TIDA-010085: TIDA-010085 Ground connection

Part Number: TIDA-010085

I would like to know how the 'C' wire is connected in the TIDA-010085 reference design. Is the ISO_GND connected to the 'C' line in the HVAC system? 

  • Hi Adnan,

    For this design, the ISO-GND is not connected to the C wire, but is a floating ground (part of the isolation rail for the gate driver for each SSR). The C wire will come from the 120V->24VAC transformer and is a common connection to each SSR, and can be used for powering remaining portions of the SR board. 

    -Brian