TMS320F28069: GPIO14 and GPIO17 cannot be configured as /TZ3 simultaneously.

Part Number: TMS320F28069


If I configure only GPIO14 or GPIO17 as /TZ3, everything works as expected, i.e. if the signal goes low I get a trip event.

If I configure both GPIO14 and GPIO17 as /TZ3 at the same time, the trip-zone stops working. I.e. if one of the signals go low or if both go low at the same time, no trip event occurs.

Is this expected behaviour?

Best regards,

Ruben