Other Parts Discussed in Thread: UCC39002
UCC29002 is used for load sharing among 3 AC-DC converters in our design. 3 No of TDK Lambda converter PFE300SA-12 outputs are connected via 3 No. of oring controller IC LTC4357 for final output loading of +12V @ 60A. When module is loaded for current more then 21A (ie 7A per converter), load sharing is failing randomly.
It is noted that the failure is happening always for higher output currents and load sharing failure 'current values' changes over testing, but nearly greater than 21A.
We have developed 3 modules, and each module load sharing section is behaving differently. First module is failing very rare where the second and third module is failing very often - and there is no hardware change among the modules.
Our input to the module is AC 200V 400Hz, which is convertered into +12V DC , which is the VDD for UCC29002. Switching frequency of the converter is 232KHz for the output side.
We have got better result (Load sharing failed for higher out put current) while configuring the EAO pin compensation. 10uF and 220 Ohm resistor is used in First module gives better current sharing, where same implimented in second and third modules not helping for load sharing.
While probing the IC pin functioning, 400Hz noise is observed in the 'EAO pin' for an amplitude of 50mV (Approx) in the sections where the load sharing is failing. For Example, In second module there are three UCC29002 located at different places of PCB. In that, UCC29002 at Location 2 is having 400Hz component noise in its EAO pin, comparatively higher than that of location 1 & 3. While increasing module output current, Location 2 EAO is saturating 3.4V (Approx) and CSO measures 0V. So always the current sharing section with higher '400Hz noise coponent' is failing in load sharing.
Once the load sharing is failed, oring mosfet corresponding to failed Load sharing IC found as OFF (Vgs < Vgs th). Also individual output voltage of the converter corresponding to the failed Load sharing IC section, output voltage is measured less than the ored voltage (ie other converter voltages). Example, For Vadj set as 450mV - Load sharing failed Converter output measures as 12.4V where the remaining two converters are at 12.45V. So oring section is not turning ON the mosfet since it senses a negative voltage from OUT to IN.
Kindly advice for any further check to be done. Pls advice the correction.
Pls advice the EAO compensation - capacitance and resistor values for Load sharing LOOP to not to respond for the 400Hz noise observed in the IC.
Regards