Hello,

I try to determine the Unit-Load paramter (Input Resistance) of SN75176BP following the description given in

  • TIA-485-A-1998, Section 4.1.1 - dc Unit load specification

and article


You can determine the unit-load parameter by sweeping the input voltage from -7 to +12V on one bus pin, with the other bus pin held at ground, and then measuring the input leakage current. You will measure both bus pins individually, with the transceiver both in a powered and unpowered state.


and

The U.L. Test Circuits I'm refering to are looking like this:



I know that I can get the Line input current / Input resistance from the according datasheet:

and



But as mentioned above I would like to measure the Line input current and calaculate the according Input resistance. For that I created the following two circuits

a) Isolated Power Supply / Arduino (Atmega 328p pu microcontroller / SN75176BP



b) Isolated Power Supply / LM7805 / SN15176BP


Vin = Vcc_PowerSupplyOut = 5V / 7V / 9V /12 V
Vcc = Vcc_SN75176BP = 0V or 5V
Driver Enable = low (0V)
Receiver Enable = low (0V)
Data Input = low (0V)

If I'm not mistaken both circuits above should reflect the test circuits mentioned in

meaning in order to measure the RECEIVERS Line input current the

  • DRIVER needs to be disabled (Driver Enable = low (0V))
  • RECEIVER needs to be enabled (Receiver Enable = low (0V))
  • Data Input doesnt matter (I put it to low (0V))

My problem is the following:
In case the SN75176BP is unpowered (Vcc_SN75176BP = 0V) everything seems to look ok, I measure as an example 0,85μA having Vin = Vcc_PowerSupplyOut = 11.16 V.

As soon as the SN75176BP is powered (Vcc_SN75176BP = 5V) and applying for example Vin = Vcc_PowerSupplyOut = 9.0 V or 12.0 V the device get's

  • extremely hot within seconds
  • the Input current measured at A or B is way beyond 300 mA
  • eventually the device is damaged and is no longer working


I figured out - or at least it looks to me - that this is happening as soon as I conect either

  • Terminal A or B to Ground
  • Driver/Enable Inputs to Ground


I'm pretty sure I'm doing something wrong here/the way I think how U.L. test circuits should work but I dont know what. Any help/explanation would be highly appreciated.


Thanks a lot in advance!

  • Hello,

    I'd expect the input currents to be low even with the device powered as long as the driver is disabled. To start, can you please verify that VCC is 5 V and DE is at 0 V? Does the issue show up when A or B is shorted to a test voltage while the other terminal remains floating?

    Max

  • Hello Max,

    thanks a lot for your quick reply and looking into this. Highly appreciated!

    To answer your question I checked VCC and DE and the results are as follows when using the circuit outlined in a) Isolated Power Supply / Arduino (Atmega 328p pu microcontroller / SN75176BP:

    • VCC --> Local_Ground: 5.02 V
    • DE --> Local_Ground: 0 V

    Everything is working fine when applying Test Voltages ranging from 3.0 V up to 7.0 V while having one of the terminals shorted to GND. As soon as I apply Test Voltages 9.0 V and 12.0 V the "issue" starts (Device get's extremely hot and finally get's damaged).

    As well no issue observed when applying Test Voltages 9.0 V and 12.0 V to either A or B terminal while keeping the other terminal floating (so no connection to GND).

    On top I build a "small" RS-485 bus having one SN75176B running as

    • SENDER (RE = DE = HIGH (5.0 V)

    and another SN75176B running as

    • RECEIVER (RE = DE = LOW (0.0 V))

    Signals generated on SENDER's D-Input (HIGH and LOW) can be well seen seen/received on the other device running as RECEIVER.

    Best Regards,
    Peter

  • Hello Max,

    I need to correct my statement/answer made above in regards to


    Everything is working fine when applying Test Voltages ranging from 3.0 V up to 7.0 V while having one of the terminals shorted to GND. As soon as I apply Test Voltages 9.0 V and 12.0 V the "issue" starts (Device get's extremely hot and finally get's damaged).

    In fact the statement/answer should be:
    Everything is working fine when applying Test Voltages ranging from 3.0 V up to 5.0 V while having one of the terminals shorted to GND. As soon as I apply Test Voltages >= 7.0 V up to 12.0 V the "issue" starts (Device get's extremely hot and eventaully get's damaged).

    Best Regards
    Peter

  • Peter,

    What you have seen really puzzled us. If the driver is disabled, the device should have input current in the order of uA. However I cannot figure out what went wrong. To debug, could you start from the very basic setup, for example, providing a single DC supply to the device and repeating the test? Please make sure the pin voltage is reference to the same ground as the device.

    Regards,

    Hao

  • Hello Hao,

    thanks a lot for your reply. It puzzles me as well as everything is working like a charm as long as the voltage is below 7.0 V. Anyhow I repeated the tests using the setup's listed above in a) and b) having even resistor R1 removed - same result as in my initial problem statement. Maybe worth to mention that EVERYTHING ELSE is working as it should and as well the measurement circuits provided in the datasheet are working like a charm.

    Could it be due to the power supply I'm using? It's a regular power supply with PRIMARY 100V - 240V ~ and SECONDARY 3.0V / 4.5V / 5.0V / 6.0V / 7.5 V / 9.0 V / 12.0 V DC as mentioned above.

    Any schematic of how an Unit Load test circuit should look like would be highly appreciated.

    Best Regards,
    Peter

  • Hello,

    I think my problem is (partially) solved. Using quadruple differential line receiver SN75175 and following circuit

    c) Isolated Power Supply / SN75175

    Vin = Vcc_PowerSupplyOut = 5V / 7V / 9V /12V
    Vcc = Vcc_SN75175 = 0V or 5V
    Receiver Enable = high (5V)

    everything is working as expected. The device is

    • not getting hot
    • line input current is in the range of μA

    when applying for example Vin = Vcc_PowerSupplyOut = 9V or 12V to either terminal A or B while the other terminal is held at 0V (GND).

    On top when building RS-485 using

    • MAX485 as Sender (DE = HIGH, RE = LOW [echoing what I'm sending])
    • SN75176B as Receiver (DE = LOW, RE = LOW)

    and sending data via the

    • MAX485 DI pin

    I can see the signals sent echoed on MAX485 and arriving at SN75176B.

    Same is true when building RS-485 using

    • SN75176B as Sender (DE = HIGH, RE = LOW [echoing what I'm sending])
    • MAX485 as Receiver (DE = LOW, RE = LOW)

    and sending data via the

    • SN75176B DI pin

    I can see the signals sent echoed on SN75176B and arriving at MAX485.

    So what I wanted to show here is that I'm correctly setting the input signals when it comes to configuring the according tranceiver as Sender and/or Receiver which is apparently the case, no?

    In both aforementioned cases I did not change the MCU nor the power supply. So I'm almost certain that it has nothing to do the way I set HIGH and/or LOW on the MCU nor the power supply.
    As well when repeating the tests using hardwired input signal levels it's working as expected.

    The only difference I'm able to spot between SN75175 and SN75176BP is - apart from SN75175 having only Receiver units - is that SN75175 has

    • no fail-safe feature

    that guarantees a logic-high output if the input is open circuit.

    Interestingly enough I see the same behavior when using MAX485 configured as Receiver and applying for example Vin = Vcc_PowerSupplyOut = 9.0 V or 12.0 V. As well the device gets

    • extremely hot within seconds
    • the Input current measured at A or B is way beyond 300 mA
    • eventually the device is damaged and is no longer working


    So same behavior as seen for SN75176B. But both transceivers SN75176B and MAX485 have the fail-safe feature whereas SN75175 doesn't.

    So maybe my issue is related to that (fail-safe feature) but I'm not at all expert enough to judge on that.

    Anyhow using the SN75175 and measuring the unit-load parameter by sweeping the input voltage from -7 to +12V on one bus pin, with the other bus pin held at ground is working now as expected.


    Best Regards,
    Peter

  • Hi Peter,

    I wouldn't expect fail-safe functionality to have a significant effect on input currents like you are reporting.  Plus, SN75176B does not feature internal fail-safe biasing.  So, I think something else is going on here.  But if you're happy with the solution, maybe it isn't worth debugging further.  By the way, if you wanted to change to a different single-channel transceiver, I'd recommend a newer device like THVD1550.  SN75176 was developed in the mid-80s, and there have been great strides made in integrated circuit technology since then.

    Regarding the DE/RE control lines - it sounds like you have them correct.  Some users prefer pulling /RE high when sending messages to block the echo, but that is a personal preference.  (Having the echo enabled can be useful in detecting transmission errors if the software implementation allows for it.)  The most important thing is that the DE line be high on at most one transceiver at a time.  You want to avoid having multiple nodes sending at the same time - this would corrupt the messages.

    Max

  • Hello Max,

    thanks a lot for your detailed response. In regards to


    Plus, SN75176B does not feature internal fail-safe biasing.

    you are absolutely correct - my apologies for that. Was mixing it up with


    The driver differential outputs and the receiver differential inputs are connected internally to form differential input/output (I/O) bus ports that are designed to offer minimum loading to the bus when the driver is disabled or VCC = 0.

    My intention was to get familiar/play a bit/gain some further knowledge with RS485 Transeivers in general and the SN75176B transceiver looked to me as the ideal candidate (as well when looking at the price of a single device and given the fact how many devices I destroyed by now it seemed to be a good decision). Same is true for having DE and /RE control lines enabled at the same time - I just wanted to make sure that my understanding is correct and the according HIGH and LOW signals are send correctly by the MCU towards the transceier.

    As you mentioned above - overall I'm happy with the solution found. Maybe I will invest in a newer device as suggested by you.

    Overall thanks a lot for all your answers, the time spend and great support! As well a big thank you to Hao.


    Peter

  • Hello,

    just for the sake of completeness I replaced TI SN75176B with Linear Technology RS485-Transceiver LTC485CN8 and measured the Receiver Line input current using the circuits outlined in

    • a) Isolated Power Supply / Arduino (Atmega 328p pu microcontroller / SN75176BP
    • b) Isolated Power Supply / LM7805 / SN75176BP

    above.

    And guess what? Everything is working like a charm. The device is

    • not getting hot at all
    • line input current is in the range of μA (< 1 mA) as specified in the according datasheet


    So long story short: Using

    • Linear Technology RS485-Transceiver LTC485CN8

    or

    • TI quadruple differential line receiver SN75175

    one can determine the unit-load parameter as described here for example:

    • RS-485 basics: how to calculate unit loads and the maximum number of nodes on your network


    You can determine the unit-load parameter by sweeping the input voltage from -7 to +12V on one bus pin, with the other bus pin held at ground, and then measuring the input leakage current. You will measure both bus pins individually, with the transceiver both in a powered and unpowered state.

    Best Regards,
    Peter

  • Peter,

    Thanks for your further investigation. We will order SN75176B samples for the bench testing.

    Hao

  • Hello Hao,

    any results yet from the bench testing?

    Best Regards,
    Peter

  • Peter,

    I'm sorry for the delay. I just received the samples last week. I plan to update you early next week.

    Regards,

    Hao

  • Peter,

    Thanks so much for your patience. I tested a few devices with high common mode voltage, but didn't see any issues. Here are the curve trace results for your reference. The curve trace machine feeds the voltage on the pin and records the current as the voltage varies.

    In this test, the device is powered off. You can see the leakage current is low until the voltage reaches +/- 20V.

    Similarly in this test, the device is powered on but in receiver only mode. The results are similar.

    Please let me know if you have further questions about the device. If you want us to test the parts you see abnormal, you can consider the return process through the vendor.

    Regards,

    Hao

  • Hello Hao,

    thank you so much for your dedication, hard work and contribution to this topic (my problem). The tests performed by you show clearly that I'm doing something wrong on my end (as mentioned in my initial post). Would you mind to share  the schema/wiring/circuit you have used for determining the UL for SN75176B?

    BTW: I'm using a digital multimeter for current/voltage measurements. I guess this shouldn't matter/causing the issue I face when the device is powered on and trying to determine the UL paramter of SN75176B.

    Best Regards,
    Peter

  • Peter,

    You can refer to this app note (page 6-7) about the UL measurement setup.

    www.ti.com/.../slla036d.pdf

    You can put the multimeter in serial with a voltage source for the measurement.

    I found a diagram online and hopefully it's helpful to you.

    www.hagerty.com/.../

    Regards,

    Hao

  • Hello Hao,

    once again a big thank you for all the links, efforts and time spend. Still donno what I'm doing wrong when trying to determine the UL for TI SN75176B whereas it's working like a charm when using

    • Linear Technology RS485-Transceiver LTC485CN8
    • TI quadruple differential line receiver SN75175


    So I think with all the time and efforts spend this topic can be closed.


    Best Regards,
    Peter