Identifying inductance stops the rotor

Other Parts Discussed in Thread: DRV8301

I'm attempting to identify a transverse flux machine using lab 2a. The rotor spins during the ramp-up and appears to identify Flux_VpHz, but then halts when it moves on to identifying the inductances. My user.h file is attached below. I'm using a custom board, which the full scale voltages and currents have been changed for. Thanks for your help!

//! \brief CURRENTS AND VOLTAGES
// **************************************************************************
//! \brief Defines the full scale frequency for IQ variable, Hz
//! \brief All frequencies are converted into (pu) based on the ratio to this value
//! \brief this value MUST be larger than the maximum speed that you are expecting from the motor
#define USER_IQ_FULL_SCALE_FREQ_Hz (2000) // 800 Example with buffer for 8-pole 6 KRPM motor to be run to 10 KRPM with field weakening; Hz =(RPM * Poles) / 120

//! \brief Defines full scale value for the IQ30 variable of Voltage inside the system
//! \brief All voltages are converted into (pu) based on the ratio to this value
//! \brief WARNING: this value MUST meet the following condition: USER_IQ_FULL_SCALE_VOLTAGE_V > 0.5 * USER_MOTOR_MAX_CURRENT * USER_MOTOR_Ls_d * USER_VOLTAGE_FILTER_POLE_rps,
//! \brief WARNING: otherwise the value can saturate and roll-over, causing an inaccurate value
//! \brief WARNING: this value is OFTEN greater than the maximum measured ADC value, especially with high Bemf motors operating at higher than rated speeds
//! \brief WARNING: if you know the value of your Bemf constant, and you know you are operating at a multiple speed due to field weakening, be sure to set this value higher than the expected Bemf voltage
//! \brief It is recommended to start with a value ~3x greater than the USER_ADC_FULL_SCALE_VOLTAGE_V and increase to 4-5x if scenarios where a Bemf calculation may exceed these limits
//! \brief This value is also used to calculate the minimum flux value: USER_IQ_FULL_SCALE_VOLTAGE_V/USER_EST_FREQ_Hz/0.7
#define USER_IQ_FULL_SCALE_VOLTAGE_V (100.0)

//! \brief Defines the maximum voltage at the input to the AD converter
//! \brief The value that will be represented by the maximum ADC input (3.3V) and conversion (0FFFh)
//! \brief Hardware dependent, this should be based on the voltage sensing and scaling to the ADC input
#define USER_ADC_FULL_SCALE_VOLTAGE_V (63.023)

//! \brief Defines the voltage scale factor for the system
//! \brief Compile time calculation for scale factor (ratio) used throughout the system
#define USER_VOLTAGE_SF ((float_t)((USER_ADC_FULL_SCALE_VOLTAGE_V)/(USER_IQ_FULL_SCALE_VOLTAGE_V)))

//! \brief Defines the full scale current for the IQ variables, A
//! \brief All currents are converted into (pu) based on the ratio to this value
//! \brief WARNING: this value MUST be larger than the maximum current readings that you are expecting from the motor or the reading will roll over to 0, creating a control issue
#define USER_IQ_FULL_SCALE_CURRENT_A (200.0)

//! \brief Defines the maximum current at the AD converter
//! \brief The value that will be represented by the maximum ADC input (3.3V) and conversion (0FFFh)
//! \brief Hardware dependent, this should be based on the current sensing and scaling to the ADC input
#define USER_ADC_FULL_SCALE_CURRENT_A (400.0)

//! \brief Defines the current scale factor for the system
//! \brief Compile time calculation for scale factor (ratio) used throughout the system
#define USER_CURRENT_SF ((float_t)((USER_ADC_FULL_SCALE_CURRENT_A)/(USER_IQ_FULL_SCALE_CURRENT_A)))

//! \brief Defines the number of current sensors used
//! \brief Defined by the hardware capability present
//! \brief May be (2) or (3)
#define USER_NUM_CURRENT_SENSORS (3) // 3 Preferred setting for best performance across full speed range, allows for 100% duty cycle

//! \brief Defines the number of voltage (phase) sensors
//! \brief Must be (3)
#define USER_NUM_VOLTAGE_SENSORS (3) // 3 Required

//! \brief ADC current offsets for A, B, and C phases
//! \brief One-time hardware dependent, though the calibration can be done at run-time as well
//! \brief After initial board calibration these values should be updated for your specific hardware so they are available after compile in the binary to be loaded to the controller
//#define I_A_offset (0.8701236248)
//#define I_B_offset (0.8719444871)
//#define I_C_offset (0.8683906794)
//tesla-below if for small chakra
//#define I_A_offset (1.997333348)
//#define I_B_offset (1.988148093)
//#define I_C_offset (1.995664179)


#define I_A_offset (0.9933668375)
#define I_B_offset (0.98912853)
#define I_C_offset (0.9924683571)


//! \brief ADC voltage offsets for A, B, and C phases
//! \brief One-time hardware dependent, though the calibration can be done at run-time as well
//! \brief After initial board calibration these values should be updated for your specific hardware so they are available after compile in the binary to be loaded to the controller
//#define V_A_offset (0.4976325631)
//#define V_B_offset (0.4942032695)
//#define V_C_offset (0.4895076752)
//tesla-below is for small chakra
//#define V_A_offset (0.4801746011)
//#define V_B_offset (0.4769578576)
//#define V_C_offset (0.4753715396)


#define V_A_offset (0.1999764442)
#define V_B_offset (0.1988437176)
#define V_C_offset (0.1980687976)

//! \brief CLOCKS & TIMERS
// **************************************************************************
//! \brief Defines the system clock frequency, MHz
#define USER_SYSTEM_FREQ_MHz (90.0)

//! \brief Defines the Pulse Width Modulation (PWM) frequency, kHz
//! \brief PWM frequency can be set directly here up to 30 KHz safely (60 KHz MAX in some cases)
//! \brief For higher PWM frequencies (60 KHz+ typical for low inductance, high current ripple motors) it is recommended to use the ePWM hardware
//! \brief and adjustable ADC SOC to decimate the ADC conversion done interrupt to the control system, or to use the software Que example.
//! \brief Otherwise you risk missing interrupts and disrupting the timing of the control state machine
#define USER_PWM_FREQ_kHz (20.0)

//! \brief Defines the maximum Voltage vector (Vs) magnitude allowed. This value sets the maximum magnitude for the output of the
//! \brief Id and Iq PI current controllers. The Id and Iq current controller outputs are Vd and Vq.
//! \brief The relationship between Vs, Vd, and Vq is: Vs = sqrt(Vd^2 + Vq^2). In this FOC controller, the
//! \brief Vd value is set equal to USER_MAX_VS_MAG*USER_VD_MAG_FACTOR. Vq = sqrt(USER_MAX_VS_MAG^2 - Vd^2).
//! \brief Set USER_MAX_VS_MAG = 1.0 for a pure sinewave with a peak at SQRT(3)/2 = 86.6% duty cycle. No current reconstruction is needed for this scenario.
//! \brief Set USER_MAX_VS_MAG = 2/SQRT(3) = 1.1547 for a pure sinewave with a peak at 100% duty cycle. Current reconstruction will be needed for this scenario (Lab10a-x).
//! \brief Set USER_MAX_VS_MAG = 4/3 = 1.3333 to create a trapezoidal voltage waveform. Current reconstruction will be needed for this scenario (Lab10a-x).
//! \brief For space vector over-modulation, see lab 10 for details on system requirements that will allow the SVM generator to go all the way to trapezoidal.
#define USER_MAX_VS_MAG_PU (1.0) // Set to 1.0 if a current reconstruction technique is not used. Look at the module svgen_current in lab10a-x for more info.


//! \brief Defines the Pulse Width Modulation (PWM) period, usec
//! \brief Compile time calculation
#define USER_PWM_PERIOD_usec (1000.0/USER_PWM_FREQ_kHz)

//! \brief Defines the Interrupt Service Routine (ISR) frequency, Hz
//!
#define USER_ISR_FREQ_Hz ((float_t)USER_PWM_FREQ_kHz * 1000.0 / (float_t)USER_NUM_PWM_TICKS_PER_ISR_TICK)

//! \brief Defines the Interrupt Service Routine (ISR) period, usec
//!
#define USER_ISR_PERIOD_usec (USER_PWM_PERIOD_usec * (float_t)USER_NUM_PWM_TICKS_PER_ISR_TICK)


//! \brief DECIMATION
// **************************************************************************
//! \brief Defines the number of pwm clock ticks per isr clock tick
//! Note: Valid values are 1, 2 or 3 only
#define USER_NUM_PWM_TICKS_PER_ISR_TICK (1)

//! \brief Defines the number of isr ticks (hardware) per controller clock tick (software)
//! \brief Controller clock tick (CTRL) is the main clock used for all timing in the software
//! \brief Typically the PWM Frequency triggers (can be decimated by the ePWM hardware for less overhead) an ADC SOC
//! \brief ADC SOC triggers an ADC Conversion Done
//! \brief ADC Conversion Done triggers ISR
//! \brief This relates the hardware ISR rate to the software controller rate
//! \brief Typcially want to consider some form of decimation (ePWM hardware, CURRENT or EST) over 16KHz ISR to insure interrupt completes and leaves time for background tasks
#define USER_NUM_ISR_TICKS_PER_CTRL_TICK (1) // 2 Example, controller clock rate (CTRL) runs at PWM / 2; ex 30 KHz PWM, 15 KHz control

//! \brief Defines the number of controller clock ticks per current controller clock tick
//! \brief Relationship of controller clock rate to current controller (FOC) rate
#define USER_NUM_CTRL_TICKS_PER_CURRENT_TICK (1) // 1 Typical, Forward FOC current controller (Iq/Id/IPARK/SVPWM) runs at same rate as CTRL.

//! \brief Defines the number of controller clock ticks per estimator clock tick
//! \brief Relationship of controller clock rate to estimator (FAST) rate
//! \brief Depends on needed dynamic performance, FAST provides very good results as low as 1 KHz while more dynamic or high speed applications may require up to 15 KHz
#define USER_NUM_CTRL_TICKS_PER_EST_TICK (1) // 1 Typical, FAST estimator runs at same rate as CTRL;

//! \brief Defines the number of controller clock ticks per speed controller clock tick
//! \brief Relationship of controller clock rate to speed loop rate
#define USER_NUM_CTRL_TICKS_PER_SPEED_TICK (5) // 15 Typical to match PWM, ex: 15KHz PWM, controller, and current loop, 1KHz speed loop

//! \brief Defines the number of controller clock ticks per trajectory clock tick
//! \brief Relationship of controller clock rate to trajectory loop rate
//! \brief Typically the same as the speed rate
#define USER_NUM_CTRL_TICKS_PER_TRAJ_TICK (5) // 15 Typical to match PWM, ex: 10KHz controller & current loop, 1KHz speed loop, 1 KHz Trajectory

//! \brief Defines the controller frequency, Hz
//! \brief Compile time calculation
#define USER_CTRL_FREQ_Hz (uint_least32_t)(USER_ISR_FREQ_Hz/USER_NUM_ISR_TICKS_PER_CTRL_TICK)

//! \brief Defines the estimator frequency, Hz
//! \brief Compile time calculation
#define USER_EST_FREQ_Hz (uint_least32_t)(USER_CTRL_FREQ_Hz/USER_NUM_CTRL_TICKS_PER_EST_TICK)

//! \brief Defines the trajectory frequency, Hz
//! \brief Compile time calculation
#define USER_TRAJ_FREQ_Hz (uint_least32_t)(USER_CTRL_FREQ_Hz/USER_NUM_CTRL_TICKS_PER_TRAJ_TICK)

//! \brief Defines the controller execution period, usec
//! \brief Compile time calculation
#define USER_CTRL_PERIOD_usec (USER_ISR_PERIOD_usec * USER_NUM_ISR_TICKS_PER_CTRL_TICK)

//! \brief Defines the controller execution period, sec
//! \brief Compile time calculation
#define USER_CTRL_PERIOD_sec ((float_t)USER_CTRL_PERIOD_usec/(float_t)1000000.0)


//! \brief LIMITS
// **************************************************************************
//! \brief Defines the maximum negative current to be applied in Id reference
//! \brief Used in field weakening only, this is a safety setting (e.g. to protect against demagnetization)
//! \brief User must also be aware that overall current magnitude [sqrt(Id^2 + Iq^2)] should be kept below any machine design specifications
#define USER_MAX_NEGATIVE_ID_REF_CURRENT_A (-0.5 * USER_MOTOR_MAX_CURRENT) // -0.5 * USER_MOTOR_MAX_CURRENT Example, adjust to meet safety needs of your motor

//! \brief Defines the low speed limit for the flux integrator, pu
//! \brief This is the speed range (CW/CCW) at which the ForceAngle object is active, but only if Enabled
//! \brief Outside of this speed - or if Disabled - the ForcAngle will NEVER be active and the angle is provided by FAST only
#define USER_ZEROSPEEDLIMIT (2.0 / USER_IQ_FULL_SCALE_FREQ_Hz) // 0.002 pu, 1-5 Hz typical; Hz = USER_ZEROSPEEDLIMIT * USER_IQ_FULL_SCALE_FREQ_Hz
//#define USER_ZEROSPEEDLIMIT (.003125)

//! \brief Defines the force angle frequency, Hz
//! \brief Frequency of stator vector rotation used by the ForceAngle object
//! \brief Can be positive or negative
//#define USER_FORCE_ANGLE_FREQ_Hz (USER_ZEROSPEEDLIMIT * USER_IQ_FULL_SCALE_FREQ_Hz) // 1.0 Typical force angle start-up speed
#define USER_FORCE_ANGLE_FREQ_Hz (4.0)

//! \brief Defines the maximum current slope for Id trajectory during PowerWarp
//! \brief For Induction motors only, controls how fast Id input can change under PowerWarp control
#define USER_MAX_CURRENT_SLOPE_POWERWARP (0.3*USER_MOTOR_RES_EST_CURRENT/USER_IQ_FULL_SCALE_CURRENT_A/USER_TRAJ_FREQ_Hz) // 0.3*RES_EST_CURRENT / IQ_FULL_SCALE_CURRENT / TRAJ_FREQ Typical to produce 1-sec rampup/down

//! \brief Defines the starting maximum acceleration AND deceleration for the speed profiles, Hz/s
//! \brief Updated in run-time through user functions
//! \brief Inverter, motor, inertia, and load will limit actual acceleration capability
#define USER_MAX_ACCEL_Hzps (20.0) // 20.0 Default

//! \brief Defines maximum acceleration for the estimation speed profiles, Hz/s
//! \brief Only used during Motor ID (commission)
#define USER_MAX_ACCEL_EST_Hzps (5.0) // 5.0 Default, don't change

//! \brief Defines the maximum current slope for Id trajectory during estimation
#define USER_MAX_CURRENT_SLOPE (USER_MOTOR_RES_EST_CURRENT/USER_IQ_FULL_SCALE_CURRENT_A/USER_TRAJ_FREQ_Hz) // USER_MOTOR_RES_EST_CURRENT/USER_IQ_FULL_SCALE_CURRENT_A/USER_TRAJ_FREQ_Hz Default, don't change

//! \brief Defines the fraction of IdRated to use during rated flux estimation
//!
#define USER_IDRATED_FRACTION_FOR_RATED_FLUX (1.0) // 1.0 Default, don't change

//! \brief Defines the fraction of IdRated to use during inductance estimation
//!
#define USER_IDRATED_FRACTION_FOR_L_IDENT (1.0) // 1.0 Default, don't change

//! \brief Defines the IdRated delta to use during estimation
//!
#define USER_IDRATED_DELTA (0.00002)

//! \brief Defines the fraction of SpeedMax to use during inductance estimation
//!
#define USER_SPEEDMAX_FRACTION_FOR_L_IDENT (1.0) // 1.0 Default, don't change

//! \brief Defines flux fraction to use during inductance identification
//!
#define USER_FLUX_FRACTION (1.0) // 1.0 Default, don't change

//! \brief Defines the PowerWarp gain for computing Id reference
//! \brief Induction motors only
#define USER_POWERWARP_GAIN (1.0) // 1.0 Default, don't change

//! \brief Defines the R/L estimation frequency, Hz
//! \brief User higher values for low inductance motors and lower values for higher inductance
//! \brief motors. The values can range from 100 to 300 Hz.
#define USER_R_OVER_L_EST_FREQ_Hz (100) // 300 Default


//! \brief POLES
// **************************************************************************
//! \brief Defines the analog voltage filter pole location, Hz
//! \brief Must match the hardware filter for Vph
//#define USER_VOLTAGE_FILTER_POLE_Hz (637.954)
//tesla-tested in LTspice to have this filter pole
#define USER_VOLTAGE_FILTER_POLE_Hz (714.15)

//! \brief Defines the analog voltage filter pole location, rad/s
//! \brief Compile time calculation from Hz to rad/s
#define USER_VOLTAGE_FILTER_POLE_rps (2.0 * MATH_PI * USER_VOLTAGE_FILTER_POLE_Hz)

//! \brief Defines the software pole location for the voltage and current offset estimation, rad/s
//! \brief Should not be changed from default of (20.0)
#define USER_OFFSET_POLE_rps (20.0) // 20.0 Default, do not change

//! \brief Defines the software pole location for the flux estimation, rad/s
//! \brief Should not be changed from default of (100.0)
#define USER_FLUX_POLE_rps (100.0) // 100.0 Default, do not change

//! \brief Defines the software pole location for the direction filter, rad/s
#define USER_DIRECTION_POLE_rps (6.0) // 6.0 Default, do not change

//! \brief Defines the software pole location for the speed control filter, rad/s
#define USER_SPEED_POLE_rps (100.0) // 100.0 Default, do not change

//! \brief Defines the software pole location for the DC bus filter, rad/s
#define USER_DCBUS_POLE_rps (100.0) // 100.0 Default, do not change

//! \brief Defines the convergence factor for the estimator
//! \brief Do not change from default for FAST
#define USER_EST_KAPPAQ (1.5) // 1.5 Default, do not change

// **************************************************************************
// end the defines


//! \brief USER MOTOR & ID SETTINGS
// **************************************************************************

//tesla--below was added for spintac control
//#define USER_SYSTEM_BANDWIDTH_SCALE (1.0)

//! \brief Define each motor with a unique name and ID number
// BLDC & SMPM motors


#define Cmotor 115

//! \brief Uncomment the motor which should be included at compile
//! \brief These motor ID settings and motor parameters are then available to be used by the control system
//! \brief Once your ideal settings and parameters are identified update the motor section here so it is available in the binary code

#define USER_MOTOR Cmotor

#elif (USER_MOTOR == Cmotor) // Name must match the motor #define
#define USER_MOTOR_TYPE MOTOR_Type_Pm // Motor_Type_Pm (All Synchronous: BLDC, PMSM, SMPM, IPM) or Motor_Type_Induction (Asynchronous ACI)
#define USER_MOTOR_NUM_POLE_PAIRS (48) // PAIRS, not total poles. Used to calculate user RPM from rotor Hz only
#define USER_MOTOR_Rr (NULL) // Induction motors only, else NULL
#define USER_MOTOR_Rs (NULL) // Identified phase to neutral resistance in a Y equivalent circuit (Ohms, float)
#define USER_MOTOR_Ls_d (NULL) // For PM, Identified average stator inductance (Henry, float)
#define USER_MOTOR_Ls_q (NULL) //was 0.00013 For PM, Identified average stator inductance (Henry, float)
#define USER_MOTOR_RATED_FLUX (NULL) // Identified TOTAL flux linkage between the rotor and the stator (V/Hz)
#define USER_MOTOR_MAGNETIZING_CURRENT (NULL) // Induction motors only, else NULL
#define USER_MOTOR_RES_EST_CURRENT (5.0) // During Motor ID, maximum current (Amperes, float) used for Rs estimation, 10-20% rated current
#define USER_MOTOR_IND_EST_CURRENT (-5.0) // During Motor ID, maximum current (negative Amperes, float) used for Ls estimation, use just enough to enable rotation
#define USER_MOTOR_MAX_CURRENT (50.0) // CRITICAL: Used during ID and run-time, sets a limit on the maximum current command output of the provided Speed PI Controller to the Iq controller
#define USER_MOTOR_FLUX_EST_FREQ_Hz (100.0)

  • I have many comments for you.

    1. is this really a 2000 Hz machine @ 96 poles?  That means 2500 RPM max?
    2. what is your bus voltage?  you have your maximum ADC voltage at 63V but your IQ_VOLTAGE at (100.0).
    3. confirm you are measuring +/- 200A on your hardware?
    4. For this current you aren't using shunts, I assume you are using LEM and have scaled appropriately AND set your current polarity correctly per the User's Guide?
    5. Why only 20 KHz PWM?  I have the sense this is probably a very low inductance motor to meet the current requirements so you probably need to PWM at 45 KHz minimum
    6. Your decimation ticks are not correct. I recommend starting with the following

      #define USER_PWM_FREQ_kHz (45.0)

      //! \brief Defines the maximum Voltage vector (Vs) magnitude allowed. This value sets the maximum magnitude for the output of the
      //! \brief Id and Iq PI current controllers. The Id and Iq current controller outputs are Vd and Vq.
      //! \brief The relationship between Vs, Vd, and Vq is: Vs = sqrt(Vd^2 + Vq^2). In this FOC controller, the
      //! \brief Vd value is set equal to USER_MAX_VS_MAG*USER_VD_MAG_FACTOR. Vq = sqrt(USER_MAX_VS_MAG^2 - Vd^2).
      //! \brief Set USER_MAX_VS_MAG = 1.0 for a pure sinewave with a peak at SQRT(3)/2 = 86.6% duty cycle. No current reconstruction is needed for this scenario.
      //! \brief Set USER_MAX_VS_MAG = 2/SQRT(3) = 1.1547 for a pure sinewave with a peak at 100% duty cycle. Current reconstruction will be needed for this scenario (Lab10a-x).
      //! \brief Set USER_MAX_VS_MAG = 4/3 = 1.3333 to create a trapezoidal voltage waveform. Current reconstruction will be needed for this scenario (Lab10a-x).
      //! \brief For space vector over-modulation, see lab 10 for details on system requirements that will allow the SVM generator to go all the way to trapezoidal.
      #define USER_MAX_VS_MAG_PU (1.0) // Set to 1.0 if a current reconstruction technique is not used. Look at the module svgen_current in lab10a-x for more info.


      //! \brief Defines the Pulse Width Modulation (PWM) period, usec
      //! \brief Compile time calculation
      #define USER_PWM_PERIOD_usec (1000.0/USER_PWM_FREQ_kHz)

      //! \brief Defines the Interrupt Service Routine (ISR) frequency, Hz
      //!
      #define USER_ISR_FREQ_Hz ((float_t)USER_PWM_FREQ_kHz * 1000.0 / (float_t)USER_NUM_PWM_TICKS_PER_ISR_TICK)

      //! \brief Defines the Interrupt Service Routine (ISR) period, usec
      //!
      #define USER_ISR_PERIOD_usec (USER_PWM_PERIOD_usec * (float_t)USER_NUM_PWM_TICKS_PER_ISR_TICK)


      //! \brief DECIMATION
      // **************************************************************************
      //! \brief Defines the number of pwm clock ticks per isr clock tick
      //! Note: Valid values are 1, 2 or 3 only
      #define USER_NUM_PWM_TICKS_PER_ISR_TICK (3)

      //! \brief Defines the number of isr ticks (hardware) per controller clock tick (software)
      //! \brief Controller clock tick (CTRL) is the main clock used for all timing in the software
      //! \brief Typically the PWM Frequency triggers (can be decimated by the ePWM hardware for less overhead) an ADC SOC
      //! \brief ADC SOC triggers an ADC Conversion Done
      //! \brief ADC Conversion Done triggers ISR
      //! \brief This relates the hardware ISR rate to the software controller rate
      //! \brief Typcially want to consider some form of decimation (ePWM hardware, CURRENT or EST) over 16KHz ISR to insure interrupt completes and leaves time for background tasks
      #define USER_NUM_ISR_TICKS_PER_CTRL_TICK (1) // 2 Example, controller clock rate (CTRL) runs at PWM / 2; ex 30 KHz PWM, 15 KHz control

      //! \brief Defines the number of controller clock ticks per current controller clock tick
      //! \brief Relationship of controller clock rate to current controller (FOC) rate
      #define USER_NUM_CTRL_TICKS_PER_CURRENT_TICK (1) // 1 Typical, Forward FOC current controller (Iq/Id/IPARK/SVPWM) runs at same rate as CTRL.

      //! \brief Defines the number of controller clock ticks per estimator clock tick
      //! \brief Relationship of controller clock rate to estimator (FAST) rate
      //! \brief Depends on needed dynamic performance, FAST provides very good results as low as 1 KHz while more dynamic or high speed applications may require up to 15 KHz
      #define USER_NUM_CTRL_TICKS_PER_EST_TICK (1) // 1 Typical, FAST estimator runs at same rate as CTRL;

      //! \brief Defines the number of controller clock ticks per speed controller clock tick
      //! \brief Relationship of controller clock rate to speed loop rate
      #define USER_NUM_CTRL_TICKS_PER_SPEED_TICK (15) // 15 Typical to match PWM, ex: 15KHz PWM, controller, and current loop, 1KHz speed loop

      //! \brief Defines the number of controller clock ticks per trajectory clock tick
      //! \brief Relationship of controller clock rate to trajectory loop rate
      //! \brief Typically the same as the speed rate
      #define USER_NUM_CTRL_TICKS_PER_TRAJ_TICK (15) // 15 Typical to match PWM, ex: 10KHz controller & current loop, 1KHz speed loop, 1 KHz Trajectory

      7. update the frequency used for RoverL
      #define USER_R_OVER_L_EST_FREQ_Hz (300.0)

      8. confirm this pole is correct per the filter used on YOUR hardware. In the future, if you really have a 2000 Hz motor I recommend making this as small as possible, which means 2000 / 4 + some buffer = ~550

  • USER_MOTOR settings

    These you will have to play with once everything above is correct.

    You may need more RES_EST_CURRENT to start-up and reach the target speed.

    #define USER_MOTOR_RES_EST_CURRENT (8.0) // During Motor ID, maximum current (Amperes, float) used for Rs estimation, 10-20% rated current

    You man need less IND_EST_CURRENT during Ls to keep stability
    #define USER_MOTOR_IND_EST_CURRENT (-3.0) // During Motor ID, maximum current (negative Amperes, float) used for Ls estimation, use just enough to enable rotation


    #define USER_MOTOR_MAX_CURRENT (50.0) // CRITICAL: Used during ID and run-time, sets a limit on the maximum current command output of the provided Speed PI Controller to the Iq controller

    You may want to try a slightly lower target speed to keep stability during ID

    #define USER_MOTOR_FLUX_EST_FREQ_Hz (50.0)

    By the way, have you ever tried to ID this motor on the DRV8301 EVM at 50V bus?  It should be possible and will let you try to ID on known hardware vs. trying to debug your HW for an issue.

  • Hi Chris,

    Many thanks for your help—really appreciate it. 

    1. It's a 96 pole machine that I'm trying to spin up to around 2000 RPM. I added some headroom.
    2. Bus voltage is 48V.
    3. Yes, can confirm
    4. The board has Hall effect sensors at ±200A (ACS758ECB-200B)
    5. I'm not sure about the PWM freq. choice. Transverse flux machines are generally high inductance, as the winding is simply a single circumferential coil.
    6. Unfortunately, I've blown out my control board trying to get the motor identified. I will try your recommendations as soon as it is back in operation.

    Thanks again for your help.

    -Alex

  • do you have a general idea about the expected Rs, Ls, and Flux of this machine?

    from that we can look at needed frequencies and scaling of the variables.

    For now set your IQ_VOLTAGE to your bus voltage of (48.0)

    Only increase to keep > identified flux in V/Hz * 1600 Hz target frequency

    based on this you should expect a flux of < 0.03 V/Hz

  • It's a custom-built machine, and isn't well understood. Apparently someone identified it previously (I'm not sure with what success) and obtained the following parameters:

    Rs: 0.036 ohms

    Ls: 0.00003 Henry

    Rated flux: 0.025 V/Hz

  • Rs / Ls = 1200, a bit low if you think the machine can do 1600 Hz, but could be correct.  Ls may be a bit lower than you measured, or may decrease under heavy current.

    Isc = Flux / 2pi / Ls = 132A, which is reasonable for a 50A machine

    With this Isc and an Ls of 30uH, you will certainly need to PWM at 45 KHz, and since you are using the F28069 device you may want to consider PWM at 60 KHz with decimation of (3) and (1), (1),  to run ctrl and est at 20 KHz; then run speed and traj at (20)

  • I will try increasing the PWM frequency as soon as I get the board up and running again.

    Can you clarify something about the filter pole for me? From the UG: 

    "The voltage filter pole is needed by the FAST estimator to allow an accurate detection of the voltage
    feedback. The filter should be low enough to filter out the PWM signals, and at the same time allow a high
    speed voltage feedback signal to pass through the filter"

    Would using a pole that's 1/4 the full scale frequency attenuate the feedback voltages? I think I'm missing something simple here...

  • Alexander Broekhof said:
    Can you clarify something about the filter pole for me? From the UG:

    Yes, I've been trying to get the UG updated since this summer as it's not accurate. It looks like this was missed in the last UG revision for some reason (a bug is filed and on the system).

    The original recommendation for the voltage filter pole that we used internally (as we developed these solutions) was based on more "standard" motors that were in the 60-400 Hz range.  Once we saw so many people using these high speed motors it has changed.  What we saw is that if you do increase the frequency of this filter the drift/error of the capacitors negates (and even makes much worse) any benefits of having a pole above the rotor speed.

    So it is more important to keep the filter in the 200 - 500 Hz range, lower is better.  And you MUST keep the USER_IQ_FULL_SCALE_FREQ_Hz < 4 * USER_VOLTAGE_FILTER_POLE_Hz