This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Tool/software:
Hello,
The RTD measurements with an ADC made with a ratiometric measurements where a single IDAC excitationcurrent source and a the voltage accross the Reference resistance is used as voltage reference for the ADC.
My question is: What happens if an RTD sensor is cut (fails and it become equivelent to an open circuit) ? wouldn't that stop the flow of current, therefore no longer have a voltage reference for the ADC and that would screw up the ADC ?
Maybe I don't understand something.
Thank you in advance.
Hi Youness,
welcome to our e2e forum and thanks a lot for your interest in our ADS124S08.
Your understanding is absolutely correct, if you are using only one excitation current source to measure a 3-wire RTD.
The reference voltage for the ADC will be 0V in that case. The conversion results will then be quite undetermined, but most likely +FS or -FS.
To detect this fault situation I added the reference undervoltage monitor in the ADS124S08.
If you want to learn more about sensor fault detection with our ADCs, I can highly recommend the following app note:
RTD Wire-Break Detection Using Precision Delta-Sigma ADCs
Regards,
Joachim Wuerker