I'm using comparator subsystem to trip the epwm. This peripheral is useful especially for hardware cycle by cycle current limiting. I configured the CMPSS1 as a window comparator application, so COMPH generates trip signal for upper limit and COMPL comparator generates for the lower limit.
Here the issue; COMPH generates trip signal within a couple of hundred nanoseconds but COMPL generates trip within few microseconds. All the configuration is same for both comparators. I also tried bypassing the digital filter using ASYNCH path but the result is same. The trip signal goes to epwm module using output xbar module.
Is there any hardware data about this topic, or should I check the software? How can I make COMPL to response fast like COMPH?