Hi team,
Customer have some questions about "OSR" and "Sinc" setting for F28377D filters.
1 Can I change the OSR to numbers which is not 2^n, I mean OSR_125,or OSR_136? is there any influence to the accuracy?
2 From the parameter below, the OSR has a corresponding SINC, what's the relationship behind that? can I set OSR=128 with sinc=6?
Thank you!
Hi Yuan,
2 From the parameter below, the OSR has a corresponding SINC, what's the relationship behind that? can I set OSR=128 with sinc=6?
The values in above table are the shift values which need to be configured to keep the result in valid range. For OSR = 128 & Sinc3 filter, shift value of 7 should be used.
Thanks
Vasudha