My Applications:
Application #1 Vin = +12V
Application #2 Vin = +5V
Nominal Load Current: 250 mA for both cases.
The IC is used to protect a system where DC is run up the center conductor of a coax cable to a remote active antenna.
Can you explain from the Excel calculators ?: Rload - start input . The default values in the high (10K) and low voltage (1 ohm) calculators are significantly different.
Locally there is bulk capacitance at the IC output, but the final load is a significant distance from the IC. Does this factor into component or IC settings in any way?
Can you explain what leads to "No start-up. Load to big" for the Tcap calculation. That is the case for the 5V version of the circuit with the parameters I entered.
Is there an FAE who could review the calculators and my schematic? The 5V version of the calculator for my application is pasted below.
Is the current monitor scaling fixed based on other inputs (i.e. not independent)? Ideally this would be independent to scale to the range matched with an A/D converter used to monitor the system.
Example: My Inputs
ILIM | Current Limit (Recommended >10% over max load) | 0.3 | A |
VBUS_MAX | maximum input bus voltage | 5.0 | V |
CLOAD | Output load capacitance | 47.0 | uF |
RLOAD-start | Resistive load present at start up (not recommended) | 1.0 | Ohm |
TAMB | Maximum Ambient Temperature | 50.0 | ˚C |
RJA | Junction to ambient thermal resistance | 40.0 | ˚C/W |
QB_FET | Gate charge (Vg = 5.8V) of blocking FET. Enter 0 if no blocking FET is used. | 000.0E+0 | C |
Rsns_max | Maximum Sense Resistor | 173.3 | m-ohm |
Rsense | Sense Resistor | 10.0 | m-ohm |
PLIM,MIN | Minimum recommended Power Limit | 1.5 | W |
Plim-typ | Programmed power limit | 3.0 | W |
Retry? | Is this configured in retry mode? (Yes or No) | Yes | |
dV/dt? | Gate slew rate control? (Yes or No) | Yes | |
Iramp | Choose output capacitor charge current (<Plim/Vccmax) | 0.2 | A |
Results:
Basic Circuit Design Results | |||
Parameter | Description | Value | Units |
Tcap | Time to charge output cap under Power Limiting | No start up, load too big | ms |
T_FET | Time to charge Vgs to Vt, and Vt to 5.8V once Vout is up | 0.733 | ms |
T-dvdt | Time for Vgate = Vbus+5.8, when using dv/dt start-up with C-gate | 3.600 | ms |
T_total | Typical Start Time | 4.333 | ms |
T_fault | Needed Fault time for margin to start-up time | 6.500 | ms |
PDCFET | Maximum steady state FET power dissipation | 0.12 | W |
TJDCMAX | Maximum Steady State Junction temperature | 54.8 | ˚C |
SOA_25C | Power FET can handle for T_fault @ 25C | 36.366 | W |
SOA_der | derate above for the eleveated junction temperature | 27.696 | W |
SOA_mrg | SOA margin | 89.2 | % |
Power Limit Pass | YES | ||
SOA Pass | YES |
Compute Required Circuit Values | |||
Parameter | Description | Value | Units |
Rset | Choose Rset value | 51.1 | Ohm |
Rimon1 | Calculate Rimon value for current limit | 11497.500 | Ohm |
Rimon | Choose closest 1% resistor | 11500.000 | Ohm |
Ilimit_act | Actual I-limit value | 0.300 | A |
Rprog1 | Calculated Rprog value for Plim-typ | 12497 | Ohm |
Rprog | Choose closest 1% resistor | 12400 | Ohm |
Plimit_act | Actual power limit for Rprog | 3.024 | W |
Cgatec | Calculated gate capacitor to obtain inrush current = Iramp | 3.3E-9 | F |
Cgate | Gate capacitor used for dV/dt Control | 10.0E-9 | F |
Iramp_act | Actual Inrush (Ramp) Current for dV/dt Control | 0.102 | A |
Ctimer1 | Calculate fault timer capacitor value | 48.1E-9 | F |
Ctimer | Choose Ctimer >= Ctimer1 | 220.0E-9 | F |
Tfault_act | Actual fault Time | 29.7 | ms |
ENRise | Circuit turn on voltage with rising Vin | 4.5 | V |
OVRise | Circuit turn off under over voltage event | 5.5 | V |
R2 | Target middle resistor | 10000.0 | Ohm |
R3_c | Calculated bottom resistor | 45000.0 | Ohm |
R3 | Choose R3 | 45300.0 | Ohm |
R1_c | Calculated top resistor | 129255.6 | Ohm |
R1 | Choose R1 | 130000.0 | Ohm |
UVLO-R | Actual turn on with rising input voltage (low voltage) | 4.524 | V |
UVLO-F | Actual turn off with falling input voltage (low voltage) | 4.356 | V |
OVLO-R | Actual turn off with rising input voltage (overvoltage) | 5.522 | V |
OVLO-F | Actual turn on with falling input voltage (overvoltage) | 5.277 | V |
IMONsf | Current monitor scale factor (I = Vimon x IMONsf) | 0.444 | A/V |