Hi:
when USE DB_ACTV_HIC to initial ePWM , a unexpected plus occur on EPWM1B when execute initial, the display as below:
CH1: Trigger signal CH2:EPWM1B, EPWM1A is always low( do not display on scope)
the initial code:
EPwm1Regs.AQCTLA.bit.CAU = AQ_CLEAR;
EPwm1Regs.AQCTLA.bit.CAD = AQ_SET;
EPwm1Regs.AQCTLB.bit.CBU = AQ_CLEAR;
EPwm1Regs.AQCTLB.bit.CBD = AQ_SET;
EPwm1Regs.AQSFRC.bit.RLDCSF = 3; //The active register load immediately
EPwm1Regs.AQCSFRC.bit.CSFA = FORCE_LOW; //FORCE the EPWM2A output LOW
EPwm1Regs.AQCSFRC.bit.CSFB = FORCE_HIGH; //FORCE the EPWM2B output HIGH
EPwm1Regs.DBCTL.bit.IN_MODE = DBA_RED_DBB_FED; //EPWMxA In is the source for rising-edge delayed signal.
EPwm1Regs.DBCTL.bit.DEDB_MODE = 0;
EPwm1Regs.DBCTL.bit.POLSEL = DB_ACTV_HIC; //Active high complementary (AHC). EPWMxB is inverted.
EPwm1Regs.DBCTL.bit.OUT_MODE = DB_FULL_ENABLE; //Enable dead band time configuration
EPwm1Regs.DBCTL.bit.OUTSWAP = 0;
EPwm1Regs.DBRED.all = EPWM1_DBRED;
EPwm1Regs.DBFED.all = EPWM1_DBFED;
then change to DB_ACTV_HI, the display as below:
CH1: Trigger signal CH2:EPWM1B, EPWM1A is always low( do not display on scope)
the initial code:
EPwm1Regs.AQCTLA.bit.CAU = AQ_CLEAR;
EPwm1Regs.AQCTLA.bit.CAD = AQ_SET;
EPwm1Regs.AQCTLB.bit.CBU =AQ_SET ;
EPwm1Regs.AQCTLB.bit.CBD = AQ_CLEAR;
EPwm1Regs.AQSFRC.bit.RLDCSF = 3; //The active register load immediately
EPwm1Regs.AQCSFRC.bit.CSFA = FORCE_LOW; //FORCE the EPWM2A output LOW
EPwm1Regs.AQCSFRC.bit.CSFB = FORCE_LOW; //FORCE the EPWM2B output HIGH
EPwm1Regs.DBCTL.bit.IN_MODE = DBA_RED_DBB_FED; //EPWMxA In is the source for rising-edge delayed signal.
EPwm1Regs.DBCTL.bit.DEDB_MODE = 0;
EPwm1Regs.DBCTL.bit.POLSEL = DB_ACTV_HI; //Active high complementary (AHC). Neither EPWMxA nor EPWMxB is inverted (default).
EPwm1Regs.DBCTL.bit.OUT_MODE = DB_FULL_ENABLE; //Enable dead band time configuration
EPwm1Regs.DBCTL.bit.OUTSWAP = 0;
EPwm1Regs.DBRED.all = EPWM1_DBRED;
EPwm1Regs.DBFED.all = EPWM1_DBFED;
Between the two plans ,the first give EPWM1B force high then inverter in DBCTL[POLSEL], the second give EPWM1B force low then Neither EPWMxA nor EPWMxB isinverted in DBCTL[POLSEL].
The initial code is execute in sequence, the two plans should have same output on EPWM1B, why the fisrt have a 20us high pluse.
Addition information:
fpwm:20kHz
EPwm1Regs.CMPCTL.bit.SHDWAMODE = CC_SHADOW;
EPwm1Regs.CMPCTL.bit.SHDWBMODE = CC_SHADOW;
EPwm1Regs.CMPCTL.bit.LOADAMODE = CC_CTR_ZERO_PRD;
EPwm1Regs.CMPCTL.bit.LOADBMODE = CC_CTR_ZERO_PRD;
Thanks
Supplement:
In the first plan , EPWM1A and 1B have same value and action, use DBCTL[POLSEL] to inverte EPWM1B, and use DBRED and DBFED to set DEADBAND time.
In the second plan , EPWM1A and 1B have same value and Complementary action, use +/- Dtime value to set DEADBAND time.
Prefer the first plan ,but can not accept the unexpected high pluse when initial.
Thanks
Hi,
Can you refer this post and let me know if it helps?
https://e2e.ti.com/support/microcontrollers/c2000/f/171/t/838289?TMS320F280049-Active-high-complementary-PWMs This seems to refer to the same issue you've explained here, if i understand correctly.
HI:
Thanks for you reply.
As my post above , i use DB_ACTV_HI to dismiss the unexpected plus.But about DB_ACTV_HIC, before EPwm1Regs.DBCTL.bit.POLSEL = DB_ACTV_HI, i set the EPwm1Regs.AQCSFRC.bit.CSFA = FORCE_LOW; EPwm1Regs.AQCSFRC.bit.CSFB = FORCE_HIGH;.
The initial code is execute in sequence, so i think the high plus shouid be the execute time of the two code between . The execute time should less than 20us , why the high plus have 20us
the post you suggest is less than 20us
Hi,
The deadband configuration, be it active high or active high complimentary (edge based configuration/delay) would come into effect upon PWM edge occurrence.
EPwm1Regs.AQCSFRC.bit.CSFA/B forces would take effect immediately. It's not clear to me why you had to do continuous software force in the initial configuration.
Also, in case you use CSFA/B but NOT configure PWM to be EPwm1Regs.DBCTL.bit.POLSEL = DB_ACTV_HI and only use DB_ACTV_HIC, do you still see the same results?
Can you also cross check configuration w.r.t. example below?
C:\ti\c2000\C2000Ware_2_01_00_00\device_support\f2837xd\examples\cpu1\epwm_deadband\cpu01
EPWM3 uses DB_ACTV_HIC.