReference = STVELCTL_getTorqueReference(stObj->velCtlHandle);
    
    	if(gMotorVars.SpinTAC.VelCtlEnb == true) {
    		// Set the Iq reference that came out of SpinTAC Velocity Control
    		CTRL_setIq_ref_pu(ctrlHandle, iqReference);
    		// Update internal PI integrator, if running SpinTAC
    		gSpdError = TRAJ_getIntValue(ctrlObj->trajHandle_spd) - speedFeedback;
    		gUp = _IQmpy(gSpdError, CTRL_getKp(handle, CTRL_Type_PID_spd));
    		gUi = _IQmpy(gSpdError, CTRL_getKi(handle, CTRL_Type_PID_spd));
    		CTRL_setUi(handle, CTRL_Type_PID_spd, iqReference - gUp - gUi);
    	}
    }
    //@} //defgroup
    // end of file
    

  • still not working and I highly suspect that ctrl.c and ctrl.h somehow were mistakenly changed...

    Could you post these original two files as well? MW_11

  • /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
     * *  Neither the name of Texas Instruments Incorporated nor the names of
     *    its contributors may be used to endorse or promote products derived
     *    from this software without specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    
     
     
    //! \file   solutions/instaspin_motion/src/ctrl.c
    //! \brief  Contains the various functions related to the controller (CTRL) object
    //!
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    
    // **************************************************************************
    // the includes
    
    #include <math.h>
    
    
    // drivers
    
    
    // modules
    #include "sw/modules/dlog/src/32b/dlog4ch.h"
    #include "sw/modules/math/src/32b/math.h"
    
    
    // platforms
    #include "ctrl.h"
    #include "drv.h"
    #include "user.h"
    
    
    #ifdef FLASH
    #pragma CODE_SECTION(CTRL_run,"ramfuncs");
    #pragma CODE_SECTION(CTRL_setup,"ramfuncs");
    #endif
    
    
    // **************************************************************************
    // the defines
    
    
    // **************************************************************************
    // the globals
    
    
    // **************************************************************************
    // the function prototypes
    
    void CTRL_getGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       _iq *pKp,_iq *pKi,_iq *pKd)
    {
    
      *pKp = CTRL_getKp(handle,ctrlType);
      *pKi = CTRL_getKi(handle,ctrlType);
      *pKd = CTRL_getKd(handle,ctrlType);
    
      return;    
    } // end of CTRL_getGains() function
    
    
    void CTRL_getIab_filt_pu(CTRL_Handle handle,MATH_vec2 *pIab_filt_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_filt_pu->value[0] = obj->Iab_filt.value[0];
      pIab_filt_pu->value[1] = obj->Iab_filt.value[1];
    
      return;
    } // end of CTRL_getIab_filt_pu() function
    
    
    void CTRL_getIab_in_pu(CTRL_Handle handle,MATH_vec2 *pIab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_in_pu->value[0] = obj->Iab_in.value[0];
      pIab_in_pu->value[1] = obj->Iab_in.value[1];
    
      return;
    } // end of CTRL_getIab_in_pu() function
    
    
    void CTRL_getIdq_in_pu(CTRL_Handle handle,MATH_vec2 *pIdq_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_in_pu->value[0] = obj->Idq_in.value[0];
      pIdq_in_pu->value[1] = obj->Idq_in.value[1];
    
      return;
    } // end of CTRL_getIdq_in_pu() function
    
    
    void CTRL_getIdq_ref_pu(CTRL_Handle handle,MATH_vec2 *pIdq_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_ref_pu->value[0] = obj->Idq_ref.value[0];
      pIdq_ref_pu->value[1] = obj->Idq_ref.value[1];
    
      return;
    } // end of CTRL_getIdq_ref_pu() function
    
    
    _iq CTRL_getMagCurrent_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getIdRated_pu(handle));
    } // end of CTRL_getMagCurrent_pu() function
    
    
    _iq CTRL_getMaximumSpeed_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getSpd_max_pu(handle));
    } // end of CTRL_getMaximumSpeed_pu() function
    
    
    void CTRL_getVab_in_pu(CTRL_Handle handle,MATH_vec2 *pVab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_in_pu->value[0] = obj->Vab_in.value[0];
      pVab_in_pu->value[1] = obj->Vab_in.value[1];
    
      return;
    } // end of CTRL_getVab_in_pu() function
    
    
    void CTRL_getVab_out_pu(CTRL_Handle handle,MATH_vec2 *pVab_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_out_pu->value[0] = obj->Vab_out.value[0];
      pVab_out_pu->value[1] = obj->Vab_out.value[1];
    
      return;
    } // end of CTRL_getVab_out_pu() function
    
    
    void CTRL_getVdq_out_pu(CTRL_Handle handle,MATH_vec2 *pVdq_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVdq_out_pu->value[0] = obj->Vdq_out.value[0];
      pVdq_out_pu->value[1] = obj->Vdq_out.value[1];
    
      return;
    } // end of CTRL_getVdq_out_pu() function
    
    
    void CTRL_getWaitTimes(CTRL_Handle handle,uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          pWaitTimes[stateCnt] = obj->waitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_getWaitTimes() function
    
    
    void CTRL_run(CTRL_Handle handle,DRV_Handle drvHandle,
                  const DRV_AdcData_t *pAdcData,
                  DRV_PwmData_t *pPwmData)
    {
      uint_least16_t count_isr = CTRL_getCount_isr(handle);
      uint_least16_t numIsrTicksPerCtrlTick = CTRL_getNumIsrTicksPerCtrlTick(handle);
    
    
      // if needed, run the controller
      if(count_isr >= numIsrTicksPerCtrlTick)
        {
          CTRL_State_e ctrlState = CTRL_getState(handle);
    
          // reset the isr count
          CTRL_resetCounter_isr(handle);
    
          // increment the state counter
          CTRL_incrCounter_state(handle);
    
          // increment the trajectory count
          CTRL_incrCounter_traj(handle);
    
          // run the appropriate controller
          if(ctrlState == CTRL_State_OnLine)
            {
        	  CTRL_Obj *obj = (CTRL_Obj *)handle;
    
              // increment the current count
              CTRL_incrCounter_current(handle);
    
              // increment the speed count
              CTRL_incrCounter_speed(handle);
    
              if(EST_getState(obj->estHandle) >= EST_State_MotorIdentified)
                {
                  // run the online controller
                  CTRL_runOnLine_User(handle,pAdcData,pPwmData);
                }
              else
                {
                  // run the online controller
                  CTRL_runOnLine(handle,pAdcData,pPwmData);
                }
            }
          else if(ctrlState == CTRL_State_OffLine)
            {
              // run the offline controller
              CTRL_runOffLine(handle,drvHandle,pAdcData,pPwmData);
            }
        }
      else
        {
          // increment the isr count
          CTRL_incrCounter_isr(handle);
        }
    
      return;
    } // end of CTRL_run() function
    
    
    void CTRL_setGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       const _iq Kp,const _iq Ki,const _iq Kd)
    {
    
      CTRL_setKp(handle,ctrlType,Kp);
      CTRL_setKi(handle,ctrlType,Ki);
      CTRL_setKd(handle,ctrlType,Kd);
    
      return;    
    } // end of CTRL_setGains() function
    
    
    void CTRL_setMagCurrent_pu(CTRL_Handle handle,const _iq magCurrent_pu)
    {
    
      CTRL_setIdRated_pu(handle,magCurrent_pu);
    
      return;    
    } // end of CTRL_setMagCurrent_pu() function
    
    
    void CTRL_setMaximumSpeed_pu(CTRL_Handle handle,const _iq maxSpeed_pu)
    {
    
      CTRL_setSpd_max_pu(handle,maxSpeed_pu);
    
      return;    
    } // end of CTRL_setMaximumSpeed_pu() function
    
    
    void CTRL_setParams(CTRL_Handle handle,USER_Params *pUserParams)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq Kp,Ki,Kd;
      _iq outMin,outMax;
      _iq maxModulation;
    
      MATH_vec2 Iab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_ref_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_in_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vdq_out_pu = {_IQ(0.0),_IQ(0.0)};
    
    
      // assign the motor type
      CTRL_setMotorParams(handle,pUserParams->motor_type,
                          pUserParams->motor_numPolePairs,
                          pUserParams->motor_ratedFlux,
                          pUserParams->motor_Ls_d,
                          pUserParams->motor_Ls_q,
                          pUserParams->motor_Rr,
                          pUserParams->motor_Rs);
    
    
      // assign other controller parameters
      CTRL_setNumIsrTicksPerCtrlTick(handle,pUserParams->numIsrTicksPerCtrlTick);
      CTRL_setNumCtrlTicksPerCurrentTick(handle,pUserParams->numCtrlTicksPerCurrentTick);
      CTRL_setNumCtrlTicksPerSpeedTick(handle,pUserParams->numCtrlTicksPerSpeedTick);
      CTRL_setNumCtrlTicksPerTrajTick(handle,pUserParams->numCtrlTicksPerTrajTick);
    
      CTRL_setCtrlFreq_Hz(handle,pUserParams->ctrlFreq_Hz);
      CTRL_setTrajFreq_Hz(handle,pUserParams->trajFreq_Hz);
      CTRL_setTrajPeriod_sec(handle,_IQ(1.0/pUserParams->trajFreq_Hz));
    
      CTRL_setCtrlPeriod_sec(handle,pUserParams->ctrlPeriod_sec);
    
      CTRL_setMaxVsMag_pu(handle,_IQ(pUserParams->maxVsMag_pu));
    
      CTRL_setIab_in_pu(handle,&Iab_out_pu);
      CTRL_setIdq_in_pu(handle,&Idq_out_pu);
      CTRL_setIdq_ref_pu(handle,&Idq_ref_pu);
    
      CTRL_setIdRated_pu(handle,_IQ(pUserParams->IdRated/pUserParams->iqFullScaleCurrent_A));
    
      CTRL_setVab_in_pu(handle,&Vab_in_pu);
      CTRL_setVab_out_pu(handle,&Vab_out_pu);
      CTRL_setVdq_out_pu(handle,&Vdq_out_pu);
    
      CTRL_setSpd_out_pu(handle,_IQ(0.0));
    
      CTRL_setRhf(handle,0.0);
      CTRL_setLhf(handle,0.0);
      CTRL_setRoverL(handle,0.0);
    
    
      // reset the counters
      CTRL_resetCounter_current(handle);
      CTRL_resetCounter_isr(handle);
      CTRL_resetCounter_speed(handle);
      CTRL_resetCounter_state(handle);
      CTRL_resetCounter_traj(handle);
    
    
      // set the wait times for each state
      CTRL_setWaitTimes(handle,&pUserParams->ctrlWaitTime[0]);
    
    
      // set flags
      CTRL_setFlag_enableEpl(handle,false);
      CTRL_setFlag_enableCtrl(handle,false);
      CTRL_setFlag_enableEpl(handle,false);
      CTRL_setFlag_enableOffset(handle,true);
      CTRL_setFlag_enableSpeedCtrl(handle,true);
      CTRL_setFlag_enableUserMotorParams(handle,false);
      CTRL_setFlag_enableDcBusComp(handle,true);
    
    
      // initialize the controller error code
      CTRL_setErrorCode(handle,CTRL_ErrorCode_NoError);
    
    
      // set the default controller state
      CTRL_setState(handle,CTRL_State_Idle);
    
    
      // set the number of current sensors
      CTRL_setupClarke_I(handle,pUserParams->numCurrentSensors);
    
    
      // set the number of voltage sensors
      CTRL_setupClarke_V(handle,pUserParams->numVoltageSensors);
    
    
      // set the default Id PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Id,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Id,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Id,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp,Ki,Kd);
    
    
      // set the default the Iq PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Iq,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Iq,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Iq,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp,Ki,Kd);
    
    
      // set the default speed PID controller parameters
      Kp = _IQ(0.02*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz/pUserParams->iqFullScaleCurrent_A);
      Ki = _IQ(2.0*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz*pUserParams->ctrlPeriod_sec/pUserParams->iqFullScaleCurrent_A);
      Kd = _IQ(0.0);
      outMin = _IQ(-1.0);
      outMax = _IQ(1.0);
    
      PID_setGains(obj->pidHandle_spd,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_spd,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_spd,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_spd,Kp,Ki,Kd);
    
    
      // set the speed reference
      CTRL_setSpd_ref_pu(handle,_IQ(0.0));
    
    
      // set the default Id current trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxSlope(obj->trajHandle_Id,_IQ(0.0));
    
    
      // set the default the speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxSlope(obj->trajHandle_spd,_IQ(0.0));
    
    
      // set the default maximum speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxSlope(obj->trajHandle_spdMax,_IQ(0.0)); // not used
    
      
      // set the default estimator parameters
      CTRL_setEstParams(obj->estHandle,pUserParams);
    
    
      // set the maximum modulation for the SVGEN module
      maxModulation = SVGEN_4_OVER_3;
      SVGEN_setMaxModulation(obj->svgenHandle,maxModulation);
    
      return;
    } // end of CTRL_setParams() function
    
    
    void CTRL_setSpd_ref_pu(CTRL_Handle handle,const _iq spd_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_pu() function
    
    
    void CTRL_setSpd_ref_krpm(CTRL_Handle handle,const _iq spd_ref_krpm)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq krpm_to_pu_sf = EST_get_krpm_to_pu_sf(obj->estHandle);
    
      _iq spd_ref_pu = _IQmpy(spd_ref_krpm,krpm_to_pu_sf);
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_krpm() function
    
    
    void CTRL_setup(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      uint_least16_t count_traj = CTRL_getCount_traj(handle);
      uint_least16_t numCtrlTicksPerTrajTick = CTRL_getNumCtrlTicksPerTrajTick(handle);
    
    
      // as needed, update the trajectory
      if(count_traj >= numCtrlTicksPerTrajTick)
        {
          _iq intValue_Id = TRAJ_getIntValue(obj->trajHandle_Id);
    
          // reset the trajectory count
          CTRL_resetCounter_traj(handle);
    
          // run the trajectories
          CTRL_runTraj(handle);
        } // end of if(gFlag_traj) block
    
      return;
    } // end of CTRL_setup() function
    
    
    void CTRL_setupClarke_I(CTRL_Handle handle,uint_least8_t numCurrentSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numCurrentSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else if(numCurrentSensors == 2)
        {
          alpha_sf = _IQ(1.0);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_I,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_I,numCurrentSensors);
    
      return;
    } // end of CTRL_setupClarke_I() function
    
    
    void CTRL_setupClarke_V(CTRL_Handle handle,uint_least8_t numVoltageSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numVoltageSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
     else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_V,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_V,numVoltageSensors);
    
      return;
    } // end of CTRL_setupClarke_V() function
    
    
    void CTRL_setWaitTimes(CTRL_Handle handle,const uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          obj->waitTimes[stateCnt] = pWaitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_setWaitTimes() function
    
    
    bool CTRL_updateState(CTRL_Handle handle)
    {
      CTRL_State_e ctrlState = CTRL_getState(handle);
      bool flag_enableCtrl = CTRL_getFlag_enableCtrl(handle);
      bool stateChanged = false;
    
    
      if(flag_enableCtrl)
        {
          uint_least32_t waitTime = CTRL_getWaitTime(handle,ctrlState);
          uint_least32_t counter_ctrlState = CTRL_getCount_state(handle);
    
    
          // check for errors
          CTRL_checkForErrors(handle);
    
    
          if(counter_ctrlState >= waitTime)
            {
              // reset the counter
              CTRL_resetCounter_state(handle);
    
    
              if(ctrlState == CTRL_State_OnLine)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  _iq Id_target = TRAJ_getTargetValue(obj->trajHandle_Id);
    
                  // update the estimator state
                  bool flag_estStateChanged = EST_updateState(obj->estHandle,Id_target);
    
                  if(flag_estStateChanged)
                    {
                      // setup the controller
                      CTRL_setupCtrl(handle);
    
                      // setup the trajectory
                      CTRL_setupTraj(handle);
                    }
    
                  if(EST_isOnLine(obj->estHandle))
                    {
                      // setup the estimator for online state
                      CTRL_setupEstOnLineState(handle);
                    }
    
                  if(EST_isLockRotor(obj->estHandle) || 
                     (EST_isIdle(obj->estHandle) && EST_isMotorIdentified(obj->estHandle)))
                    {
                      // set the enable controller flag to false
                      CTRL_setFlag_enableCtrl(handle,false);
    
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_Idle);
                    }
                }
              else if(ctrlState == CTRL_State_OffLine)
                {
                  // set the next controller state
                  CTRL_setState(handle,CTRL_State_OnLine);
                }
              else if(ctrlState == CTRL_State_Idle)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  bool  flag_enableUserMotorParams = CTRL_getFlag_enableUserMotorParams(handle);
    
                  if(flag_enableUserMotorParams)
                    {
                      // initialize the motor parameters using values from the user.h file
                      CTRL_setUserMotorParams(handle);
                    }
    
                  if(EST_isIdle(obj->estHandle))
                    {
                      // setup the estimator for idle state
                      CTRL_setupEstIdleState(handle);
    
                      if(EST_isMotorIdentified(obj->estHandle))
                        {
                          if(CTRL_getFlag_enableOffset(handle))
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OffLine);
                            }
                          else
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OnLine);
                            }
                        }
                      else
                        {
                          // set the next controller state
                          CTRL_setState(handle,CTRL_State_OffLine);
                        }
                    }
                  else if(EST_isLockRotor(obj->estHandle))
                    {
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_OnLine);
                    }
                }
            }  // if(counter_ctrlState >= waitTime) loop
        } 
      else
        {
          CTRL_Obj *obj = (CTRL_Obj *)handle;
    
          // set the next controller state
          CTRL_setState(handle,CTRL_State_Idle);
    
          // set the estimator to idle
          if(!EST_isLockRotor(obj->estHandle))
            {
              if(EST_isMotorIdentified(obj->estHandle))
                {
                  EST_setIdle(obj->estHandle);
                }
              else
                {
                  EST_setIdle_all(obj->estHandle);
    
                  EST_setRs_pu(obj->estHandle,_IQ30(0.0));
                }
            }
        }
    
    
      // check to see if the state changed
      if(ctrlState != CTRL_getState(handle))
        {
          stateChanged = true;
        }
    
      return(stateChanged);
    } // end of CTRL_updateState() function
    
    // end of file
    

    4024.ctrl.h

    just a note, when I added this to _12 I was just using instaspin_foc ctrl/main

     

  • Chris,

    Could you send me ctrl.c, ctrl.h and main.h for _MOTION (MW_11)? Because I was using proj_lab5f.

  • I thought that's what I attached. Again, from MW _11 _motion

    /* --COPYRIGHT--,BSD
     * Copyright (c) 2012, Texas Instruments Incorporated
     * All rights reserved.
     *
     * Redistribution and use in source and binary forms, with or without
     * modification, are permitted provided that the following conditions
     * are met:
     *
     * *  Redistributions of source code must retain the above copyright
     *    notice, this list of conditions and the following disclaimer.
     *
     * *  Redistributions in binary form must reproduce the above copyright
     *    notice, this list of conditions and the following disclaimer in the
     *    documentation and/or other materials provided with the distribution.
     *
     * *  Neither the name of Texas Instruments Incorporated nor the names of
     *    its contributors may be used to endorse or promote products derived
     *    from this software without specific prior written permission.
     *
     * THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS "AS IS"
     * AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT LIMITED TO,
     * THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR
     * PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT OWNER OR
     * CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, SPECIAL,
     * EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT LIMITED TO,
     * PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, DATA, OR PROFITS;
     * OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY THEORY OF LIABILITY,
     * WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR
     * OTHERWISE) ARISING IN ANY WAY OUT OF THE USE OF THIS SOFTWARE,
     * EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE.
     * --/COPYRIGHT--*/
    
     
     
    //! \file   solutions/instaspin_motion/src/ctrl.c
    //! \brief  Contains the various functions related to the controller (CTRL) object
    //!
    //! (C) Copyright 2011, Texas Instruments, Inc.
    
    
    // **************************************************************************
    // the includes
    
    #include <math.h>
    
    
    // drivers
    
    
    // modules
    #include "sw/modules/dlog/src/32b/dlog4ch.h"
    #include "sw/modules/math/src/32b/math.h"
    
    
    // platforms
    #include "ctrl.h"
    #include "drv.h"
    #include "user.h"
    
    
    #ifdef FLASH
    #pragma CODE_SECTION(CTRL_run,"ramfuncs");
    #pragma CODE_SECTION(CTRL_setup,"ramfuncs");
    #endif
    
    
    // **************************************************************************
    // the defines
    
    
    // **************************************************************************
    // the globals
    
    
    // **************************************************************************
    // the function prototypes
    
    void CTRL_getGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       _iq *pKp,_iq *pKi,_iq *pKd)
    {
    
      *pKp = CTRL_getKp(handle,ctrlType);
      *pKi = CTRL_getKi(handle,ctrlType);
      *pKd = CTRL_getKd(handle,ctrlType);
    
      return;    
    } // end of CTRL_getGains() function
    
    
    void CTRL_getIab_filt_pu(CTRL_Handle handle,MATH_vec2 *pIab_filt_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_filt_pu->value[0] = obj->Iab_filt.value[0];
      pIab_filt_pu->value[1] = obj->Iab_filt.value[1];
    
      return;
    } // end of CTRL_getIab_filt_pu() function
    
    
    void CTRL_getIab_in_pu(CTRL_Handle handle,MATH_vec2 *pIab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIab_in_pu->value[0] = obj->Iab_in.value[0];
      pIab_in_pu->value[1] = obj->Iab_in.value[1];
    
      return;
    } // end of CTRL_getIab_in_pu() function
    
    
    void CTRL_getIdq_in_pu(CTRL_Handle handle,MATH_vec2 *pIdq_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_in_pu->value[0] = obj->Idq_in.value[0];
      pIdq_in_pu->value[1] = obj->Idq_in.value[1];
    
      return;
    } // end of CTRL_getIdq_in_pu() function
    
    
    void CTRL_getIdq_ref_pu(CTRL_Handle handle,MATH_vec2 *pIdq_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pIdq_ref_pu->value[0] = obj->Idq_ref.value[0];
      pIdq_ref_pu->value[1] = obj->Idq_ref.value[1];
    
      return;
    } // end of CTRL_getIdq_ref_pu() function
    
    
    _iq CTRL_getMagCurrent_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getIdRated_pu(handle));
    } // end of CTRL_getMagCurrent_pu() function
    
    
    _iq CTRL_getMaximumSpeed_pu(CTRL_Handle handle)
    {
    
      return(CTRL_getSpd_max_pu(handle));
    } // end of CTRL_getMaximumSpeed_pu() function
    
    
    void CTRL_getVab_in_pu(CTRL_Handle handle,MATH_vec2 *pVab_in_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_in_pu->value[0] = obj->Vab_in.value[0];
      pVab_in_pu->value[1] = obj->Vab_in.value[1];
    
      return;
    } // end of CTRL_getVab_in_pu() function
    
    
    void CTRL_getVab_out_pu(CTRL_Handle handle,MATH_vec2 *pVab_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVab_out_pu->value[0] = obj->Vab_out.value[0];
      pVab_out_pu->value[1] = obj->Vab_out.value[1];
    
      return;
    } // end of CTRL_getVab_out_pu() function
    
    
    void CTRL_getVdq_out_pu(CTRL_Handle handle,MATH_vec2 *pVdq_out_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      pVdq_out_pu->value[0] = obj->Vdq_out.value[0];
      pVdq_out_pu->value[1] = obj->Vdq_out.value[1];
    
      return;
    } // end of CTRL_getVdq_out_pu() function
    
    
    void CTRL_getWaitTimes(CTRL_Handle handle,uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          pWaitTimes[stateCnt] = obj->waitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_getWaitTimes() function
    
    
    void CTRL_run(CTRL_Handle handle,DRV_Handle drvHandle,
                  const DRV_AdcData_t *pAdcData,
                  DRV_PwmData_t *pPwmData)
    {
      uint_least16_t count_isr = CTRL_getCount_isr(handle);
      uint_least16_t numIsrTicksPerCtrlTick = CTRL_getNumIsrTicksPerCtrlTick(handle);
    
    
      // if needed, run the controller
      if(count_isr >= numIsrTicksPerCtrlTick)
        {
          CTRL_State_e ctrlState = CTRL_getState(handle);
    
          // reset the isr count
          CTRL_resetCounter_isr(handle);
    
          // increment the state counter
          CTRL_incrCounter_state(handle);
    
          // increment the trajectory count
          CTRL_incrCounter_traj(handle);
    
          // run the appropriate controller
          if(ctrlState == CTRL_State_OnLine)
            {
        	  CTRL_Obj *obj = (CTRL_Obj *)handle;
    
              // increment the current count
              CTRL_incrCounter_current(handle);
    
              // increment the speed count
              CTRL_incrCounter_speed(handle);
    
              if(EST_getState(obj->estHandle) >= EST_State_MotorIdentified)
                {
                  // run the online controller
                  CTRL_runOnLine_User(handle,pAdcData,pPwmData);
                }
              else
                {
                  // run the online controller
                  CTRL_runOnLine(handle,pAdcData,pPwmData);
                }
            }
          else if(ctrlState == CTRL_State_OffLine)
            {
              // run the offline controller
              CTRL_runOffLine(handle,drvHandle,pAdcData,pPwmData);
            }
        }
      else
        {
          // increment the isr count
          CTRL_incrCounter_isr(handle);
        }
    
      return;
    } // end of CTRL_run() function
    
    
    void CTRL_setGains(CTRL_Handle handle,const CTRL_Type_e ctrlType,
                       const _iq Kp,const _iq Ki,const _iq Kd)
    {
    
      CTRL_setKp(handle,ctrlType,Kp);
      CTRL_setKi(handle,ctrlType,Ki);
      CTRL_setKd(handle,ctrlType,Kd);
    
      return;    
    } // end of CTRL_setGains() function
    
    
    void CTRL_setMagCurrent_pu(CTRL_Handle handle,const _iq magCurrent_pu)
    {
    
      CTRL_setIdRated_pu(handle,magCurrent_pu);
    
      return;    
    } // end of CTRL_setMagCurrent_pu() function
    
    
    void CTRL_setMaximumSpeed_pu(CTRL_Handle handle,const _iq maxSpeed_pu)
    {
    
      CTRL_setSpd_max_pu(handle,maxSpeed_pu);
    
      return;    
    } // end of CTRL_setMaximumSpeed_pu() function
    
    
    void CTRL_setParams(CTRL_Handle handle,USER_Params *pUserParams)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq Kp,Ki,Kd;
      _iq outMin,outMax;
      _iq maxModulation;
    
      MATH_vec2 Iab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Idq_ref_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_in_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vab_out_pu = {_IQ(0.0),_IQ(0.0)};
      MATH_vec2 Vdq_out_pu = {_IQ(0.0),_IQ(0.0)};
    
    
      // assign the motor type
      CTRL_setMotorParams(handle,pUserParams->motor_type,
                          pUserParams->motor_numPolePairs,
                          pUserParams->motor_ratedFlux,
                          pUserParams->motor_Ls_d,
                          pUserParams->motor_Ls_q,
                          pUserParams->motor_Rr,
                          pUserParams->motor_Rs);
    
    
      // assign other controller parameters
      CTRL_setNumIsrTicksPerCtrlTick(handle,pUserParams->numIsrTicksPerCtrlTick);
      CTRL_setNumCtrlTicksPerCurrentTick(handle,pUserParams->numCtrlTicksPerCurrentTick);
      CTRL_setNumCtrlTicksPerSpeedTick(handle,pUserParams->numCtrlTicksPerSpeedTick);
      CTRL_setNumCtrlTicksPerTrajTick(handle,pUserParams->numCtrlTicksPerTrajTick);
    
      CTRL_setCtrlFreq_Hz(handle,pUserParams->ctrlFreq_Hz);
      CTRL_setTrajFreq_Hz(handle,pUserParams->trajFreq_Hz);
      CTRL_setTrajPeriod_sec(handle,_IQ(1.0/pUserParams->trajFreq_Hz));
    
      CTRL_setCtrlPeriod_sec(handle,pUserParams->ctrlPeriod_sec);
    
      CTRL_setMaxVsMag_pu(handle,_IQ(pUserParams->maxVsMag_pu));
    
      CTRL_setIab_in_pu(handle,&Iab_out_pu);
      CTRL_setIdq_in_pu(handle,&Idq_out_pu);
      CTRL_setIdq_ref_pu(handle,&Idq_ref_pu);
    
      CTRL_setIdRated_pu(handle,_IQ(pUserParams->IdRated/pUserParams->iqFullScaleCurrent_A));
    
      CTRL_setVab_in_pu(handle,&Vab_in_pu);
      CTRL_setVab_out_pu(handle,&Vab_out_pu);
      CTRL_setVdq_out_pu(handle,&Vdq_out_pu);
    
      CTRL_setSpd_out_pu(handle,_IQ(0.0));
    
      CTRL_setRhf(handle,0.0);
      CTRL_setLhf(handle,0.0);
      CTRL_setRoverL(handle,0.0);
    
    
      // reset the counters
      CTRL_resetCounter_current(handle);
      CTRL_resetCounter_isr(handle);
      CTRL_resetCounter_speed(handle);
      CTRL_resetCounter_state(handle);
      CTRL_resetCounter_traj(handle);
    
    
      // set the wait times for each state
      CTRL_setWaitTimes(handle,&pUserParams->ctrlWaitTime[0]);
    
    
      // set flags
      CTRL_setFlag_enableEpl(handle,false);
      CTRL_setFlag_enableCtrl(handle,false);
      CTRL_setFlag_enableEpl(handle,false);
      CTRL_setFlag_enableOffset(handle,true);
      CTRL_setFlag_enableSpeedCtrl(handle,true);
      CTRL_setFlag_enableUserMotorParams(handle,false);
      CTRL_setFlag_enableDcBusComp(handle,true);
    
    
      // initialize the controller error code
      CTRL_setErrorCode(handle,CTRL_ErrorCode_NoError);
    
    
      // set the default controller state
      CTRL_setState(handle,CTRL_State_Idle);
    
    
      // set the number of current sensors
      CTRL_setupClarke_I(handle,pUserParams->numCurrentSensors);
    
    
      // set the number of voltage sensors
      CTRL_setupClarke_V(handle,pUserParams->numVoltageSensors);
    
    
      // set the default Id PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Id,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Id,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Id,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Id,Kp,Ki,Kd);
    
    
      // set the default the Iq PID controller parameters
      Kp = _IQ(0.1);
      Ki = _IQ(pUserParams->ctrlPeriod_sec/0.004);
      Kd = _IQ(0.0);
      outMin = _IQ(-0.95);
      outMax = _IQ(0.95);
    
      PID_setGains(obj->pidHandle_Iq,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_Iq,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_Iq,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_Iq,Kp,Ki,Kd);
    
    
      // set the default speed PID controller parameters
      Kp = _IQ(0.02*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz/pUserParams->iqFullScaleCurrent_A);
      Ki = _IQ(2.0*pUserParams->maxCurrent*pUserParams->iqFullScaleFreq_Hz*pUserParams->ctrlPeriod_sec/pUserParams->iqFullScaleCurrent_A);
      Kd = _IQ(0.0);
      outMin = _IQ(-1.0);
      outMax = _IQ(1.0);
    
      PID_setGains(obj->pidHandle_spd,Kp,Ki,Kd);
      PID_setUi(obj->pidHandle_spd,_IQ(0.0));
      PID_setMinMax(obj->pidHandle_spd,outMin,outMax);
      CTRL_setGains(handle,CTRL_Type_PID_spd,Kp,Ki,Kd);
    
    
      // set the speed reference
      CTRL_setSpd_ref_pu(handle,_IQ(0.0));
    
    
      // set the default Id current trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_Id,_IQ(0.0));
      TRAJ_setMaxSlope(obj->trajHandle_Id,_IQ(0.0));
    
    
      // set the default the speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxValue(obj->trajHandle_spd,_IQ(0.0));
      TRAJ_setMaxSlope(obj->trajHandle_spd,_IQ(0.0));
    
    
      // set the default maximum speed trajectory module parameters
      TRAJ_setIntValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setTargetValue(obj->trajHandle_spdMax,_IQ(0.0));
      TRAJ_setMinValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxValue(obj->trajHandle_spdMax,_IQ(0.0)); // not used
      TRAJ_setMaxSlope(obj->trajHandle_spdMax,_IQ(0.0)); // not used
    
      
      // set the default estimator parameters
      CTRL_setEstParams(obj->estHandle,pUserParams);
    
    
      // set the maximum modulation for the SVGEN module
      maxModulation = SVGEN_4_OVER_3;
      SVGEN_setMaxModulation(obj->svgenHandle,maxModulation);
    
      return;
    } // end of CTRL_setParams() function
    
    
    void CTRL_setSpd_ref_pu(CTRL_Handle handle,const _iq spd_ref_pu)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_pu() function
    
    
    void CTRL_setSpd_ref_krpm(CTRL_Handle handle,const _iq spd_ref_krpm)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      _iq krpm_to_pu_sf = EST_get_krpm_to_pu_sf(obj->estHandle);
    
      _iq spd_ref_pu = _IQmpy(spd_ref_krpm,krpm_to_pu_sf);
    
      obj->spd_ref = spd_ref_pu;
    
      return;
    } // end of CTRL_setSpd_ref_krpm() function
    
    
    void CTRL_setup(CTRL_Handle handle)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
    
      uint_least16_t count_traj = CTRL_getCount_traj(handle);
      uint_least16_t numCtrlTicksPerTrajTick = CTRL_getNumCtrlTicksPerTrajTick(handle);
    
    
      // as needed, update the trajectory
      if(count_traj >= numCtrlTicksPerTrajTick)
        {
          _iq intValue_Id = TRAJ_getIntValue(obj->trajHandle_Id);
    
          // reset the trajectory count
          CTRL_resetCounter_traj(handle);
    
          // run the trajectories
          CTRL_runTraj(handle);
        } // end of if(gFlag_traj) block
    
      return;
    } // end of CTRL_setup() function
    
    
    void CTRL_setupClarke_I(CTRL_Handle handle,uint_least8_t numCurrentSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numCurrentSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else if(numCurrentSensors == 2)
        {
          alpha_sf = _IQ(1.0);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
      else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_I,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_I,numCurrentSensors);
    
      return;
    } // end of CTRL_setupClarke_I() function
    
    
    void CTRL_setupClarke_V(CTRL_Handle handle,uint_least8_t numVoltageSensors)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      _iq alpha_sf,beta_sf;
      
    
      // initialize the Clarke transform module for current
      if(numVoltageSensors == 3)
        {
          alpha_sf = _IQ(MATH_ONE_OVER_THREE);
          beta_sf = _IQ(MATH_ONE_OVER_SQRT_THREE);
        }
     else 
        {
          alpha_sf = _IQ(0.0);
          beta_sf = _IQ(0.0);
        }
    
      // set the parameters
      CLARKE_setScaleFactors(obj->clarkeHandle_V,alpha_sf,beta_sf);
      CLARKE_setNumSensors(obj->clarkeHandle_V,numVoltageSensors);
    
      return;
    } // end of CTRL_setupClarke_V() function
    
    
    void CTRL_setWaitTimes(CTRL_Handle handle,const uint_least32_t *pWaitTimes)
    {
      CTRL_Obj *obj = (CTRL_Obj *)handle;
      uint_least16_t stateCnt;
    
      for(stateCnt=0;stateCnt<CTRL_numStates;stateCnt++)
        {
          obj->waitTimes[stateCnt] = pWaitTimes[stateCnt];
        }
    
      return;
    } // end of CTRL_setWaitTimes() function
    
    
    bool CTRL_updateState(CTRL_Handle handle)
    {
      CTRL_State_e ctrlState = CTRL_getState(handle);
      bool flag_enableCtrl = CTRL_getFlag_enableCtrl(handle);
      bool stateChanged = false;
    
    
      if(flag_enableCtrl)
        {
          uint_least32_t waitTime = CTRL_getWaitTime(handle,ctrlState);
          uint_least32_t counter_ctrlState = CTRL_getCount_state(handle);
    
    
          // check for errors
          CTRL_checkForErrors(handle);
    
    
          if(counter_ctrlState >= waitTime)
            {
              // reset the counter
              CTRL_resetCounter_state(handle);
    
    
              if(ctrlState == CTRL_State_OnLine)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  _iq Id_target = TRAJ_getTargetValue(obj->trajHandle_Id);
    
                  // update the estimator state
                  bool flag_estStateChanged = EST_updateState(obj->estHandle,Id_target);
    
                  if(flag_estStateChanged)
                    {
                      // setup the controller
                      CTRL_setupCtrl(handle);
    
                      // setup the trajectory
                      CTRL_setupTraj(handle);
                    }
    
                  if(EST_isOnLine(obj->estHandle))
                    {
                      // setup the estimator for online state
                      CTRL_setupEstOnLineState(handle);
                    }
    
                  if(EST_isLockRotor(obj->estHandle) || 
                     (EST_isIdle(obj->estHandle) && EST_isMotorIdentified(obj->estHandle)))
                    {
                      // set the enable controller flag to false
                      CTRL_setFlag_enableCtrl(handle,false);
    
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_Idle);
                    }
                }
              else if(ctrlState == CTRL_State_OffLine)
                {
                  // set the next controller state
                  CTRL_setState(handle,CTRL_State_OnLine);
                }
              else if(ctrlState == CTRL_State_Idle)
                {
                  CTRL_Obj *obj = (CTRL_Obj *)handle;
                  bool  flag_enableUserMotorParams = CTRL_getFlag_enableUserMotorParams(handle);
    
                  if(flag_enableUserMotorParams)
                    {
                      // initialize the motor parameters using values from the user.h file
                      CTRL_setUserMotorParams(handle);
                    }
    
                  if(EST_isIdle(obj->estHandle))
                    {
                      // setup the estimator for idle state
                      CTRL_setupEstIdleState(handle);
    
                      if(EST_isMotorIdentified(obj->estHandle))
                        {
                          if(CTRL_getFlag_enableOffset(handle))
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OffLine);
                            }
                          else
                            {
                              // set the next controller state
                              CTRL_setState(handle,CTRL_State_OnLine);
                            }
                        }
                      else
                        {
                          // set the next controller state
                          CTRL_setState(handle,CTRL_State_OffLine);
                        }
                    }
                  else if(EST_isLockRotor(obj->estHandle))
                    {
                      // set the next controller state
                      CTRL_setState(handle,CTRL_State_OnLine);
                    }
                }
            }  // if(counter_ctrlState >= waitTime) loop
        } 
      else
        {
          CTRL_Obj *obj = (CTRL_Obj *)handle;
    
          // set the next controller state
          CTRL_setState(handle,CTRL_State_Idle);
    
          // set the estimator to idle
          if(!EST_isLockRotor(obj->estHandle))
            {
              if(EST_isMotorIdentified(obj->estHandle))
                {
                  EST_setIdle(obj->estHandle);
                }
              else
                {
                  EST_setIdle_all(obj->estHandle);
    
                  EST_setRs_pu(obj->estHandle,_IQ30(0.0));
                }
            }
        }
    
    
      // check to see if the state changed
      if(ctrlState != CTRL_getState(handle))
        {
          stateChanged = true;
        }
    
      return(stateChanged);
    } // end of CTRL_updateState() function
    
    // end of file
    

    3125.ctrl.h

  • I think the main.h you gave me was not from _MOTION, since it doesn't have "ST_Vars_t SpinTAC" etc.

  • Just wanna update you that I have found the problem:

    I left blank lines before and after  " _IQ(0.0), \" in main.h initialization part like below:

          

    _IQ(0.0), \

    _IQ(0.0), \       // add for new var Ia

            {0,0,0}, \
            {0,0,0}}

    Obviously, BLANK LINE means sth to the ccs...