Hi, the datasheet is not clear on whether the reverse current fault is latched or not. I'm having a problem with a latching fault, which occurs when other e-fuse devices fed from the same source power up after the TPS2663. The power source droops by a couple of hundred mV while the new device turns on, and existing TPS2663 allow a small amount of current back from the load. I don't need reverse flow protection as such, but it triggers the /FLT output and remains latched. The datasheet (page 8, electrical characteristics) shows a thresholds V(revth) & V(fwdth) which would indicate that a reasonable amount of forward current would be needed to clear the fault. All other faults self clear, but this one requires a substantial amount of 'normal' to go away: with the nominal 30mOhm Pass Fet on resistance, it would need around 2 amps to clear the fault?