Part Number: RM48L540
Hi,
To qualify SIL3 as per IEC61508 functional safety can we used 2 nos. of RM48L540 controller or single RM48L540 controller is ok for this?
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Part Number: RM48L540
Hi,
To qualify SIL3 as per IEC61508 functional safety can we used 2 nos. of RM48L540 controller or single RM48L540 controller is ok for this?
Hi Rohit,
A single Hercules MCU is designed to support IEC61508 up to SIL3 and ISO 22201 up to SIL 2 compliance. Dual Hercules MCU can support IEC 61508 SIL 4 and ISO 22201 SIL 3 (dual channels with comparison).
For more details refer below thread:
--
Thanks & regards,
Jagadish.
where should I get failure mode Distribution & FIT value of this microcontroller. could you share the link?
Hi Jagadish Ji,
Hope you are fine and doing well.
I have been continuously followed up on for an NDA with the Texas Instruments Engineer in India. But still, I am not getting any feedback from them. As time is running out, I request that you help me with an NDA agreement for the RM48 controller.
Hi Rohit,
I forwarded your and company details to TI India Local sales team. I hope they will contact you soon.
Please wait for couple of days. If you don't get any response, please ping me back.
--
Thanks & regards,
Jagadish.