Manual issue concerning ADC calibration

Hi,
I think there is a bug in the manual.
According the manual, BRIDGE_EN == 0 and HILO == 0 gives:
/* (AD(REFHI)*R1 + AD(REFLO)*R2) / (R1 + R2) */
but (at least on the TMS570USB stick) it seems to be
/* (AD(REFLO)*R1 + AD(REFHI)*R2) / (R1 + R2) */

The other bit-combinations give correct values.
  • Hello,

    The resistances R1 and R2 are typically 7K-ohm and 5K-ohm respectively. These values are selected such that two combinations of the BRIDGE_EN and HILO bits yield 7/12th and 5/12th of VREFHI as the reference voltage converted (with VREFLO = 0V). The {BRIDGE_EN = 0, HILO = 0} combination gives a conversion result of 0x952.

    This is a result of the reference voltage being VREFHI * 7/12.

    Similarly, you will get a reference voltage of VREFHI * 5/12 for the {BRIDGE_EN = 0, HILO = 1} combination.

    I have verified this on a USB stick here.

    Please confirm that there is no issue with the documentation.

    Regards,

    Sunil

  • Hi
    sorry, for the late answer.
    On the USB stick I get:

    BRIDGE_EN = 0, HILO = 0 => 2386 ( ~ 7/12)
    BRIDGE_EN = 0, HILO = 1 => 1704 ( ~ 5/12)
    BRIDGE_EN = 1, HILO = 0 => 0
    BRIDGE_EN = 1, HILO = 1 => 4094

    But the documentation states that BRIDGE_EN = 0, HILO = 0 shall give 5/12 (table 15-3).
    So, yes there seems to be a bug in the docu.
  •  

    Hi Bastian,

    Since R1 is 7KOhm and R2 is 5KOhm, BRIDGE_EN = 0, HILO = 0, and AD_REFLO is 0V then I would interpret row 1 of the following table

    to result in 7K*AD_REFHI / (7K+5K) or 7/12*AD_REFHI rather than 5/12*AD_REFHI.  You don't agree?


  • Hi Brian,
    right, but Fig. 15-16 says R1 == 5k :-)
    So what is now correct ? The table or the figure.
  • Hi Bastian,

    The table is correct as evidenced by the actual conversion results. The figure will be corrected in the next update to the TRM. Thanks for identifying this issue.

    Regards,

    Sunil

  • Hi
    ok, I will fix my code.
    Maybe it is a good idea to have the values of R1/R2 also noted somewhere in the text and not only in the figure!
  • Bastian,

    You are correct.  We need to be more clear on this point.  We have this as a ticket to fix this in future TRM releases.   Sorry for your trouble!