Can i use two diffrent lvdt with 3 wire connection to single PGA970 chip
comman exitation frpm p1 and p2 and S1P and S2p to respective lvdt ,
as well as can i use additional LVDT with multiflexed mode with help pf GPIO
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Can i use two diffrent lvdt with 3 wire connection to single PGA970 chip
comman exitation frpm p1 and p2 and S1P and S2p to respective lvdt ,
as well as can i use additional LVDT with multiflexed mode with help pf GPIO
Hi Kundan,
In order to get meaningful phase information so that you can determine the direction of travel of the LVDT sensor with respect to the center position, you will have to sense both secondary coils from the LVDT, one at S1 and one at S2.
Because of this you cannot use the PGA970 to sense more than one LVDT at a time. It is possible to supply primary side excitation to more than one LVDT from the same PGA970, however.
Here is an application diagram showing how to use two PGA970 devices to synchronously measure 2 different LVDTs: