Dir Sir/Madam
Could you tell me the meanings of CML:"Other Comms Fault" in FUSION Digital Power Designer's Monitor UI ?
What can be the reason of this error message?
Regards,
The PMBus spec lists some possible cases that could be flagged with this bit. What it means in practice depends on the device/program. Different programs in UCD3xxx devices check and flag different communication faults (or none, in some cases). I don't know what specific things the UCD9xxx devices check for this bit.
If you look at the PMBus 1.3 Spec, it mentions several spots where this bit can be set:
10.8.2 - Sending Too Few Bits
10.8.3 - Reading Too Few Bits
10.8.4 - Host Send Or Reads Too Few Bytes
10.8.6 - Reading Too Many Bytes
10.9.1. Improperly Set Read Bit In The Address Byte
Which device/program are you using?