This thread has been locked.

If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.

TMS320F28335: Linking PWM modules

Part Number: TMS320F28335


Team, 

My customer has had his PWM modules linked together with the SYNC output of PWM1 provided to PWM2 – PWM6 through the master/slave PWM module configuration options. He is trying to break the link between modules 2 & 3 so that he can have the following daisy chains:

  • PWM1 -> PWM2
  • PWM3 -> PWM4 -> PWM5 -> PWM6

When customer tried setting EPwm3Regs.TBCTL.bit.PHSEN = TB_DISABLE he found that the CTR would pause at one count for a period of time on both the count up and count down. This is all using Matlab Simulink auto-generated code that is pulling in a custom C module to help with the configuration of the PWM. The PWM is also triggering an ISR that is used for calculation of all of the control code. There is some issue with the way that it is configured that is preventing him from achieving good operation when he does not link all the PWMs as a slave to PWM1.

See figure 51 - here: http://www.ti.com/lit/ug/sprug04a/sprug04a.pdf

Your inputs would be greatly appreciated. 

Thanks!

Viktorija

  • Viktorija,

    There should be no issue with separating the ePWM sync chain into two time domains.

    Viktorija Cecil said:
    he found that the CTR would pause at one count for a period of time on both the count up and count down.

    Can you provide more details here?

    1. How long did it pause?
    2. What were the counter values?
    3. What PWMs experienced this phenomena?  
    4. Is the customer preforming any on-the-fly changes to the PWM?
    5. Does this only happen once, or does this happen every period?
    6. How is the customer detecting that the TBCTR has stopped?
      1. Have the customer observe if TBCLKSYNC's value changes during run time.

     have you seen any issues similar to this when using ePWM sync chain?

    Regards,
    Cody 

  • Cody, 

    Here are details from customer:

    I finally was able to reproduce a problem(s) that we need to resolve with the PWM modulators written with purely C code. There are two problems that I can replicate in C code, as well as model-based. I apologize for the length of this e-mail, but it is very important to communicate the issue(s) so that they can be understood and addressed.

     

    First, our objective is to have:

     

    1. ePWM1 and ePWM2
      1. Run at 24kHz
      2. Phase synchronized at startup with 0 degree phase shift
      3. Center-aligned, interleaved modulation, i.e., Up/Down counter.
    1. ePWM3 and ePWM4
      1. Run at 72kHz
      2. Phase synchronized at startup with 0 degree phase shift
      3. Constant 50% modulation
    1. ePWM5 and ePWM6
      1. Run at 72kHz
      2. Phase synchronized at 180 degrees with respect to ePWM3 and ePWM4 at startup
      3. Constant 50% modulation
      4. Variable phase shift with respect to ePWM3 and ePWM4 while operating

     

    Here’s how I have setup the PWM modulators:

     

    Active Front End (ePWM1 and ePWM2):

     

    1. Frequency is 24kHz with an every 3rd event SOCA (Start of Conversion for ADCs) and ePWM1 interrupt, i.e., EPwm1Regs.ETPS.1bit.INTPRD = ET_3RD
    2. Uses an Up/Down counter for center-aligned interleaved modulation, i.e., EPwm1Regs.TBCTL.bit.CTRMODE = TB_COUNT_UPDOWN
    3. Phase Enabled for startup synchronization, so the PHSEN bit is set for both with a phase offset of zero, i.e., EPwm1Regs.TBPHS.half.TBPHS = 0.

     

    Here is my code for initialization of ePWM1 and ePWM2 to achieve the above results:

     

    void EPwm1Init(void)

    {

           /*** Initialize ePWM1 modules ***/

     

           /*-- Setup Time-Base (TB) Submodule --*/

     

           EPwm1Regs.TBPRD = PLL_FREQUENCY / AfePwmFrequency * 0.5;             // Multiply by 0.5 because we're using an up/down counter and the period is half the frequency

     

           // Time-Base Control Register

           EPwm1Regs.TBCTL.bit.CTRMODE    = TB_COUNT_UPDOWN;                 // Counter Mode

           EPwm1Regs.TBCTL.bit.SYNCOSEL   = TB_CTR_ZERO;                       // Sync output select to downstream ePWM2 module

           EPwm1Regs.TBCTL.bit.PRDLD      = TB_SHADOW;                          // Shadow select

           EPwm1Regs.TBCTL.bit.PHSEN      = TB_ENABLE;                          // Phase load enable

           EPwm1Regs.TBCTL.bit.PHSDIR     = TB_DOWN;                            // Phase Direction

           EPwm1Regs.TBCTL.bit.HSPCLKDIV  = TB_DIV1;                            // High speed time pre-scale

           EPwm1Regs.TBCTL.bit.CLKDIV     = TB_DIV1;                            // Timebase clock pre-scale

     

           // Time-Base Phase Register

           EPwm1Regs.TBPHS.half.TBPHS     = 0;          // Phase offset register

     

           EPwm1Regs.TBCTR = 0x0000;  /* Clear counter*/

     

           /*-- Setup Counter_Compare (CC) Submodule --*/

           // Counter-Compare Control Register

           EPwm1Regs.CMPCTL.bit.SHDWAMODE = CC_SHADOW;                       // Compare A block operating mode.

           EPwm1Regs.CMPCTL.bit.SHDWBMODE = CC_SHADOW;                               // Compare B block operating mode.

           EPwm1Regs.CMPCTL.bit.LOADAMODE = CC_CTR_ZERO_PRD;                 // Active compare A

           EPwm1Regs.CMPCTL.bit.LOADBMODE = CC_CTR_ZERO_PRD;                 // Active compare A

     

           EPwm1Regs.CMPA.half.CMPA = EPwm1Regs.TBPRD * 0.5;                // 50% modulation

           EPwm1Regs.CMPB = EPwm1Regs.TBPRD * 0.5;                                 // 50% modulation

     

           /*-- Setup Action-Qualifier (AQ) Submodule --*/

           EPwm1Regs.AQCTLA.bit.CAU = AQ_CLEAR;                                   // Clear PWM when latch value = counter when counting up

           EPwm1Regs.AQCTLA.bit.CAD = AQ_SET;                                            // Set PWM when latch value = counter when counting down

           EPwm1Regs.AQCTLA.bit.ZRO = AQ_NO_ACTION;                                // No action PWM when counter = 0

           EPwm1Regs.AQCTLA.bit.PRD = AQ_NO_ACTION;                                // Do nothing when counter = period

           EPwm1Regs.AQCTLA.bit.CBU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm1Regs.AQCTLA.bit.CBD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           /* Setup action qualifiers for B module */

           EPwm1Regs.AQCTLB.bit.CAU = AQ_SET;                                            // Set PWM when latch value = counter when counting up

           EPwm1Regs.AQCTLB.bit.CAD = AQ_CLEAR;                                    // Clear when latch value = counter when counting down

           EPwm1Regs.AQCTLB.bit.ZRO = AQ_NO_ACTION;                                // Do nothing PWM when latch counter = 0

           EPwm1Regs.AQCTLB.bit.PRD = AQ_NO_ACTION;                                // Do nothing when counter = period

           EPwm1Regs.AQCTLB.bit.CBU = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting up on B sub-module

           EPwm1Regs.AQCTLB.bit.CBD = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting down on B sub-module

     

           // Action-Qualifier Software Force Register

           EPwm1Regs.AQSFRC.bit.RLDCSF    = 3;                              // Reload from Shadow options

     

           // Action-Qualifier Continuous S/W Force Register Set

           EPwm1Regs.AQCSFRC.bit.CSFA     = 0;          // Continuous Software Force on output A

           EPwm1Regs.AQCSFRC.bit.CSFB     = 0;          // Continuous Software Force on output B

     

           /*-- Setup Dead-Band Generator (DB) Submodule --*/

           // Dead-Band Generator Control Register

           EPwm1Regs.DBCTL.bit.OUT_MODE   = 3;          // Dead Band Output Mode Control

           EPwm1Regs.DBCTL.bit.IN_MODE    = 0;          // Dead Band Input Select Mode Control

           EPwm1Regs.DBCTL.bit.POLSEL     = 2;          // Polarity Select Control

     

           EPwm1Regs.DBRED = (Uint16)(PLL_FREQUENCY * AfeDeadtime);

           EPwm1Regs.DBFED = (Uint16)(PLL_FREQUENCY * AfeDeadtime);

     

           /*-- Setup Event-Trigger (ET) Submodule --*/

           // Event-Trigger Selection and Event-Trigger Pre-Scale Register

           EPwm1Regs.ETSEL.bit.SOCAEN     = 1;          // Start of conversion A Enable

           EPwm1Regs.ETSEL.bit.SOCASEL    = 1;          // Start of conversion A Select

           EPwm1Regs.ETPS.bit.SOCAPRD     = 2;          // EPWM1SOCA Period Select

           EPwm1Regs.ETSEL.bit.SOCBEN     = 0;          // Start of conversion B Enable

           EPwm1Regs.ETSEL.bit.SOCBSEL    = 1;          // Start of conversion B Select

           EPwm1Regs.ETPS.bit.SOCBPRD     = 1;          // EPWM1SOCB Period Select

           EPwm1Regs.ETSEL.bit.INTEN      = 1;          // EPWM1INTn Enable

           EPwm1Regs.ETSEL.bit.INTSEL     = ET_CTR_PRD; // EPWM1INTn Select

           EPwm1Regs.ETPS.bit.INTPRD      = ET_3RD;     // EPWM1INTn Period Select

     

           /*-- Setup PWM-Chopper (PC) Submodule --*/

           // PWM-Chopper Control Register

           EPwm1Regs.PCCTL.bit.CHPEN      = 0;          // PWM chopping enable

           EPwm1Regs.PCCTL.bit.CHPFREQ    = 0;          // Chopping clock frequency

           EPwm1Regs.PCCTL.bit.OSHTWTH    = 0;          // One-shot pulse width

           EPwm1Regs.PCCTL.bit.CHPDUTY    = 0;          // Chopping clock Duty cycle

     

     

           /*-- Set up Trip-Zone (TZ) Submodule --*/

           EALLOW;

           EPwm1Regs.TZSEL.all = 0;

     

           // Trip-Zone Control Register

           EPwm1Regs.TZCTL.bit.TZA        = 2;          // TZ1 to TZ6 Trip Action On EPWM1A

           EPwm1Regs.TZCTL.bit.TZB        = 2;          // TZ1 to TZ6 Trip Action On EPWM1B

     

           // Trip-Zone Enable Interrupt Register

           EPwm1Regs.TZEINT.bit.OST       = 0;          // Trip Zones One Shot Int Enable

           EPwm1Regs.TZEINT.bit.CBC       = 0;          // Trip Zones Cycle By Cycle Int Enable

     

           EDIS;

     

    } /* End of EPwm1Init */

     

     

    void EPwm2Init(void)

    {

           /*** Initialize ePWM2 modules ***/

           /*-- Setup Time-Base (TB) Submodule --*/

           EPwm2Regs.TBPRD = PLL_FREQUENCY / AfePwmFrequency * 0.5;             // Multiply by 0.5 because we're using an up/down counter and the period is half the frequency

     

           // Time-Base Control Register

           EPwm2Regs.TBCTL.bit.CTRMODE    = TB_COUNT_UPDOWN;                 // Counter Mode

           EPwm2Regs.TBCTL.bit.SYNCOSEL   = TB_DISABLE;                       // NO downstream synchronization to ePWM3 module

           EPwm2Regs.TBCTL.bit.PRDLD      = TB_SHADOW;                       // Shadow select

           EPwm2Regs.TBCTL.bit.PHSEN      = TB_ENABLE;                       // Phase load enable

           EPwm2Regs.TBCTL.bit.PHSDIR     = TB_DOWN;                       // Phase Direction

           EPwm2Regs.TBCTL.bit.HSPCLKDIV  = TB_DIV1;                       // High speed time pre-scale

           EPwm2Regs.TBCTL.bit.CLKDIV     = TB_DIV1;                       // Timebase clock pre-scale

     

           // Time-Base Phase Register

           EPwm2Regs.TBPHS.half.TBPHS     = 0;          // Phase offset register

     

           EPwm2Regs.TBCTR = 0x0000;  /* Clear counter*/

     

           /*-- Setup Counter_Compare (CC) Submodule --*/

           // Counter-Compare Control Register

           EPwm2Regs.CMPCTL.bit.SHDWAMODE = CC_SHADOW;  // Compare A block operating mode.

           EPwm2Regs.CMPCTL.bit.SHDWBMODE = CC_SHADOW;  // Compare B block operating mode.

           EPwm2Regs.CMPCTL.bit.LOADAMODE = CC_CTR_ZERO_PRD;          // Active compare A

           EPwm2Regs.CMPCTL.bit.LOADBMODE = CC_CTR_ZERO_PRD;          // Active compare A

     

           EPwm2Regs.CMPA.half.CMPA = (Uint16)(EPwm2Regs.TBPRD * 0.5);        // Startup with 50% modulation

           EPwm2Regs.CMPB = (Uint16)(EPwm2Regs.TBPRD * 0.5);                       // Startup with 50% modulation

     

           /*-- Setup Action-Qualifier (AQ) Submodule --*/

           EPwm2Regs.AQCTLA.bit.CAU = AQ_CLEAR;                                   // Clear PWM when latch value = counter when counting up

           EPwm2Regs.AQCTLA.bit.CAD = AQ_SET;                                            // Set PWM when latch value = counter when counting down

           EPwm2Regs.AQCTLA.bit.ZRO = AQ_NO_ACTION;                                // No action PWM when counter = 0

           EPwm2Regs.AQCTLA.bit.PRD = AQ_NO_ACTION;                                // Do nothing when counter = period

           EPwm2Regs.AQCTLA.bit.CBU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm2Regs.AQCTLA.bit.CBD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           /* Setup action qualifiers for B module */

           EPwm2Regs.AQCTLB.bit.CAU = AQ_SET;                                            // Set PWM when latch value = counter when counting up

           EPwm2Regs.AQCTLB.bit.CAD = AQ_CLEAR;                                    // Clear when latch value = counter when counting down

           EPwm2Regs.AQCTLB.bit.ZRO = AQ_NO_ACTION;                                // Do nothing PWM when latch counter = 0

           EPwm2Regs.AQCTLB.bit.PRD = AQ_NO_ACTION;                                // Do nothing when counter = period

           EPwm2Regs.AQCTLB.bit.CBU = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting up on B sub-module

           EPwm2Regs.AQCTLB.bit.CBD = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting down on B sub-module

     

           // Action-Qualifier Software Force Register

           EPwm2Regs.AQSFRC.bit.RLDCSF    = 3;          // Reload from Shadow options

     

           // Action-Qualifier Continuous S/W Force Register Set

           EPwm2Regs.AQCSFRC.bit.CSFA     = 0;          // Continuous Software Force on output A

           EPwm2Regs.AQCSFRC.bit.CSFB     = 0;          // Continuous Software Force on output B

     

           /*-- Setup Dead-Band Generator (DB) Submodule --*/

           // Dead-Band Generator Control Register

           EPwm2Regs.DBCTL.bit.OUT_MODE   = 3;          // Dead Band Output Mode Control

           EPwm2Regs.DBCTL.bit.IN_MODE    = 0;          // Dead Band Input Select Mode Control

           EPwm2Regs.DBCTL.bit.POLSEL     = 2;          // Polarity Select Control

     

           EPwm2Regs.DBRED = (Uint16)(PLL_FREQUENCY * AfeDeadtime);

           EPwm2Regs.DBFED = (Uint16)(PLL_FREQUENCY * AfeDeadtime);

     

           /*-- Setup Event-Trigger (ET) Submodule --*/

           // Event-Trigger Selection and Event-Trigger Pre-Scale Register

           EPwm2Regs.ETSEL.bit.SOCAEN     = 0;          // Start of conversion A Enable

           EPwm2Regs.ETSEL.bit.SOCASEL    = 1;          // Start of conversion A Select

           EPwm2Regs.ETPS.bit.SOCAPRD     = 3;          // EPWM2SOCA Period Select

           EPwm2Regs.ETSEL.bit.SOCBEN     = 0;          // Start of conversion B Enable

           EPwm2Regs.ETSEL.bit.SOCBSEL    = 1;          // Start of conversion B Select

           EPwm2Regs.ETPS.bit.SOCBPRD     = 1;          // EPWM2SOCB Period Select

           EPwm2Regs.ETSEL.bit.INTEN      = 0;          // EPWM2INTn Enable

           EPwm2Regs.ETSEL.bit.INTSEL     = 2;          // EPWM2INTn Select

           EPwm2Regs.ETPS.bit.INTPRD      = 3;          // EPWM2INTn Period Select

     

           /*-- Setup PWM-Chopper (PC) Submodule --*/

           // PWM-Chopper Control Register

           EPwm2Regs.PCCTL.bit.CHPEN      = 0;          // PWM chopping enable

           EPwm2Regs.PCCTL.bit.CHPFREQ    = 0;          // Chopping clock frequency

           EPwm2Regs.PCCTL.bit.OSHTWTH    = 0;          // One-shot pulse width

           EPwm2Regs.PCCTL.bit.CHPDUTY    = 0;          // Chopping clock Duty cycle

     

           /*-- Set up Trip-Zone (TZ) Submodule --*/

           EALLOW;

           EPwm2Regs.TZSEL.all = 0;

     

           // Trip-Zone Control Register

           EPwm2Regs.TZCTL.bit.TZA        = 2;          // TZ1 to TZ6 Trip Action On EPWM2A

           EPwm2Regs.TZCTL.bit.TZB        = 2;          // TZ1 to TZ6 Trip Action On EPWM2B

     

           // Trip-Zone Enable Interrupt Register

           EPwm2Regs.TZEINT.bit.OST       = 0;          // Trip Zones One Shot Int Enable

           EPwm2Regs.TZEINT.bit.CBC       = 0;          // Trip Zones Cycle By Cycle Int Enable

     

           EDIS;

     

    }      /* End of EPwm2Init */

     

     

    NOTE that EPwm2Regs.TBCTL.bit.SYNCOSEL = TB_DISABLE; This should disable downstream synchronization with module ePWM3

     

    ePWM3 and ePWM4 are initialized with the following code to achieve the above defined objectives:

     

    void EPwm3Init(void)

    {

           /*** Initialize ePWM3 modules ***/

           /*-- Setup Time-Base (TB) Submodule --*/

           EPwm3Regs.TBPRD = (Uint32)(PLL_FREQUENCY / DabPwmFrequency * 0.5);          // Multiply by 0.5 because we're using an up/down counter and the period is half the frequency

     

           // Time-Base Control Register

           EPwm3Regs.TBCTL.bit.CTRMODE    = TB_COUNT_UPDOWN;                // Counter Mode

           EPwm3Regs.TBCTL.bit.SYNCOSEL   = TB_CTR_ZERO;                    // Synchronize downstream modules

           EPwm3Regs.TBCTL.bit.PRDLD      = TB_SHADOW;                       // Shadow select

           EPwm3Regs.TBCTL.bit.PHSEN      = TB_ENABLE;                       // Phase load enable

           EPwm3Regs.TBCTL.bit.PHSDIR     = TB_DOWN;                       // Phase Direction

           EPwm3Regs.TBCTL.bit.HSPCLKDIV  = TB_DIV1;                       // High speed time pre-scale

           EPwm3Regs.TBCTL.bit.CLKDIV     = TB_DIV1;                       // Timebase clock pre-scale

     

           // Time-Base Phase Register

           EPwm3Regs.TBPHS.half.TBPHS     = 0;                              // Phase offset register

     

           EPwm3Regs.TBCTR = 0x0000;  /* Clear counter*/

     

           /*-- Setup Counter_Compare (CC) Submodule --*/

           // Counter-Compare Control Register

           EPwm3Regs.CMPCTL.bit.SHDWAMODE = 0;                                     // Compare A block operating mode.

           EPwm3Regs.CMPCTL.bit.SHDWBMODE = 0;                                     // Compare B block operating mode.

           EPwm3Regs.CMPCTL.bit.LOADAMODE = 0;                              // Active compare A

           EPwm3Regs.CMPCTL.bit.LOADBMODE = 0;                              // Active compare A

     

           EPwm3Regs.CMPA.half.CMPA = (Uint16)(EPwm3Regs.TBPRD * 0.5);  // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifiers

           EPwm3Regs.CMPB = (Uint16)(EPwm3Regs.TBPRD * 0.5);                // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifiers

     

           /*-- Setup Action-Qualifier (AQ) Submodule --*/

           /* Setup action qualifiers for A module */

           EPwm3Regs.AQCTLA.bit.CAU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm3Regs.AQCTLA.bit.CAD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           EPwm3Regs.AQCTLA.bit.ZRO = AQ_SET;                                            // Set PWM when counter = 0

           EPwm3Regs.AQCTLA.bit.PRD = AQ_CLEAR;                                    // Clear when counter = period

           EPwm3Regs.AQCTLA.bit.CBU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm3Regs.AQCTLA.bit.CBD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           /* Setup action qualifiers for B module */

           EPwm3Regs.AQCTLB.bit.CAU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm3Regs.AQCTLB.bit.CAD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           EPwm3Regs.AQCTLB.bit.ZRO = AQ_CLEAR;                                    // Clear PWM when latch counter = 0

           EPwm3Regs.AQCTLB.bit.PRD = AQ_SET;                                            // Set when counter = period

           EPwm3Regs.AQCTLB.bit.CBU = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting up on B sub-module

           EPwm3Regs.AQCTLB.bit.CBD = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting down on B sub-module

     

     

           // Action-Qualifier Software Force Register

           EPwm3Regs.AQSFRC.bit.RLDCSF    = 3;                              // Reload from Shadow options

     

           // Action-Qualifier Continuous S/W Force Register Set

           EPwm3Regs.AQCSFRC.bit.CSFA     = 0;                              // Continuous Software Force on output A

           EPwm3Regs.AQCSFRC.bit.CSFB     = 0;                              // Continuous Software Force on output B

     

           /*-- Setup Dead-Band Generator (DB) Submodule --*/

           // Dead-Band Generator Control Register

           EPwm3Regs.DBCTL.bit.OUT_MODE   = 3;                              // Dead Band Output Mode Control

           EPwm3Regs.DBCTL.bit.IN_MODE    = 0;                              // Dead Band Input Select Mode Control

           EPwm3Regs.DBCTL.bit.POLSEL     = 2;                              // Polarity Select Control

     

           // EPwm3Regs.DBCTL.all = (EPwm3Regs.DBCTL.all & ~0x3F) | 0xB;

           EPwm3Regs.DBRED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

           EPwm3Regs.DBFED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

     

           /*-- Setup Event-Trigger (ET) Submodule --*/

           // Event-Trigger Selection and Event-Trigger Pre-Scale Register

           EPwm3Regs.ETSEL.bit.SOCAEN     = 0;                                           // Start of conversion A Enable

           EPwm3Regs.ETSEL.bit.SOCASEL    = 1;                              // Start of conversion A Select

           EPwm3Regs.ETPS.bit.SOCAPRD     = 3;                              // EPWM3SOCA Period Select

           EPwm3Regs.ETSEL.bit.SOCBEN     = 0;                              // Start of conversion B Enable

           EPwm3Regs.ETSEL.bit.SOCBSEL    = 1;                              // Start of conversion B Select

           EPwm3Regs.ETPS.bit.SOCBPRD     = 1;                              // EPWM3SOCB Period Select

           EPwm3Regs.ETSEL.bit.INTEN      = 0;                              // EPWM3INTn Enable

           EPwm3Regs.ETSEL.bit.INTSEL     = 1;                              // EPWM3INTn Select

           EPwm3Regs.ETPS.bit.INTPRD      = 3;                              // EPWM3INTn Period Select

     

           /*-- Setup PWM-Chopper (PC) Submodule --*/

           // PWM-Chopper Control Register

           EPwm3Regs.PCCTL.bit.CHPEN      = 0;                              // PWM chopping enable

           EPwm3Regs.PCCTL.bit.CHPFREQ    = 0;                              // Chopping clock frequency

           EPwm3Regs.PCCTL.bit.OSHTWTH    = 0;                              // One-shot pulse width

           EPwm3Regs.PCCTL.bit.CHPDUTY    = 0;                              // Chopping clock Duty cycle

     

           /*-- Set up Trip-Zone (TZ) Submodule --*/

           EALLOW;

           EPwm3Regs.TZSEL.all = 0;

     

           // Trip-Zone Control Register

           EPwm3Regs.TZCTL.bit.TZA        = 2;                              // TZ1 to TZ6 Trip Action On EPWM3A

           EPwm3Regs.TZCTL.bit.TZB        = 2;                              // TZ1 to TZ6 Trip Action On EPWM3B

     

           // Trip-Zone Enable Interrupt Register

           EPwm3Regs.TZEINT.bit.OST       = 0;                              // Trip Zones One Shot Int Enable

           EPwm3Regs.TZEINT.bit.CBC       = 0;                              // Trip Zones Cycle By Cycle Int Enable

     

           EDIS;

     

    } /* End of EPwm3Init */

     

     

     

    void EPwm4Init(void)

    {

           /*** Initialize ePWM4 modules ***/

           /*-- Setup Time-Base (TB) Submodule --*/

           EPwm4Regs.TBPRD = PLL_FREQUENCY / DabPwmFrequency * 0.5;       // Multiply by 0.5 because we're using an up/down counter and the period is half the frequency

     

           // Time-Base Control Register

           EPwm4Regs.TBCTL.bit.CTRMODE    = TB_COUNT_UPDOWN;                // Counter Mode

           EPwm4Regs.TBCTL.bit.SYNCOSEL   = TB_SYNC_IN;                     // Synchronize downstream module ePWM5

           EPwm4Regs.TBCTL.bit.PRDLD      = TB_SHADOW;                             // Shadow select

           EPwm4Regs.TBCTL.bit.PHSEN      = TB_ENABLE;                             // Phase load enable

           EPwm4Regs.TBCTL.bit.PHSDIR     = TB_DOWN;                               // Phase Direction

           EPwm4Regs.TBCTL.bit.HSPCLKDIV  = TB_DIV1;                               // High speed time pre-scale

           EPwm4Regs.TBCTL.bit.CLKDIV     = TB_DIV1;                               // Timebase clock pre-scale

     

           // EPwm4Regs.TBCTL.all = (EPwm4Regs.TBCTL.all & ~0x3FBF) | 0x484;

     

           // Time-Base Phase Register

           EPwm4Regs.TBPHS.half.TBPHS     = 0;                              // Phase offset register

     

           EPwm4Regs.TBCTR = 0x0000;  /* Clear counter*/

     

           /*-- Setup Counter_Compare (CC) Submodule --*/

           // Counter-Compare Control Register

           EPwm4Regs.CMPCTL.bit.SHDWAMODE = 0;                                      // Compare A block operating mode.

           EPwm4Regs.CMPCTL.bit.SHDWBMODE = 0;                                           // Compare B block operating mode.

           EPwm4Regs.CMPCTL.bit.LOADAMODE = 0;                                     // Active compare A

           EPwm4Regs.CMPCTL.bit.LOADBMODE = 0;                              // Active compare A

     

           EPwm4Regs.CMPA.half.CMPA = (Uint16)(EPwm4Regs.TBPRD * 0.5);  // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifiers

           EPwm4Regs.CMPB = (Uint16)(EPwm4Regs.TBPRD * 0.5);                // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifiers

     

           /*-- Setup Action-Qualifier (AQ) Submodule --*/

           /* Setup action qualifiers for A module */

           EPwm4Regs.AQCTLA.bit.CAU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm4Regs.AQCTLA.bit.CAD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           EPwm4Regs.AQCTLA.bit.ZRO = AQ_CLEAR;                                    // Clear PWM when counter = 0

           EPwm4Regs.AQCTLA.bit.PRD = AQ_SET;                                            // Set when counter = period

           EPwm4Regs.AQCTLA.bit.CBU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm4Regs.AQCTLA.bit.CBD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           /* Setup action qualifiers for B module */

           EPwm4Regs.AQCTLB.bit.CAU = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting up

           EPwm4Regs.AQCTLB.bit.CAD = AQ_NO_ACTION;                                // Do nothing when latch value = counter when counting down

           EPwm4Regs.AQCTLB.bit.ZRO = AQ_SET;                                            // Set PWM when latch counter = 0

           EPwm4Regs.AQCTLB.bit.PRD = AQ_CLEAR;                                    // Clear when counter = period

           EPwm4Regs.AQCTLB.bit.CBU = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting up on B sub-module

           EPwm4Regs.AQCTLB.bit.CBD = AQ_NO_ACTION;                                // Do nothing when counter = latch value when counting down on B sub-module

     

           // Action-Qualifier Software Force Register

           EPwm4Regs.AQSFRC.bit.RLDCSF    = 3;                                  // Reload from Shadow options

     

           // Action-Qualifier Continuous S/W Force Register Set

           EPwm4Regs.AQCSFRC.bit.CSFA     = 0;                              // Continuous Software Force on output A

           EPwm4Regs.AQCSFRC.bit.CSFB     = 0;                              // Continuous Software Force on output B

     

           /*-- Setup Dead-Band Generator (DB) Submodule --*/

           // Dead-Band Generator Control Register

           EPwm4Regs.DBCTL.bit.OUT_MODE   = 3;                              // Dead Band Output Mode Control

           EPwm4Regs.DBCTL.bit.IN_MODE    = 0;                              // Dead Band Input Select Mode Control

           EPwm4Regs.DBCTL.bit.POLSEL     = 2;                              // Polarity Select Control

     

           EPwm4Regs.DBRED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

           EPwm4Regs.DBFED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

     

           /*-- Setup Event-Trigger (ET) Submodule --*/

           // Event-Trigger Selection and Event-Trigger Pre-Scale Register

           EPwm4Regs.ETSEL.bit.SOCAEN     = 0;                              // Start of conversion A Enable

           EPwm4Regs.ETSEL.bit.SOCASEL    = 1;                              // Start of conversion A Select

           EPwm4Regs.ETPS.bit.SOCAPRD     = 3;                              // EPWM4SOCA Period Select

           EPwm4Regs.ETSEL.bit.SOCBEN     = 0;                              // Start of conversion B Enable

           EPwm4Regs.ETSEL.bit.SOCBSEL    = 1;                              // Start of conversion B Select

           EPwm4Regs.ETPS.bit.SOCBPRD     = 1;                              // EPWM4SOCB Period Select

           EPwm4Regs.ETSEL.bit.INTEN      = 0;                              // EPWM4INTn Enable

           EPwm4Regs.ETSEL.bit.INTSEL     = 1;                                           // EPWM4INTn Select

           EPwm4Regs.ETPS.bit.INTPRD      = 1;                                           // EPWM4INTn Period Select

     

           /*-- Setup PWM-Chopper (PC) Submodule --*/

           // PWM-Chopper Control Register

           EPwm4Regs.PCCTL.bit.CHPEN      = 0;                              // PWM chopping enable

           EPwm4Regs.PCCTL.bit.CHPFREQ    = 0;                              // Chopping clock frequency

           EPwm4Regs.PCCTL.bit.OSHTWTH    = 0;                              // One-shot pulse width

           EPwm4Regs.PCCTL.bit.CHPDUTY    = 0;                              // Chopping clock Duty cycle

     

           /*-- Set up Trip-Zone (TZ) Submodule --*/

           EALLOW;

           EPwm4Regs.TZSEL.all = 0;

     

           // Trip-Zone Control Register

           EPwm4Regs.TZCTL.bit.TZA        = 2;                              // TZ1 to TZ6 Trip Action On EPWM4A

           EPwm4Regs.TZCTL.bit.TZB        = 2;                              // TZ1 to TZ6 Trip Action On EPWM4B

     

           // Trip-Zone Enable Interrupt Register

           EPwm4Regs.TZEINT.bit.OST       = 0;                              // Trip Zones One Shot Int Enable

           EPwm4Regs.TZEINT.bit.CBC       = 0;                              // Trip Zones Cycle By Cycle Int Enable

     

           EDIS;

     

    }      /* End of EPwm4Init */

     

     

    NOTE that EPwm3Regs.TBCTL.bit.SYNCOSEL = TB_CTR_ZERO; This should initiate a downstream synchronization pulse when the counter = 0, thus having the effect of synchronizing the time-bases and phase changes for EPwm4, 5 and 6 with EPwm3, as long as EPwmNRegs.TBCTL.bit.SYNCOSEL = TB_SYNC_IN, where N = 4, 5 and 6.

     

    Finally, ePWM5 and ePWM6 must be initialized to be 180 degrees out of phase with ePWM3 and ePWM4, but also allow for continuous phase changes during operation to control current. This is accomplished with the following code to initialize ePWM 5 and ePWM6:

     

    void EPwm5Init(void)

    {

           /*** Initialize ePWM5 modules ***/

           /*-- Setup Time-Base (TB) Submodule --*/

           EPwm5Regs.TBPRD = PLL_FREQUENCY / DabPwmFrequency * 0.5;             // Multiply by 0.5 because we're using an up/down counter and the period is half the frequency

     

           // Time-Base Control Register

           EPwm5Regs.TBCTL.bit.CTRMODE    = TB_COUNT_UPDOWN;                       // Counter Mode

           EPwm5Regs.TBCTL.bit.SYNCOSEL   = TB_SYNC_IN;                              // Sync output select

           EPwm5Regs.TBCTL.bit.PRDLD      = TB_SHADOW;                              // Shadow select

           EPwm5Regs.TBCTL.bit.PHSEN      = TB_ENABLE;                              // Phase load enable

           EPwm5Regs.TBCTL.bit.PHSDIR     = TB_DOWN;                              // Phase Direction

           EPwm5Regs.TBCTL.bit.HSPCLKDIV  = TB_DIV1;                               // High speed time pre-scale

           EPwm5Regs.TBCTL.bit.CLKDIV     = TB_DIV1;                              // Timebase clock pre-scale

     

           // Time-Base Phase Register

           EPwm5Regs.TBPHS.half.TBPHS     = PLL_FREQUENCY / DabPwmFrequency * 0.5 * 0.5;          // Multiply by 0.5 for up/down counter to obtain the period, then multiply by 0.5 to shift 180 degrees

     

           EPwm5Regs.TBCTR = 0x0000;  /* Clear counter*/

     

           /*-- Setup Counter_Compare (CC) Submodule --*/

           // Counter-Compare Control Register

           EPwm5Regs.CMPCTL.bit.SHDWAMODE = CC_SHADOW;                             // Compare A block operating mode.

           EPwm5Regs.CMPCTL.bit.SHDWBMODE = CC_SHADOW;                             // Compare B block operating mode.

           EPwm5Regs.CMPCTL.bit.LOADAMODE = CC_SHADOW;                              // Active compare A

           EPwm5Regs.CMPCTL.bit.LOADBMODE = CC_SHADOW;                              // Active compare A

     

           EPwm5Regs.CMPA.half.CMPA = (Uint16)(EPwm5Regs.TBPRD * 0.5);        // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifiers

           EPwm5Regs.CMPB = (Uint16)(EPwm5Regs.TBPRD * 0.5);                       // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifiers

     

           /*-- Setup Action-Qualifier (AQ) Submodule --*/

           /* Setup action qualifiers for A module */

           EPwm5Regs.AQCTLA.bit.CAU = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting up

           EPwm5Regs.AQCTLA.bit.CAD = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting down

           EPwm5Regs.AQCTLA.bit.ZRO = AQ_CLEAR;                                          // Clear PWM when counter = 0

           EPwm5Regs.AQCTLA.bit.PRD = AQ_SET;                                                   // Set when counter = period

           EPwm5Regs.AQCTLA.bit.CBU = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting up

           EPwm5Regs.AQCTLA.bit.CBD = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting down

           /* Setup action qualifiers for B module */

           EPwm5Regs.AQCTLB.bit.CAU = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting up

           EPwm5Regs.AQCTLB.bit.CAD = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting down

           EPwm5Regs.AQCTLB.bit.ZRO = AQ_SET;                                                   // Set PWM when latch counter = 0

           EPwm5Regs.AQCTLB.bit.PRD = AQ_CLEAR;                                          // Clear PWM when counter = period

           EPwm5Regs.AQCTLB.bit.CBU = AQ_NO_ACTION;                                      // Do nothing when counter = latch value when counting up on B sub-module

           EPwm5Regs.AQCTLB.bit.CBD = AQ_NO_ACTION;                                      // Do nothing when counter = latch value when counting down on B sub-module

     

           // Action-Qualifier Software Force Register

           EPwm5Regs.AQSFRC.bit.RLDCSF    = 3;                                     // Reload from Shadow options

     

           // Action-Qualifier Continuous S/W Force Register Set

           EPwm5Regs.AQCSFRC.bit.CSFA     = 0;                                     // Continuous Software Force on output A

           EPwm5Regs.AQCSFRC.bit.CSFB     = 0;                                     // Continuous Software Force on output B

     

           /*-- Setup Dead-Band Generator (DB) Submodule --*/

           // Dead-Band Generator Control Register

           EPwm5Regs.DBCTL.bit.OUT_MODE   = 3;                                     // Dead Band Output Mode Control

           EPwm5Regs.DBCTL.bit.IN_MODE    = 0;                                     // Dead Band Input Select Mode Control

           EPwm5Regs.DBCTL.bit.POLSEL     = 2;                                     // Polarity Select Control

     

           EPwm5Regs.DBRED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

           EPwm5Regs.DBFED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

     

           /*-- Setup Event-Trigger (ET) Submodule --*/

           // Event-Trigger Selection and Event-Trigger Pre-Scale Register

           EPwm5Regs.ETSEL.bit.SOCAEN     = 0;                                     // Start of conversion A Enable

           EPwm5Regs.ETSEL.bit.SOCASEL    = 1;                                     // Start of conversion A Select

           EPwm5Regs.ETPS.bit.SOCAPRD     = 3;                                     // EPWM5SOCA Period Select

           EPwm5Regs.ETSEL.bit.SOCBEN     = 0;                                     // Start of conversion B Enable

           EPwm5Regs.ETSEL.bit.SOCBSEL    = 1;                                     // Start of conversion B Select

           EPwm5Regs.ETPS.bit.SOCBPRD     = 1;                                     // EPWM5SOCB Period Select

           EPwm5Regs.ETSEL.bit.INTEN      = 0;                                     // EPWM5INTn Enable

           EPwm5Regs.ETSEL.bit.INTSEL     = 1;                                     // EPWM5INTn Select

           EPwm5Regs.ETPS.bit.INTPRD      = 1;                                     // EPWM5INTn Period Select

     

           /*-- Setup PWM-Chopper (PC) Submodule --*/

           // PWM-Chopper Control Register

           EPwm5Regs.PCCTL.bit.CHPEN      = 0;                                     // PWM chopping enable

           EPwm5Regs.PCCTL.bit.CHPFREQ    = 0;                                     // Chopping clock frequency

           EPwm5Regs.PCCTL.bit.OSHTWTH    = 0;                                     // One-shot pulse width

           EPwm5Regs.PCCTL.bit.CHPDUTY    = 0;                                     // Chopping clock Duty cycle

     

           /*-- Set up Trip-Zone (TZ) Submodule --*/

           EALLOW;

           EPwm5Regs.TZSEL.all = 0;

     

           // Trip-Zone Control Register

           EPwm5Regs.TZCTL.bit.TZA        = 2;                                     // TZ1 to TZ6 Trip Action On EPWM5A

           EPwm5Regs.TZCTL.bit.TZB        = 2;                                     // TZ1 to TZ6 Trip Action On EPWM5B

     

           // Trip-Zone Enable Interrupt Register

           EPwm5Regs.TZEINT.bit.OST       = 0;                                     // Trip Zones One Shot Int Enable

           EPwm5Regs.TZEINT.bit.CBC       = 0;                                     // Trip Zones Cycle By Cycle Int Enable

     

           EDIS;

     

    }      /* End of EPwm5Init */

     

     

     

    void EPwm6Init(void)

    {

           /*** Initialize ePWM6 modules ***/

           /*-- Setup Time-Base (TB) Submodule --*/

           EPwm6Regs.TBPRD = PLL_FREQUENCY / DabPwmFrequency * 0.5;             // Multiply by 0.5 because we're using an up/down counter and the period is half the frequency

     

           // Time-Base Control Register

           EPwm6Regs.TBCTL.bit.CTRMODE    = TB_COUNT_UPDOWN;                       // Counter Mode

           EPwm6Regs.TBCTL.bit.SYNCOSEL   = TB_SYNC_IN;                       // Sync output select

           EPwm6Regs.TBCTL.bit.PRDLD      = TB_SHADOW;                                 // Shadow select

           EPwm6Regs.TBCTL.bit.PHSEN      = TB_ENABLE;                           // Phase load enable

           EPwm6Regs.TBCTL.bit.PHSDIR     = TB_DOWN;                              // Phase Direction

           EPwm6Regs.TBCTL.bit.HSPCLKDIV  = TB_DIV1;                              // High speed time pre-scale

           EPwm6Regs.TBCTL.bit.CLKDIV     = TB_DIV1;                              // Timebase clock pre-scale

     

           // Time-Base Phase Register

           EPwm6Regs.TBPHS.half.TBPHS     = 0;                                                  // Phase offset register

     

           EPwm6Regs.TBCTR = 0x0000;  /* Clear counter*/

     

           /*-- Setup Counter_Compare (CC) Submodule --*/

           // Counter-Compare Control Register

           EPwm6Regs.CMPCTL.bit.SHDWAMODE = CC_SHADOW;                              // Compare A block operating mode.

           EPwm6Regs.CMPCTL.bit.SHDWBMODE = CC_SHADOW;                             // Compare B block operating mode.

           EPwm6Regs.CMPCTL.bit.LOADAMODE = CC_SHADOW;                       // Active compare A

           EPwm6Regs.CMPCTL.bit.LOADBMODE = CC_SHADOW;                              // Active compare A

     

           EPwm6Regs.CMPA.half.CMPA = (Uint16)(EPwm6Regs.TBPRD * 0.5);        // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifierscycle

           EPwm6Regs.CMPB = (Uint16)(EPwm6Regs.TBPRD * 0.5);                       // 50% duty cycle -- no longer matters due to setting of AQCTLA.bit.ZRO and .PRD action qualifiers

     

           /*-- Setup Action-Qualifier (AQ) Submodule --*/

           EPwm6Regs.AQCTLA.bit.CAU = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting up

           EPwm6Regs.AQCTLA.bit.CAD = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting down

           EPwm6Regs.AQCTLA.bit.ZRO = AQ_SET;                                                   // Set PWM when counter = 0

           EPwm6Regs.AQCTLA.bit.PRD = AQ_CLEAR;                                          // Clear when counter = period

           EPwm6Regs.AQCTLA.bit.CBU = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting up

           EPwm6Regs.AQCTLA.bit.CBD = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting down

           /* Setup action qualifiers for B module */

           EPwm6Regs.AQCTLB.bit.CAU = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting up

           EPwm6Regs.AQCTLB.bit.CAD = AQ_NO_ACTION;                                      // Do nothing when latch value = counter when counting down

           EPwm6Regs.AQCTLB.bit.ZRO = AQ_CLEAR;                                          // Clear PWM when latch counter = 0

           EPwm6Regs.AQCTLB.bit.PRD = AQ_SET;                                                   // Set when counter = period

           EPwm6Regs.AQCTLB.bit.CBU = AQ_NO_ACTION;                                      // Do nothing when counter = latch value when counting up on B sub-module

           EPwm6Regs.AQCTLB.bit.CBD = AQ_NO_ACTION;                                      // Do nothing when counter = latch value when counting down on B sub-module

     

           // Action-Qualifier Software Force Register

           EPwm6Regs.AQSFRC.bit.RLDCSF    = 3;                                     // Reload from Shadow options

     

           // Action-Qualifier Continuous S/W Force Register Set

           /* Setup action qualifiers for A module */

           EPwm6Regs.AQCSFRC.bit.CSFA     = 0;                                                  // Continuous Software Force on output A

           EPwm6Regs.AQCSFRC.bit.CSFB     = 0;                                                  // Continuous Software Force on output B

     

           /*-- Setup Dead-Band Generator (DB) Submodule --*/

           // Dead-Band Generator Control Register

           EPwm6Regs.DBCTL.bit.OUT_MODE   = 3;                                                  // Dead Band Output Mode Control

           EPwm6Regs.DBCTL.bit.IN_MODE    = 0;                                     // Dead Band Input Select Mode Control

           EPwm6Regs.DBCTL.bit.POLSEL     = 2;                                     // Polarity Select Control

     

           EPwm6Regs.DBRED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

           EPwm6Regs.DBFED = (Uint16)(PLL_FREQUENCY * DabDeadtime);

     

           /*-- Setup Event-Trigger (ET) Submodule --*/

           // Event-Trigger Selection and Event-Trigger Pre-Scale Register

           EPwm6Regs.ETSEL.bit.SOCAEN     = 0;                                     // Start of conversion A Enable

           EPwm6Regs.ETSEL.bit.SOCASEL    = 1;                                     // Start of conversion A Select

           EPwm6Regs.ETPS.bit.SOCAPRD     = 3;                                     // EPWM6SOCA Period Select

           EPwm6Regs.ETSEL.bit.SOCBEN     = 0;                                                  // Start of conversion B Enable

           EPwm6Regs.ETSEL.bit.SOCBSEL    = 1;                                                  // Start of conversion B Select

           EPwm6Regs.ETPS.bit.SOCBPRD     = 1;                                                  // EPWM6SOCB Period Select

           EPwm6Regs.ETSEL.bit.INTEN      = 0;                                                  // EPWM6INTn Enable

           EPwm6Regs.ETSEL.bit.INTSEL     = 1;                                                  // EPWM6INTn Select

           EPwm6Regs.ETPS.bit.INTPRD      = 1;                                                  // EPWM6INTn Period Select

     

           /*-- Setup PWM-Chopper (PC) Submodule --*/

           // PWM-Chopper Control Register

           EPwm6Regs.PCCTL.bit.CHPEN      = 0;                                                  // PWM chopping enable

           EPwm6Regs.PCCTL.bit.CHPFREQ    = 0;                                                  // Chopping clock frequency

           EPwm6Regs.PCCTL.bit.OSHTWTH    = 0;                                                  // One-shot pulse width

           EPwm6Regs.PCCTL.bit.CHPDUTY    = 0;                                                  // Chopping clock Duty cycle

     

           /*-- Set up Trip-Zone (TZ) Submodule --*/

           EALLOW;

           EPwm6Regs.TZSEL.all = 0;

     

           // Trip-Zone Control Register

           EPwm6Regs.TZCTL.bit.TZA        = 2;                                                  // TZ1 to TZ6 Trip Action On EPWM6A

           EPwm6Regs.TZCTL.bit.TZB        = 2;                                     // TZ1 to TZ6 Trip Action On EPWM6B

     

           // Trip-Zone Enable Interrupt Register

           EPwm6Regs.TZEINT.bit.OST       = 0;                                     // Trip Zones One Shot Int Enable

           EPwm6Regs.TZEINT.bit.CBC       = 0;                                     // Trip Zones Cycle By Cycle Int Enable

     

           EDIS;

     

    }      /* End of EPwm6Init */

     

     

    With the above code, there is no phase synchronization between ePWM3/ePWM4 and ePWM5/ePWM6 unless the EPwm2Regs.TBCTL.bit.SYNCOSEL bit is set to 0. When I do this and add frequency dither to ePWM1 and ePWM2 by manipulating the EPwm1Regs.TBPRD value then the dither continues to the ePWM3 through ePWM6 modules. Since they are running at different frequencies, the dither represents a significantly different % change in frequency between ePWM1/ePWM2 (24kHz) and ePWM3/ePWM4/ePWM5/ePWM6 (72kHz). Thus the need for EPwm2Regs.TBCTL.bit.SYNCOSEL to be set to 3 so as not to synchronize across these different frequency domains.

     

    All of the above explains our primary and most urgent problem. The second problem is that if you change the DabPwmFrequency to 68000 from 72000, the modulators exhibit odd behavior and you can occasionally capture frequency and/or duty cycle changes that happen rare enough that if you didn’t pay close attention, you would not see them. The severity of these changes appears to be related to particular frequencies defined by the DabPwmFrequency setting, i.e., some frequency are worse than others. It is our view that ANY frequency should work in the prescribed manner, i.e., 50% duty cycle at the frequency determined by DabPwmFrequency. I have captured this behavior on a scope and inserted it below. I have included both expected and unexpected modulator output.

     

     

    Normal and expected results when ePWM1 and ePWM2 are running at 24kHz and ePWM3 – ePWM6 are running at 72kHz can be seen with phase shift in the attached movie file 20190607_155713.mp4. Just for reference, I have also attached what happens to the phase shifting when I disconnect the sync output from module ePWM2 to 3 to allow for independent operation of ePWM1/ePWM2 from ePWM3/4/5/6 in file 20190607_160114.mp4. In all examples below the EPwm2Regs.TBCTL.bit.SYNCOSEL bit is set in order to achieve controllable phase shifting between modules ePWM3/ePWM4 with respect to ePWM5/ePWM6.

     

    Unexpected Result: ePWM5A as observed on the EZDSP Development Kit (Pin 30 of P8) changes frequency and duty cycle.

     

    Another scope shot showing an unexpected result – there are subtle variations in ePWM3A (pin 13 of P8 on the EZDSP dev board) and large and erratic changes on ePWM5A (pin 30 of P8):

    Any suggestions to resolving this problem would be greatly appreciated.

    Thanks

    Viktorija

  • Viktorija,

    there was a lot of information in there, so if I did not address a question please let me know.

    Cody Watkins said:
    There should be no issue with separating the ePWM sync chain into two time domains.

    While the above quote it true, it is not clear in reference to your issue. It is true that you can split the ePWM sync chain into different time domains. However, on F28335 you cannot directly synchronize PWMS 3 and 4 without PWM 1. Please see the following sync chain diagram. PWM3 sync out does not connect to PWM4 sync in.

    The only way to synchronize PWMs 3 and 4 is to synchronize them both to PWM1. The customer will need to evaluate keeping the PWMs synchronized to ePWM1 if this is not acceptable then the may have to rework hardware. One option would be to connect PWMs 1, 4, 5, and 6 for their 72KHz signals and PWMs 2 and 3 for their slower 24KHz signals. Note: if they did go with this configuration the could not sync the 24KHz and 72KHz domains on a cycle-by-cycle basis(the could preform a sync at the beginning though)

    For the second issue its a some what unclear which signal the customer is referencing. If it is the purple signal then this may be caused by the incidental re-syncing to PWM1 expanding or reducing the high or low times. If they are referencing the green signal: that appears to be a major issue that would need more investigation. Off of the top of my head it looks like you are possibly missing a compare value... Is the customer correctly using shadow loading?

    Regards,
    Cody 

  • Cody, 

    Per customer:

    The internal connections between the ePWM modules described and outlined below is surprising. Is this elaborated upon anywhere in the ePWM Technical Reference?

    This is a problem for us and we will likely have to re-orient the modules in hardware to fully accomplish our functional objectives.

    Thanks

    Viktorija

  • Viktorija, 

    this is documented in the Data Sheet so that a customer will identify this issue early on when assessing the device. The thinking is any information that is required for "High Level" system planning should included in the datasheet.

    The synchronization chain is discussed in the ePWM Reference Guide, but the exact connections are not detailed.

    Is there some misleading information in the documentation which caused the customer believe that the ePWM modules are connected in another way?

    Does the Customer need to maintain a cycle-by-cycle synchronization? If the customer plans to keep the period and phase offset constant between ePWMs 3,4,5, and 6 then they might be able to get away with sync'ing their higher speed PWMs to ePWM 0 at initialization. After initialization the can disable the sync chain for ePWMs 3,4,5, and 6. This will establish a set phase relationship between them, and will keep the dithering of ePWM1 from affecting them.

    Regards,
    Cody 

  • Cody,
    Feedback from customer:
    I understand and appreciate that it is covered on the datasheet with a diagram. However, we all know that nobody goes to the datasheet to get detailed application programming information. IMHO, this should have been covered in a very detailed manner within the ePWM Tech Ref. It is not and it has cost us time. It’s a bit disappointing.

    Please consider adding this info into ePWM Tech Reference document as well. 

    Thanks

    Viktorija

  • Victorija,

    I agree with the customer that this information should be included in the Tech Ref., I was a little surprised when I didn't see it on first glance.

    If fact this information is actually also in the ePWM's User's Guide, Please see Figure 9.

    Regards,
    Cody