DRV8301-69M-KIT: Torque Control and Regenerative Braking

Part Number: DRV8301-69M-KIT

Hi,

I plan to run my motor on torque control. But I am wondering how would regenerative braking happen. 

This is my understanding:

1. In speed control, when motor is running at a high speed and I leave the throttle, the speed ref is set to 0. The output of speed PI controller sets a negative reference for Iq current. And that is how the energy will go back to the battery.

2. In current control (torque control), if I leave the throttle, Iq_ref will be 0 and there will be no regenerative braking. 

Is my understanding correct? 

If so, how should I map the throttle value to the Iq_ref to enable regenerative braking?  

  • 1. Right. The bus voltage will be boosted and energy will go back to the battery if the motor type is PMSM and apply an opposite torque current.
    2. Not always. The bus voltage will be boosted also if the motor was running in the field-weakening operation region.

    Typically you need to control the boosted voltage and current to the battery that depends on the reference torque current, you might need to add a control loop to implement it, not just simple linearity of throttle value.