Polarity-Reversal Relays

I am currently working on an application that involves converting +48vdc to -48vdc.

- I have an inverter that converts 120vac to 48vdc

- The 48vdc travels trough 22awg wire to a unit that requires a -48vdc input.

How can I get a -48vdc out of my inverter?

  • Hello Manny, Thank You for posting to the Forum.

    Here are some suggestions.

    1. if the 120VAC to 48VDC is isolated, you can connect the +48VDC output to ground and create a -48V output with the -48VDC output.

    2. if the 120VAC to 48VDC is NOT isolated, your downstream -48 "unit" could be connected such that its + input connects to the ground and its - input connect to +48

    3. if your first supply and second supply are not isolated, and share the same ground, then you will need a converter to take +48@xWatts and make -48@xWatts

    Here is an example.

    If I want to test this design, PMP7756, -48Vin 6V@18A out, I would take a +48V power source and connect:
          +Vout of the source to PMP7756 ground, GND P100
           -Vout(ground) of the source to PMP7756  -48V P101

    Here is a picture of PMP7756.

    This is an isolated output 6V 8A.
    Your -48 "unit" may be isolated as well.


    If the system grounding requires an intermediate stage, please provide details of the power required.