I have three (3) of the HV Motor Drive Kits that we use on our servo motor test bed fixtures. We installed Murata DMS-20RM-3-AC1-R-C Panel Meters (PM) on our test fixtures, the inputs which are connected to a three phase multi switch to selectively monitor the L1-L2, L2-L3 and L3-L1 voltage outputs from the TI HV Drive. The Murata PM voltage measurements are steady, but radically higher than the actual HV Drive output voltages. A Murata engineer told me the PM measured voltage would not be accurate due to the Pulse Width Modulated signal (PWM) generated by a Variable Frequency Drive (VFD). He said he was not aware of a panel meter that had a built-in Low Pass Filter (LPF) to eliminate the inaccurate PM measurement.
My question is; can you help or guide me with putting together a LPF that will correct the PM display measurement? The measurements below hopefully will illustrate the voltage spreads between the Murata PM and the voltages and frequencies I measured with a Fluke 289 with an internal LPF. As you know, the Fluke 289 is designed to accurately measure the parameters of PWM VFDs.
The following are actual measurements taken while running our servo motor with the TI HV Drive with the Murata PM and a Fluke 289 with the LPF engaged.
1000 RPM - Murata PM: 184 Volts. Fluke 289: 50.7 Volts @ 67.1 Hz.
2000 RPM - Murata PM: 329 Volts. Fluke 289: 101.3 Volts @ 134.2 Hz.
3000 RPM - Murata PM 360 Volts. Fluke 289: 151.3 Volts @ 201.4 Hz.
If someone could help me with a LPF (or other device) to correct the measurement problem, I would very much appreciate your help.
Thank you,
Ron Stewart