Part Number: LAUNCHXL-F28377S
Hi,
I’m trying to run the ControlSuite’s SCI Echoback example for LAUNCHXL-F28377s. Nothing appears in the TeraTerm window. I’ve searched the forum and didn’t see a solution that helped.
I can't think of anything else to check. Hopefully I missed something simple!
Thanks, dave
Hi Dave,
I'd generally recommend you get your C2000 SW examples from C2000ware (newer) vs ControlSUITE (older) when possible.
Yes, you will need to add the pre-defined launchpad symbol to get the default project to run at 200MHz. This is because the X1 input clock can vary between EVMs (i.e. Launchpad vs. ControlCard) or a custom board. By default the SW projects assume 20MHz X1 frequency (which is correct for the ControlCard). You could alternately go in and change the PLL settings in the device initialization function to match your particular board.
The values in the "Asynchronous Baud Register Values for Common SCI Bit Rates" table assume 100MHz LSPCLK. 50MHz should be the default, but you might want to verify in the expressions window (after the code has run) that LOSPCP.bit.LSPCLKDIV is indeed '2' = /4.
The project will, by default, use GPIO28 and GPIO29, which would assume the use of a transceiver and cable:
//! \b External \b Connections \n
//! Connect the SCI-A port to a PC via a transceiver and cable.
//! - GPIO28 is SCI_A-RXD (Connect to Pin3, PC-TX, of serial DB9 cable)
//! - GPIO29 is SCI_A-TXD (Connect to Pin2, PC-RX, of serial DB9 cable)
You could instead change the GPIOs to GPIO84 and GPIO85 if you wanted to use the FTDI connection (virtual COM port created when you plug in the EVM) which shouldn't require a cable and transceiver: