We are currently working on a design using a DRV421 in an RCD application.
Reading TI tech note: RCD leakage module using the DRV421, we have some question about the use of this in Type B (DC & AC measurement) scenarios.
According to DRV421 documentation, it states that the system should be powered up without a primary current, due to possible offset / residual magnetic field in the core (demag operation etc).
In these RCD applications (especially for Type B), there is a high chance that there could already be a DC current present in the primary. If we consider a 30mA RCD, there could already be significant offset. If it's quite high (perhaps equiv to 20mA or so), it will only take a few mA of current to trip a unit, which would be considered nuisance tripping.
The only way around this seems to be to use external switching components (contactor etc), so we could disconnect the primary during power up and de-mag.
Any thoughts appreciated.
Kind Regards,