Encoder position count reading is not proper but speed is measured correctly

Other Parts Discussed in Thread: TMS570LS1227, DRV8301

Hi,

I am using Encoder output from my DSpace and reading in my DRV8301LS12  kit with TMS570LS1227 control card.

My Line count is 1000 and pole pair is 8. 

When I give constant speed of 1000RPM, I am getting bellow reading in mechanical position count and in electrical angle.  The readings looks , there is something wrong. Could you please help?. Also when I change the log scale from 1 to 5. The electrical angle looks good, but the frequency of waveform is wrong ( Still my motor speed RPM is showing exactly 1000 RPM inside the CCS debug environment.)

I have attached both the waveform.

logscale1

Logscale5

My sampling frequency is 8KHz. and clock frequency is 80MHz. Encoder QUPRD=800000

Thanks & Regards,

Rathinavel

  • When I am doing my experiment repeatedly, I am able to get correct graph when the logscalar i s5 in the standard TI FOC software. ie) for 1000RPM, my mechanical cycle will exactly end with 96 sample. ( 96*5* (1/8e3)=60ms=1000rpm).

    But When I make to logscalar 1, its always something wrong, this is only due to some log problem or actual values itself varying randomly?

  • Hello Rathinavel,

    I have forwarded your post to one of our DRV8301 experts. They should be back to you shortly.

  • Hi, 

    Thanks you for your support, the problem is solved. It is due to the same issue, that is mentioned in this thread

    http://e2e.ti.com/support/development_tools/code_composer_studio/f/81/t/345907.aspx.

    Also We should maintain display size and acquisation size of the Graph should be same as buffer size  to avoid confusion in reading data.

    Regards,

    Rathinavel