Hi,
Schematic review required. Input voltage will be 240VAC. Solenoid not needed. Only ground fault detection is needed.
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Tool/software:
Hi,
Schematic review required. Input voltage will be 240VAC. Solenoid not needed. Only ground fault detection is needed.
Hi,
Just out of curiosity - is the plan to monitor fault through ALARM pin?
The schematic looks good to me. We do recommend a snubber on the output pin as shown below. It may not be matter for this application, but just in case. The values are 500Ohm + 10nF.
Regards
Guang
Hi,
Yes only fault monitoring is required and I think it can be only done through ALARM pin, correct?
Added SCR pin monitoring to MCU. Also added zener at ALARM pin as the internal logic I believe works on 5V. Anything else that can be done to monitor fault?
Basit,
Guang is out of the office today but will reply when he returns on Monday, 3/31.
Louis
Hi Basit,
Yes the internal logic is 5V. The ground fault can be monitored on ALARM according to section 7.4.2 of the datasheet.
Regards
Guang