SN65HVD3086E - Termination for 1:1 connection.

Guru 19785 points
Other Parts Discussed in Thread: SN65HVD3086E, SN65HVD72, SN65HVD75

Hello Team,

This may be a simple question, however, please allow me to clarify.

Our customer will use SN65HVD3086E as a RS-485 full duplex 1:1 communication.

Below would be the general application for multiple TX and RX, which has termination resistor at each end of the bus.

When used in 1:1 (1TX and 1RX), do you need termination resistor at RX side and also at the TX side ?
In this case what is the recommended resistor value that should be used ?


Best Regards,

Kawai

  • Hi Kawai,

    Termination resistors are always a good idea to include in an RS-485 design because they ensure good signal integrity for the application. The typical RS-485 bus impedance is 120 ohms. RS-485 is robust enough though that different termination schemes can be implemented. You could place a 120 ohm resistor at the receiver (RX) and have it work. If the data rate of the application is slow enough, giving you a really long bit time, it is OK to run the RS-485 network unterminated as any ringing that results from the unterminated lines will settle out before the sample point of the uC/uP. Here is a short blog I wrote on this topic:

    Other Parts Discussed in Post: SN65HVD72 , SN65HVD75 Welcome back to the “Get Connected” blog series on Analog Wire. In my previous post , I explored protecting your differential bus against system…
    By in Technical articles > Analog

    Please let me know if you have more questions?

  • Hello Michael-san,

    Thank you for the information. I understood that you would only require one 120 ohms termination resistor at the receiver (RX) side.

    Best Regards,
    Kawai