TMS320F28075: EPWM: Tripzone: Maintain deadtime between complimentary outputs on trip event

Part Number: TMS320F28075

Hi,

I am working on a system where complimentary ePWM A/B outputs are used to control a half bridge driver.  I'm using the Time Base, Counter Compare, Action Qualifier and Dead time IP Blocks to generate the complimentary outputs.

I want to use the CMPSS to detect overcurrent/voltage events and shut down the bridge by putting the gates in a known state until the firmware deems it safe to restart.

I initially implemented the CMPSS => ePWM XBAR => One Shot Trip Zone flow.  However, I started blowing up bridges on trip conditions.  The trip zone didn't enforce the dead times and changed the high/low channel signals at the same time which created a shoot through condition.  My understanding is this is because the trip zone block falls after the Action Qualifier.

I've been able to implement a software based approach using the "EPWM_setActionQualifierContSWForceAction" function.  This approach adheres to the dead time requirements.

However....

I feel like I must be able to tie this flow together via hardware modules so it is more responsive.  And it seems like maintaining dead times must be a pretty bread and butter requirement. 

Any suggestions on how to do this without getting the cpu involved?

Thanks,

-Colin