Hi,everyone,According to IEC61508,TMS570LS20216 is regarded as type B. and it is 1oo2(D) architecture ,so the HFT(hardware fault tolerance) of TMS570LS20216 is 1(Do I understand correctly?)
Now,TMS570LS20216 is certified to SIL3 by the third party EXDIA。according to table 3 in chapter 7.4.3.1.1 of IEC61508-2,SIL3 means the SFF(safety failure fraction) of TMS570LS20216 equals to 60%~99%. Why not increase the SFF of it to >99%,then TMS570LS20216 will achieve SIL4 ?what's the reason?technical or cost? Thanks.