Expert 4175 points
Other Parts Discussed in Thread: UCD90120A, UCD9090, UCD90160A, UCD90160, UCD90240, UCD90320U, UCD90120, UCD9090A, UCD90124, UCD90124A, UCD90320

For rails that are off due to fault response and ON_OFF_CONFIG set to AUTO, the only way to power them on again is to enable the re-sequence option at its fault response. With the re-sequence option, the faulted rail plus its fault shutdown slaves is re-sequenced when the retry account of the faulted rail is exhausted. The re-sequencing times and intervals are set through Global Configuration → Misc_config as shown in Figure 22.

For more FAQ please check the following document.

UCD90xxx Family Frequently Asked Questions and Answers 