No, it is not the base Frequency. It is the "base current", we use this number to normalize the measured phase current.
10.3 is defined becasue: if the ADC measures a phase shunt current 0 or 3.3v (dynamic range of the plug in control card), it represents -10.3A or 10.3A.
The base frequency of this setup is 230, which means 230*60/4 = 3450RPM. The motor itself can run 6000rpm or higher. But, the power supply in the kit is only 24v. The back EMF of the motor is 4.6v/1000rpm, once running at 4000rpm, the back EMF will be 18.4v, we still need to reserve some voltage to generate the toque. That is why we define 230 as the base frequency. If you want a higher base frequency, you can:
1. use other power supply, e.g a 36v DC power supply, or
2. use field weakening to increase the current consumption but reducing the back EMF. Then, be care for of hitting the current limit of the power supply.
Regards,
Haixiao
Hiroyasu,
it is the maximum ADC measurable DC Bus(66.32V)/sqrt(3).
Regards,
Haixiao