Hi TI Team,
We are now modifying our circuit based on TPS259541DSG. But I have below questions when using it, can you help to answer?
A quick response will be much appreciate, we are quite in hurry.
1. Can fault pin left float?
2. Can inrush current trigger over-current protection?
3. How to deal with large capacitance when start-up? Should I use the maximum dVdt to reduce the time at current limit state or use a lower ramp rate?
4. How to handle the back emf from relay at steady state?(The customer's load is working with 6 relay switches.)
I’m using the TI calculation tool, but it turn out give some errors on my input. Our load is a large capacitor and 2 DCDC convertor
Parameter |
Description |
Value |
Units |
Tolerance |
3.3V or 5V or 12V version |
Refer Table-1 and select based on OverVoltage Clamp/Cut-off and Active High/Low requirement |
TPS259541 |
|
|
VIN (max) |
Maximum Operating input voltage (magnitude) |
13.20 |
V |
|
UVset |
Undervoltage Threshold (VIN Rising) |
7.00 |
V |
|
VUVP |
Internal Undervoltage Protection Threshold (VIN Rising) |
2.54 |
V |
3.7% |
Cout |
Load Capacitance |
300.0 |
uF |
10.0% |
Rlstart |
Load at start-up (assumed to be resistive), Refer to Section 9.2.2.3.2 in Datasheet |
150.0 |
Ohm |
|
Imax |
Maximum continuous load current (magnitude) |
1.1 |
A |
|
Ilimit |
Current Limit, 7.5% higher than maximum continuous load current |
1.18 |
A |
|
VOVC |
Over Voltage Clamp |
13.70 |
V |
4.5% |